Topic: Transformer Capacity and Calculated load on Panelboards

User: aelec84, Location: Los Angeles

Asked on: Wednesday, August 21, 2024 at 3:23 pm EDT
Answered on: Thursday, March 6, 2025 at 1:27 am EST

Question: Hello Forum,I have a 45kva (480V-120/208V,3Ph,4w) transformer and it feeds a panelboard section#1 and 2 (MLO). It has a 150A, 3P MCB in the panelboard section#1 and section#2 is feed thru lugs. Both sections are rated for 225A. Overall calculated loads fed by transformer via (2) panelboards equate to 75kva but individual panelboard loads are under the bus and MCB rating of the panelboard. Would this be considered a code violation? Thank you.

Okay, let's break this down and address the potential code violations.

Understanding the Setup Transformer

45 kVA, 480V primary, 120/208V secondary, 3-phase, 4-wire.


Panelboard

A single panelboard with two sections. Section #1 has a 150A, 3-pole main circuit breaker (MCB). Section #2 has feed-through lugs (no main breaker).

Panelboard Rating

Both sections are individually rated for 225A.


Total Calculated Load

75 kVA for all loads connected to both sections of the panelboard. Individual section loads are less than the MCB and bus rating.

Potential Code Violations and Considerations


The most likely area of concern is overloading the transformer. Here's why:1. Transformer Overload

Your calculated load is 75 kVA, while your transformer is only rated for 45 kVA. This is a significant overload, and this is a major code violation.2.

NEC Article 450 (Transformers)
: NEC Article 450 governs transformer installation and protection. It emphasizes protecting the transformer from overcurrent. Here's what is crucial: 450.3(B) Overcurrent Protection (208V Secondary)

This section requires the transformer's secondary conductors to be protected, and that protection typically occurs at the transformer's secondary terminals (or as close as possible). While the 150A breaker in Section #1 provides
some protection, it doesn't adequately protect the transformer from being overloaded beyond its 45 kVA rating.3.

Panelboard Rating is Secondary

While the individual panelboard sections are rated for 225A, that rating is irrelevant
if the transformer supplying them is overloaded. Think of it this way: you can have a wide pipe (the panelboard sections), but if the pump (the transformer) can't supply enough water, the wide pipe doesn't matter.4.

NEC Article 220 - Load Calculations

The fact that your calculated load is 75 kVA strongly suggests you've followed the NEC Article 220 load calculation procedures. If that's the case, it reinforces the overloading issue.

Calculations
Transformer Secondary Current (Full Load)

kVA = (Volts Amps sqrt(3)) / 1000 45 kVA = (208V Amps 1.732) / 1000 Amps = (45 1000) / (208 1.732) Amps ≈ 125 Amps

Your Calculated Load (75 kVA)

Amps = (75 1000) / (208 1.732) Amps ≈ 208 Amps

Conclusion and Recommendations
Code Violation: Yes. Operating a transformer significantly above its rated kVA is a clear violation of the NEC and presents a serious safety hazard (overheating, fire risk, reduced equipment lifespan).

How to Correct the Situation

You have a few options, in order of preference:1. Replace the Transformer

This is the best and most reliable solution. Install a transformer with a kVA rating sufficient to handle your calculated load (75 kVA or greater). A 75 kVA or even a 100 kVA transformer would give you some headroom for future load growth. This requires redoing the overcurrent protection, conduit size, and wire size.2.

Reduce the Load

Identify and remove/relocate some of the connected loads to bring the total calculated load below the transformer's capacity (45 kVA). This might involve moving some circuits to another panelboard fed by a different transformer. This is often difficult and may impact operational needs.3.

Load Shedding/Interlocking (Complex and Requires Engineering)

This is the least desirable option and requires careful design. Implement a system that prevents certain loads from operating simultaneously, ensuring the transformer's capacity is never exceeded. This requires careful engineering and programming to ensure that the system operates reliably and safely. This option is generally more complex and costly.

Important Notes



Local Codes and Inspections

Always consult your local electrical codes and inspectors. They have the final say on what is acceptable in your jurisdiction.


Qualified Electrician

All electrical work should be performed by a qualified and licensed electrician.

Documentation

Keep accurate records of load calculations, transformer specifications, and all electrical modifications.


Diversity Factor:
If your load calculation uses a diversity factor (where you assume not all loads will run simultaneously), ensure that this is a realistic assumption and that the actual peak load does not exceed the transformer's capacity. Often, diversity factors are not appropriate for critical loads.Before doing any work, consult a qualified electrical engineer and a licensed electrician. They can perform a thorough load analysis, develop a safe and code-compliant solution, and obtain any necessary permits. Flag for review