User: wwhitney, Location: Berkeley, CA
Asked on: Wednesday, August 21, 2024 at 1:21 pm EDT
Answered on: Thursday, March 6, 2025 at 1:27 am EST
Question: Say I have a 2 wire 120V circuit going to a piece of utilization equipment, and say there's no connection between the equipment and earth or any bonded metal (in particular no EGC).1) Can a non-faulty GFCI nuisance trip in this situation, and what is the physics by which this happens?2) Kirchhoff's current law is instantaneously obeyed at all points in time, yes? There aren't circuit elements that can say accumulate electrons during one part of the cycle and release them during another to actually introduce a difference in the currents in the two wires, right?3) So then I infer that certain aspects of the current waveform through the CT in the GFCI are able to induce a signal in the control circuitry even though the difference in the currents is always zero? E.g. high frequency harmonics?Thanks,Wayne
Let's break down your questions about GFCI behavior in a two-wire, ungrounded 120V circuit.1. Can a non-faulty GFCI nuisance trip in this situation, and what is the physics by which this happens?
Yes, a GFCI can nuisance trip in this situation, even without a ground fault in the traditional sense. Here's why: Capacitive Coupling
All conductors have some amount of capacitance to surrounding objects, including the environment and any enclosures. Even without a dedicated ground wire, the two conductors in the circuit (hot and neutral) have a small capacitive coupling to everything around them. This capacitance allows a small amount of current to flow from each conductor to the surrounding environment.
Crucially, the current from the hot wire and the neutral wire will not necessarily be exactly equal, even if the load itself is perfectly balanced. Impedance to Ground (or Lack Thereof)
Since there is no intentional ground connection, the impedance to ground is very high (essentially, whatever leakage impedance exists through the capacitive couplings). However, this impedance isn't infinite.
GFCI Threshold
A GFCI is designed to trip when the difference in current between the hot and neutral exceeds a very small threshold (typically 5mA in the US).
How it Happens
Because the capacitive couplings from hot and neutral to the environment are not identical, the current leaking from each conductor will not be equal. Even a tiny difference in these leakage currents can exceed the GFCI's trip threshold. The GFCI detects this difference as an imbalance and trips. Think of it as two leaky pipes. One leaks 4.998 amps, the other leaks 5.003 amps. The difference (0.005 amps or 5mA) is enough to trigger the GFCI.
Other Factors
The magnitude of capacitive leakage is affected by conductor length, proximity to grounded objects, humidity, and the characteristics of the load. Some loads are more prone to generating capacitive leakage than others.2.
Kirchhoff's current law is instantaneously obeyed at all points in time, yes? There aren't circuit elements that can say accumulate electrons during one part of the cycle and release them during another to actually introduce a difference in the currents in the two wires, right?
Yes, Kirchhoff's Current Law (KCL) is always obeyed. KCL states that the sum of currents entering a node (a point in a circuit) must equal the sum of currents leaving that node. This is a fundamental law of physics.Your statement about circuit elements accumulating and releasing electrons is essentially correct. A capacitor is the component that stores charge (electrons), and the rate of change of charge on the capacitor is the current. However, in a closed loop circuit, the current entering one side of the capacitor will always equal the current leaving the other side (even though there's a phase shift). So, a capacitor within the equipment does not itself cause an imbalance in the hot and neutral currents coming into the equipment. The imbalance is caused by the capacitances to external elements.3. So then I infer that certain aspects of the current waveform through the CT in the GFCI are able to induce a signal in the control circuitry even though the difference in the currents is always zero? E.g. high frequency harmonics?
This is partially correct, but it's not the difference being zero that's key. The GFCI trips on a difference in currents that is non-zero. High-frequency harmonics can certainly exacerbate nuisance tripping for a couple of reasons: Increased Leakage Current
Higher frequencies have a lower impedance path through capacitive couplings. Therefore, a load producing significant high-frequency harmonics will generate more leakage current through those capacitances to the environment. This increases the chances of exceeding the GFCI's trip threshold.
GFCI Sensitivity
Some GFCI designs may be more sensitive to certain frequencies than others. The design of the current transformer (CT) and the detection circuitry can influence its response to different frequency components.However, it's important to reiterate that the GFCI is reacting to a difference in current that exceeds its threshold, even if that difference is small and due to capacitive leakage amplified by high-frequency components. The GFCI doesn't trip just because high-frequency components are present if those components have the same magnitude of current in both the hot and neutral wires.
In summary: GFCI nuisance tripping in ungrounded circuits is primarily due to capacitive coupling between the conductors and the environment. This capacitive coupling allows small leakage currents to flow. If the difference in these leakage currents exceeds the GFCI's trip threshold (typically 5mA), it will trip. High-frequency harmonics produced by the load can increase leakage current through the capacitive couplings, making nuisance tripping more likely. KCL is always obeyed. There is no physical mechanism that could introduce a net charge in the device that would cause the currents to be imbalanced. The imbalance is always caused by connections to the outside environment. Flag for review