Question: Good morning. I’m working on an apartment complex that has about 200 units. The electrical inspector failed us because we didn’t have a bonding bushing on the electrical panels( sub panels). We have SERs with Romex connectors. I thought we were in compliance. SERs are not raceways, what did I miss? He made us install bonding bushings to all sub panels.Thanks in advance
Good morning! I understand your frustration. The bonding requirements for service-entrance cable (SER) and subpanels can be tricky, especially when dealing with metallic enclosures. Here's a breakdown of why the inspector might have required bonding bushings, even though SER isn't considered a raceway, and what specific code sections likely apply
Why the Inspector Likely Required Bonding Bushings
The key issue revolves around ensuring proper grounding and bonding of the metallic enclosure (the subpanel itself) to provide a low-impedance path for fault current back to the source. This is essential for the operation of overcurrent protection devices (breakers) during a fault, preventing dangerous voltage from appearing on the enclosure. Metallic Enclosure Bonding
Even if SER isn't a raceway, the subpanel enclosure itself is a metallic enclosure that needs to be properly bonded. The point where the SER enters the panel is a potential point of entry for fault current onto the enclosure.
Improper Connection
Romex connectors are generally not listed for grounding or bonding purposes. Relying solely on the mechanical connection of a Romex connector to the panel enclosure isn't considered a reliable, low-impedance bonding path. It's not designed to handle fault currents.
Grounding vs. Bonding
It's important to distinguish between grounding and bonding. Grounding connects the electrical system to earth, providing a reference point. Bonding connects metallic parts to create a continuous, low-impedance path for fault current. The bonding bushing helps ensure this continuous, low-impedance path to the panel enclosure.
Relevant National Electrical Code (NEC) Sections (2020 or 2023, depending on your local adoption)
These are the sections the inspector likely used to justify the requirement:
250.4(A)(5) Bonding of Electrically Conductive Materials and Other Equipment
"Electrically conductive materials that are likely to become energized shall be connected together electrically to create a low-impedance circuit that facilitates the operation of overcurrent devices." This is a fundamental principle.
250.92 Equipment Likely to Become Energized
This section deals with bonding equipment that could become energized, including metallic enclosures.
250.96 Bonding Other Enclosures
"(A) General. Metal raceways, cable trays, cable armor, cable sheaths, enclosures, frames, fittings, and other metal non-current-carrying parts that are to serve as grounding conductors, with or without the use of supplementary equipment grounding conductors, shall be effectively bonded where necessary to ensure electrical continuity and the capacity to conduct safely any fault current likely to be imposed on them."
250.97 Bonding for Over 250 Volts
This section might apply if your apartment complex's voltage exceeds 250 volts to ground. It generally requires more robust bonding methods.
312.5(C) Cables
This section often addresses how cables entering enclosures are handled. Even though SER isn't a raceway, the method of entry still needs to provide adequate grounding/bonding.
314.4 Metallic Boxes
This section applies to junction boxes but offers guidance that extends to other metallic enclosures. (C) "Where a locknut and bushing connection is used to connect a conduit or cable to a metallic box, a bonding jumper shall be installed to the box." Although you're using SER, the principle of needing a bonding jumper when relying on a locknut/bushing connection is similar.
Why Bonding Bushings Were Installed
Bonding bushings provide a reliable, low-impedance connection between the SER cable's metal armor (if it has it) and the metal enclosure of the subpanel. They are specifically designed for this purpose. They have a setscrew that bites into the metal enclosure, creating a good electrical connection. The SER cable's grounding conductor is then connected to the bonding bushing's lug.
Compliance Solutions and Discussions with the Inspector Bonding Jumpers
An alternative to bonding bushings might be to use a bonding jumper from the SER grounding conductor terminal to a grounding screw directly on the subpanel enclosure. However, this is often less desirable as it's typically less robust and not as clearly compliant.
Review the Local Code
Double-check your local electrical code. Some jurisdictions have amendments or interpretations that can influence the requirements.
Discuss with the Inspector
It's always best to have a conversation with the electrical inspector to understand their specific concerns and ensure you're meeting their requirements. Ask them to point to the exact code sections they are enforcing. Politely discuss alternative bonding methods and their advantages/disadvantages.*
SER with Integral Ground
Ensure the SER cable itself has an adequately sized grounding conductor running inside the cable. This grounding conductor is what ultimately provides the fault current path.
In summary, even though SER isn't a raceway, the metallic enclosure of the subpanel still needs to be properly bonded to ensure a low-impedance fault current path. Relying on Romex connectors alone is generally not sufficient to meet this requirement.
I hope this explanation helps! Remember to consult with your local electrical inspector and a qualified electrician to ensure compliance with all applicable codes. Good luck with your project! Flag for review