User: branchedout, Location: Tennessee
Asked on: Wednesday, August 21, 2024 at 12:05 pm EDT
Answered on: Thursday, March 6, 2025 at 1:26 am EST
Question: Ingersoll Rand will not give specific answers on recommended sizing for the breaker or fuses even though they require Class J fast acting fuses to be installed on any VFD compressor.Here's the details-460V-3 phase-125 HP-total package amps 186Just need some help as I keep getting vague answers from IR.
You're right to be persistent. It's frustrating when manufacturers aren't clear on crucial information. While I can't provide a guarantee (as I don't have the exact VFD model and specific motor data), I can give you a very strong, code-compliant starting point and the reasoning behind it. This is for informational purposes only, consult with a licensed electrician.
Here's the approach, based on the National Electrical Code (NEC) and common practices for VFDs
1. NEC Basics & Considerations
NEC Article 430 (Motors, Motor Circuits, and Controllers)
This is the key section. Especially 430.52 (Short-Circuit and Ground-Fault Protection) and 430.130 (Conductor Sizing).
VFD as a Component
The VFD is part of the motor circuit and has its own ratings that must be respected.
Fast-Acting Fuses (Class J)
Ingersoll Rand specifying Class J is crucial. These are designed to handle the inrush current of a motor starting AND to protect the VFD's sensitive power electronics from overcurrent. Using the wrong type of fuse can damage the VFD.
"Total Package Amps"
The 186A figure is likely the maximum input current the entire package (compressor, motor, VFD, etc.) can draw under full load and worst-case conditions. This is your starting point.
2. Fuse Sizing (Class J Fast-Acting)
NEC 430.52 covers fuse sizing for motors. The general rule of thumb is to size the fuse no larger than 175% of the motor's full-load amps (FLA). However, VFDs introduce a complication because they often have internal limitations.Here is my recommendation for fuse sizing and reasoning
Fuse Size: 200 Amp Class J
Rationale
175% FLA
Since we don't have the motor FLA, we will use 186, and multiply by 175% to get 325.5 Amps. This is far above the specified rating and thus we should reduce this.
Above Total Package Amps
The fuse should be at least be rated for the total package amps of 186. The next common size is 200 amps.
Avoid Nuisance Tripping
Slightly oversizing within code limits can prevent nuisance tripping, especially with VFDs, which can sometimes cause short current spikes.
Class J is King
Do not substitute other fuse classes unless specifically approved by Ingersoll Rand.
3. Breaker Sizing
Breakers are sized to protect the conductors from overcurrent. They also serve as a disconnecting means. The conductors need to be rated for 125% of the motor's full-load amps per NEC 430.130. The breaker must be large enough to handle the load, but sized to protect the conductors.
Breaker Size: 200 Amp Rationale
Slightly oversizing
We size the breaker to match the fuse size.
Avoid Nuisance Tripping
Slightly oversizing can prevent nuisance tripping.
Conductor Ampacity
You need to select conductors that are rated to handle at least 125% of 186 amps (232.5 amps), after derating for ambient temperature, number of conductors in a raceway, etc., per NEC 310.
15. This likely means you'll need conductors sized for at least 250 amps. Consult a licensed electrician to perform this.
4. Grounding Dedicated Ground Conductor
Absolutely essential for VFDs. Run a properly sized (based on the overcurrent protection) insulated ground conductor back to the source. Do NOT rely on conduit as the sole grounding path.
VFD Grounding Point
The VFD will have a designated grounding terminal. Follow the manufacturer's instructions precisely.
Important Cautions and Steps to Take Get the Actual Motor FLA
The most accurate way to determine the exact fuse/breaker size is to get the motor's nameplate FLA and VFD model number and specifications. IR should be able to provide the motor information.
Consult Ingersoll Rand (Again)
Be persistent. Tell them you need the minimum and maximum allowable Class J fuse size specifically for the model of VFD used in your compressor package. Explain that you need it for code compliance and to protect their equipment. Escalate to a higher level of technical support if necessary.
Check the VFD Manual
The VFD manufacturer's manual will contain specific recommendations on overcurrent protection, conductor sizing, and grounding. This is often the most authoritative source.
Licensed Electrician is MANDATORY
This is not a DIY project. A qualified, licensed electrician must perform the installation, verify the calculations, select the correct components, and ensure compliance with all applicable codes. They have the training and experience to handle the complexities of VFD installations.
Document Everything: Keep a record of all calculations, manufacturer recommendations, and the electrician's work. This will be invaluable for future maintenance and troubleshooting.By following these steps and working with a qualified electrician, you can ensure a safe and code-compliant installation that protects your equipment and meets your operational needs. Good luck! Flag for review