Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Article 440

User: g-and-h_electric, Location: northern illinois

Asked on: Wednesday, August 21, 2024 at 10:22 pm EDT
Answered on: Thursday, March 6, 2025 at 1:28 am EST

Question: I need a bit of help . HVAC crew at the shop installed a new heat pump system. condenser was "size for size" btu wise.Existing unit was 4 ton wired with #10 THHN in EMT with (get this) a 20 Amp breaker. New unit wants a a minimum 42 Amp circuit, maximum breaker 45 Amp.Now for my problem The #10's wont pull out of the pipe (best guess is a buried box). It is in a finished basement, so there is no easy way to repipe things without the obvious drywall removal.Here is my question..... With a condenser load of 23 Amp (before any 125% factors), am I code compliant with the #10's on the 45? My interpretation is that I am, but I would like another opinion .Thank you.Howard

Okay, Howard, this is a tricky situation, and you're right to be concerned about code compliance. Let's break this down and get a clearer picture

Understanding the Code (Focusing on NEC - Assuming US Based)

The National Electrical Code (NEC) is the governing standard here, and we need to look at several sections: NEC 310.16 (Ampacity of Conductors)

This is the table that tells you the allowable ampacity of conductors based on their size, insulation type, and temperature rating. For #10 THHN, in a typical (30°C / 86°F) environment, it's generally rated for 30 amps.


NEC 440 (Air-Conditioning and Refrigerating Equipment)

This article specifically deals with the electrical requirements for AC and heat pump equipment. It supersedes general wiring rules in many cases.

NEC 440.22(A) (Air-Conditioning and Refrigerating Equipment – Branch-Circuit Selection Current)

This section addresses the concept of the "minimum circuit ampacity" (MCA) provided on the equipment's nameplate. It's a calculation that includes the compressor's rated-load current (RLA) or full-load amps (FLA) and the fan motor's current. The MCA is used to determine the proper conductor size.


NEC 440.22(B)(1) (Air-Conditioning and Refrigerating Equipment – Overcurrent Protection Selection)

This deals with sizing the overcurrent protection (breaker or fuse). Here's where it gets a little more complicated. The nameplate specifies a maximum overcurrent protective device (MOCP) for the equipment.

Analyzing Your Situation
1. Nameplate Data is Key

You've provided some critical numbers:

Condenser Load (presumably RLA or FLA)

23 Amps


Minimum Circuit Ampacity (MCA)

42 Amps

Maximum Overcurrent Protection (MOCP)

45 Amps2.

The Problem

Your existing #10 THHN, rated at 30 amps, is insufficient for the
minimum circuit ampacity of 42 amps.3.

Why the 20 Amp Breaker Before?
The old 20A breaker on 10 AWG wire does not meet code and would potentially damage the equipment.

Is it Compliant to Use #10 on a 45 Amp Breaker with a 23 Amp Load?
NO. It is NOT compliant, and it is very dangerous.Here's why



Overcurrent Protection

The 45-amp breaker is designed to protect the
wiring, not necessarily the equipment. Using a 45-amp breaker on a #10 wire creates a significant fire hazard. The wire can overheat and potentially cause a fire long before the breaker trips. The equipment is not meant to draw more amps than that of the rating of the wire, and therefore, the breaker may not ever trip, causing a fire hazard.

Minimum Circuit Ampacity (MCA)

The manufacturer has determined that the minimum ampacity for the circuit is 42 amps. This means that even if the compressor only draws 23 amps at a given moment, the circuit must be capable of handling 42 amps to account for starting currents, other loads (like the fan), and variations in operating conditions. You must use wiring rated for at least the MCA.

Your Options (None of them are ideal without rewiring)
1. Bite the Bullet and Rewire

This is the correct solution. It's the safest and most code-compliant. You'll need to run new conductors (likely #6 AWG copper, but confirm with a qualified electrician and the NEC tables) in the existing conduit, if possible, or run new conduit. I realize you're trying to avoid drywall damage, but the risk of fire is not worth it. Consider hiring a skilled electrician who is experienced in fishing wires and minimizing drywall damage. They may have techniques and tools to make the job less invasive.2.

Consider a Different Unit

In the very unlikely event that the manufacturer will exchange the unit for one with a lower MCA, the most simple solution is to get a smaller compressor. However, this would be an absolute last resort and may not be possible at all. And it depends if the new unit could heat and cool the home properly.

Important Considerations
Local Codes

Always check with your local building department or a licensed electrical inspector. They may have amendments to the NEC or specific requirements in your area.


Licensed Electrician

This is not a DIY project. Hire a qualified, licensed electrician to evaluate the situation and perform the work. They have the knowledge, experience, and insurance to do the job safely and correctly.*

Documentation

Keep all documentation related to the installation, including permits, inspection reports, and the equipment nameplate information.

In summary, using #10 wire on a 45-amp breaker, with a 42-amp MCA requirement, is a dangerous and code-violating practice. You need to rewire the circuit with appropriately sized conductors.
Flag for review

Previous Question Next Question