Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Non fused disc and NEC 110.26

User: 82angelfan, Location: Hesperia, Ca

Asked on: Wednesday, August 21, 2024 at 12:54 pm EDT
Answered on: Thursday, March 6, 2025 at 1:26 am EST

Question: Hello,I have a 30 amp non-fused disconnect that is 39" opposite some water pipes. the Electrical engineer is calling us on condition 2 of 110-26 (A) 1. Clearance should be 42". The equipment it is feeding is a water take pump control cabinet has a door and it's own disconnect switch. My Area GF is telling me that a non-fused disco is just a switch since there are no fuses, no need for testing, examining, adjusting, and it is only a means of disconnect in the event of replacing the control cabinet. In addition, when the switch is in the off position, there are no live exposed parts. He tells me they have argued this exact case on Los Angeles Unified School District projects, which are the one of the strictest construction codes, second only to California OSHPD/HCAI, which is where I am.Has anyone else encountered and conquered this?It will be a lot of work to relocate on switch. My next move is to suggest covering the plumbing or installing an enclosed motor rated switch.

You've outlined a common and frustrating situation. Let's break down the code and the arguments

NEC 110.26(A)(1) (2023 NEC, assuming you're on the latest)

This section dictates working clearances around electrical equipment operating at 600 volts, nominal, or less. The key phrases are: "Equipment that is likely to require examination, adjustment, servicing, or maintenance while energized shall have the following minimum clearances..." Condition 2

Exposed live parts on one side and grounded parts on the other side.

The Argument for Non-Compliance (Engineer's Point of View)

The electrical engineer is interpreting the code literally. They see the disconnect switch, notice it's opposite grounded pipes, and immediately apply the 42" clearance requirement for Condition 2. They are likely being cautious and taking a conservative approach to code compliance.

Your Argument for Compliance (GF's Point of View)

Your GF's argument hinges on several points:1.

The Disconnect is Just a Switch

Because it's non-fused, it is not expected to require examination or servicing, like a fused disconnect panel would.2.

Disconnect-Only Function

The purpose is solely for disconnecting power to the downstream control cabinet for replacement, not for regular maintenance on the disconnect itself.3.

No Exposed Live Parts When Off

When the switch is in the OFF position, there are no exposed live parts accessible to someone standing in front of the switch.4.

Precedent

The argument has been accepted on projects with stringent codes (LAUSD).

Analysis and Potential Solutions


Here's a more detailed analysis and a pathway to resolution: The Weak Point in Your GF's Argument

While your GF's points have merit, the wording "likely to require examination, adjustment, servicing, or maintenance while energized" is the key phrase. The Engineer will argue that
any electrical switch could require troubleshooting or replacement while energized, even though it's unlikely. The fact that it's possible will likely be enough for the engineer to hold his ground.

The Strongest Argument for the 39" Clearance is a "Safe Work Practice" analysis.
The most critical step is doing a Hazard assessment in accordance with NFPA 70E, Standard for Electrical Safety in the Workplace. While it is an employer to employee document, it has been accepted by inspectors and engineers across the US as a determining factor in reducing electrical hazards. Strategies for Resolution


Review the Design Specifications

Double-check the original design documents and specifications. Was there a note about the placement of this disconnect switch and clearance requirements? Was 39" ever considered an acceptable clearance?2.

Formal Request for Information (RFI)

Submit a formal RFI to the engineer detailing the situation. Clearly state your GF's reasoning, the intended use of the disconnect (only for equipment replacement), and the fact that there are no exposed live parts when de-energized. Request written clarification on why they are strictly interpreting the code this way. A well-written RFI forces the engineer to thoroughly consider the situation and document their rationale.3.

Enclosed Motor Rated Switch

This could be the most straightforward solution. Replacing the current disconnect with an enclosed, motor-rated disconnect that is suitable for installation in a damp location removes the possibility of live parts being exposed.4.

Physical Barrier

If relocation or switch replacement isn't feasible, consider a physical barrier to increase the clearance. A permanently installed, non-conductive barrier around the pipes that increases the clearance to 42" would satisfy the code. This barrier MUST be securely mounted and large enough to be effective.5.

Cover the Pipes

Covering the pipes with an insulation material, especially a non-conductive covering, might be sufficient to address the "grounded parts" aspect of Condition 2. However, the engineer might still argue that the metal pipes are still "grounded" even if covered.
6.


Local AHJ (Authority Having Jurisdiction)

Ultimately, the final decision rests with the local electrical inspector or AHJ. If you've exhausted all other options, and you are still at odds with the engineer, you may need to involve the inspector to get their opinion.

Important Considerations
OSHPD/HCAI

Since you are working on a project under California's OSHPD/HCAI, you will have a much more difficult time circumventing the code.*

Documentation

Document everything! Keep detailed records of all communication with the engineer, your GF, and any other relevant parties.

Recommendation:


Start with the RFI. A well-crafted RFI, along with a thorough hazard assessment, forces the engineer to fully consider the situation. If that doesn't work, the enclosed disconnect switch is likely the simplest and safest approach. Always prioritize safety and code compliance. Good luck! Flag for review

Previous Question Next Question