Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Service Conductors to Fire Pump Controller - Grounded Conductor

User: nhee2, Location: NH

Asked on: Wednesday, August 21, 2024 at 11:03 am EDT
Answered on: Thursday, March 6, 2025 at 1:26 am EST

Question: We have a 3 ph utility service (480/277 grounded) supplying a service switchboard, with a segregated vertical section which has a tap for service conductors (upstream of service disconnection) to supply a firewater pump controller. From the utility to switchboard we are bringing our grounded conductor and bonding within the switchboard.For the conductors that go over to the fire pump controller, I understand these are still considered service conductors, and sized per 695.6 and 695.7. Is it correct that we need to bring the grounded conductor from the switchboard to the fire pump controller, and that this is considered 'grounded service conductor', sized per 250.24(C) and 250.102(C)(1)? Then, we re-bond the conductor at the fire pump controller as well?I'm reverifying that my grounded conductor hasn't turned into an EGC due to its connection in the switchboard, but I'm thinking what I've described above is correct.

You are on the right track, but let's break it down to ensure clarity and code compliance.Here's a detailed explanation of your situation and the applicable NEC requirements

Understanding the System:
Service Entrance

You have a 480/277V, 3-phase grounded service entering a service switchboard.


Grounded Conductor Bonding

The grounded conductor is bonded within the service switchboard.

Fire Pump Tap

You are tapping the service conductors

upstream
of the main service disconnecting means within a segregated section of the switchboard to supply the fire pump controller. This is crucial. Service Conductors

Conductors tapped upstream from the main service disconnect are considered service conductors according to the definition of service conductors in Article 100, even though they are supplying a fire pump.

NEC Requirements for Fire Pump Service Conductors


Conductor Sizing (695.6 and 695.7)

You are correct; the conductors supplying the fire pump controller must be sized per 695.6 (Voltage drop) and 695.7 (Ampacity).
2.


Grounded Service Conductor (250.24(C) and 250.102(C)(1))

This is the key area where clarity is essential.

Yes, you must run the grounded conductor to the fire pump controller.
The grounded conductor remains a grounded service conductor because these conductors are tapped upstream of the service disconnecting means. It is not an EGC. It needs to be sized according to 250.24(C) which states the grounded conductor shall not be smaller than that required by 250.166 or 250.
102. In this case, 250.102(C)(1) is applicable.
Sizing the Grounded Conductor

Size the grounded conductor per 250.102(C)(1). This section dictates the grounded conductor size based on the ungrounded conductors' size supplying the fire pump controller.

Bonding at Fire Pump Controller

Yes,

you must establish a grounding electrode system at the fire pump controller
. This is in addition to the main service grounding electrode system. Typically this requires a grounding rod(s) or approved alternate in accordance with 250.52(A)(5) at the fire pump controller and the fire pump assembly. This ensures that a low-impedance ground fault path exists for the fire pump system. This bonding conductor, running from the controller to the local grounding electrode system, will need to be sized per 250.
66.
Crucial Point

The grounded conductor retains its identity as the grounded service conductor because the fire pump tap is upstream of the service disconnecting means.3.

Separation of Service and Equipment Grounding

You're right to question whether the grounded conductor becomes an EGC. The key here is the "upstream" tap. Since the fire pump is tapped before the main service disconnect, the grounded conductor is still considered a service conductor for the fire pump. It is not acting as an EGC. An EGC will be run within the fire pump circuit to all equipment.

Summary of Connections



Service Switchboard

Grounded Conductor bonded within the service switchboard.

Fire Pump Controller

Grounded Service Conductor from the service switchboard is connected to the neutral/grounding bar within the fire pump controller. A grounding electrode system (rod(s), plate, etc.) is established and connected to the neutral/grounding bar with a grounding electrode conductor sized per Table 250.66. Equipment Grounding Conductors (EGCs) are installed with all fire pump circuit conductors and connected to all metal enclosures, raceways, and equipment, back to the grounding bus in the fire pump controller and then back to the service entrance.

Important Considerations



Labeling

Be sure to label the fire pump disconnecting means clearly (695.4(B)).


Coordination

Ensure proper coordination with the utility regarding the fire pump service.

AHJ

Always consult with your local Authority Having Jurisdiction (AHJ) for any specific requirements or interpretations they may have.

In Conclusion:


Your understanding is largely correct. The grounded conductor must be run to the fire pump controller and connected to a local grounding electrode system. It remains a grounded
service* conductor and must be sized accordingly. You also need to have an equipment grounding conductor for the fire pump itself, back to the controller, and ultimately back to the service entrance. Review articles 695, 250, and applicable portions of Article 230. Ensure that the fire pump controller is specifically listed for the intended purpose. Flag for review

Previous Question Next Question