User: cppoly, Location: New York
Asked on: Thursday, August 22, 2024 at 7:35 am EDT
Answered on: Thursday, March 6, 2025 at 1:28 am EST
Question: Paraphrasing here from 2023 NEC:In 110.26 Spaces About Electrial Equipment, it says all electrical equipment requires working space, access to, and egress from.In 110.26(A) Working Space, it says equipment likely to become energized has to follow the depth clearances listed in the chart.Taking the wording literally from 110.26, can the term "Working Space" used in 110.26 be confused with the "Working Space" used in 110.26(A)?
Yes, the wording in NEC 110.26 can be confusing because it uses the term "Working Space" in two slightly different ways.Here's a breakdown of why and how: 110.26 (General) This section discusses "Spaces About Electrical Equipment" in general, and lists three basic requirements: working space, access, and egress. Here, "working space" refers to the overall area around the equipment that allows for safe operation, maintenance, and inspection. It's a broad concept. 110.26(A) (Specific) This section, titled "Working Space," defines the minimum clearances (depth, width, and height) required in front of equipment that is likely to become energized while being worked on. This section uses "Working Space" in a more specific, quantitative way – referring to the chart of minimum clearance depths.The key is that 110.26(A) further defines one aspect of the "working space" mentioned generally in 110.26. All three conditions, access, egress, and working space, apply to all equipment covered under 110.26. In addition to these three conditions, if the covered electrical equipment is likely to become energized while being worked on, the working space must also adhere to the depth clearances specified in the clearance tables in 110.26(A).
In summary
General "Working Space" (110.26)
A broad concept including enough room for safe operation, maintenance, inspection, access, and egress.
Specific "Working Space" (110.26(A)): The measured minimum clearance depths (and widths and heights) required for specific equipment that is likely to be energized. This is a subset of the general working space, and a mandated minimum clearance depth requirement that depends on voltage to ground, condition, etc.Therefore, it is easy to get confused, especially when first learning the code. The NEC could benefit from using different terminology or adding clarifying language.The best approach is to always consider the context. When you see "Working Space" in 110.26(A), think about the measured clearances. When you see "Working Space" in 110.26 generally, think about the overall area needed for all aspects of safe work.So, to answer your question directly: yes, the term "Working Space" can be confusing because it's used in a general sense in 110.26 and then in a more specific, quantitatively defined sense in 110.26(A). Flag for review