Question: Is warning tape placed 12” above the buried conductors only required for Service conductors ?I have a feeder that goes from a garage to a house.It supplies the house power.Inspector is requiring the ribbon tape be installed.I don’t have a problem doing it and it does add protection if anyone digs on the property without having marking done.I just don’t think it’s a requirement per the code.Am I correct?
You are correct. The NEC only requires warning ribbon for specific types of underground installations, and generally it's not required for standard feeder conductors.Here's the breakdown: NEC 300.5(D)(3) Protection from Damage: This section of the NEC covers requirements for underground installations and includes requirements for warning ribbon. Warning Ribbon Requirement: The NEC requires warning ribbon for underground installations that meet specific conditions, such as Direct-Buried Cable or Conduit Installed in a Trench. Service Conductors Exception: The exception to placing warning ribbon is in 230.5(5). This permits conductors without a grounding conductor to be buried at 18" deep without concrete pad or warning ribbon.
Key Considerations
Local Amendments
Local jurisdictions (city, county, etc.) can amend the NEC. It's possible your inspector is enforcing a local amendment that does require warning ribbon for all buried conductors, regardless of voltage or whether they are service conductors or feeders.
Recommendation
Ask the Inspector for the Specific Code Reference
The best course of action is to politely ask the inspector for the specific NEC (or local) code section that requires the warning ribbon for your feeder conductors. This will clarify whether they're citing a local amendment or interpreting the NEC in a way that differs from common understanding.2.
Check Local Codes
Even if the inspector can't provide a specific reference, double-check your local building codes and electrical codes. Look for amendments to the NEC that might add requirements for buried conductors.3.
Comply if Necessary
If the inspector is citing a valid local code, you'll need to comply. While you might not agree with it, following the inspector's direction is generally the best way to get the installation approved.
In Summary: The NEC doesn't generally require warning ribbon for feeder conductors buried per 300.5(D)(3). Local amendments can change this.* Get clarification from the inspector and check local codes.Good luck! Flag for review