User: Ricky A, Location: Texas
Asked on: Thursday, August 22, 2024 at 1:54 pm EDT
Answered on: Thursday, March 6, 2025 at 1:30 am EST
Question: I will be installing a 75 kva 3 phase s/u xfmr, 240 hi-leg primary to 480/277 secondary. it will supply power for a glycol chiller located 60 feet from xfmr equip. Do I need both pri and sec protection and what size?
Okay, let's break down the transformer protection requirements for your 75 kVA, 240V Delta (High-Leg) to 480Y/277V Wye transformer installation feeding a glycol chiller. Since you have both primary and secondary conductors and equipment that will need protection, you will need OCPD for both.
Understanding Transformer Protection - NEC Requirements
The National Electrical Code (NEC) provides specific guidelines for transformer protection. The general principle is to protect the transformer from overcurrent on both the primary and secondary sides. The methods differ slightly based on the application and the impedance of the transformer. NEC 450 is the key section to review.1. Primary Protection
Purpose
Protects the primary winding and the primary feeder conductors from overcurrent events originating on the secondary side (e.g., a short circuit in the chiller).
General Rule
NEC 450.3(B) covers transformer overcurrent protection over 600V, nominal. NEC 450.3(A) covers transformers 600V or less.
Your Situation (240V Primary - 600V or less)
NEC 450.3(A) is applicable. 450.3(A) allows options to protect the primary either at 125% of the transformers primary current, or 250% of the transformers primary current. Note that this is the OCPD protecting the transformer; the conductors feeding the transformer need to be sized appropriately.
Calculating Primary Current
kVA = (Volts Amps √3) / 1000 75 kVA = (240V Primary Amps √3) / 1000 Primary Amps = (75 kVA 1000) / (240V √3) = 180.4 Amps
Primary OCPD Sizing Options
125% Rule
180.4 Amps 1.25 = 225.5 Amps. You would use the next higher standard size overcurrent device, which is
250A. 250% Rule
180.4 Amps 2.50 = 451 Amps. You would use the next higher standard size overcurrent device, which is
450A.
Which Option to Choose for the Primary?
The 250% rule typically allows for the transformer's inrush current (the temporary high current when it's energized). However, a lower value like 125% can provide better protection against sustained overloads. Recommendation
Start with the 125% option (225A, using a 250A OCPD) as this offers tighter protection. If you experience nuisance tripping on transformer energization, you may have to increase the OCPD. However, before increasing the primary OCPD, you must verify that your transformer has an over-temp device and your conductors can handle the current.
2. Secondary Protection
Purpose
Protects the secondary winding, the secondary feeder conductors to the chiller, and the chiller itself from overcurrent.
General Rule
NEC 450.3(A) applies to transformers 600V or less.
Calculating Secondary Current
75 kVA = (480V Secondary Amps √3) / 1000 Secondary Amps = (75 kVA 1000) / (480V √3) = 90.2 Amps
Secondary OCPD Sizing Options
125% Rule
90.2 Amps 1.25 = 112.75 Amps. You would use the next higher standard size overcurrent device, which is
125A. 250% Rule
90.2 Amps 2.50 = 225.5 Amps. You would use the next higher standard size overcurrent device, which is
250A.
Which Option to Choose for the Secondary?
A lower value OCPD (125%) on the secondary will allow for a smaller feeder conductor size, so it makes sense to stick with that sizing method. Recommendation
Install a
125A overcurrent protective device on the secondary side of the transformer. This provides better protection for the conductors and the chiller.3. Conductor Sizing
Primary Conductors
Must be rated to at least 125% of the primary current (180.4 Amps 1.25 = 225.5 Amps). Select conductors rated for at least 225.5 Amps, considering ampacity correction factors for temperature and conduit fill. Refer to NEC Table 310.16 and related articles. Copper THHN conductors for this would need to be sized at minimum #3/0 AWG
Secondary Conductors
Must be rated to at least 125% of the secondary current (90.2 Amps 1.25 = 112.75 Amps). Select conductors rated for at least 112.75 Amps, considering ampacity correction factors. Copper THHN conductors for this would need to be sized at minimum #2 AWG.
Grounding
Proper grounding is critical. Establish a good grounding electrode system and bond the transformer enclosure and all metallic raceways and enclosures according to NEC Article 250.
4. Glycol Chiller Considerations
Nameplate FLA
Check the Full Load Amps (FLA) rating on the glycol chiller's nameplate. The chiller's overcurrent protection should be based on the chiller's FLA, as per NEC Article 430 (Motors, Motor Circuits, and Controllers). The chiller might have internal overload protection.
Chiller Disconnect
Install a disconnect switch at the chiller location for servicing. This disconnect should be properly sized based on the chiller's nameplate data.
Summary of Recommended Protection
Primary
250A overcurrent device (fuse or circuit breaker). Size conductors for at least 225.5 Amps.
Secondary
125A overcurrent device (fuse or circuit breaker). Size conductors for at least 112.75 Amps.
Glycol Chiller
Overcurrent protection and disconnect sized according to the chiller's nameplate and NEC Article 430.
Important Notes
High-Leg Delta
Be extremely careful when working with a high-leg delta system. The voltage from the high leg (B-phase) to neutral is not 277V. It is typically around 208V. Clearly mark the high leg.
Coordination
Ideally, perform a coordination study to ensure that the overcurrent devices are properly coordinated to minimize nuisance tripping and maximize system protection. This is especially important for larger or more complex systems.
Local Codes
Always check with your local electrical inspector for any specific requirements or amendments to the NEC that may be in effect in your jurisdiction.*
Qualified Electrician
This information is for guidance only. Transformer and electrical system installations should be performed by a qualified and licensed electrician who is familiar with the NEC and local codes.
Disclaimer: Consult with a qualified electrician or electrical engineer for a complete and code-compliant design for your specific installation. Flag for review