Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Secondary Feeder from Step-Dn to Panel

User: Aistobasbistoc9, Location: Texas

Asked on: Thursday, August 22, 2024 at 3:33 pm EDT
Answered on: Thursday, March 6, 2025 at 1:31 am EST

Question: I'm having a hard time understanding what the actual requirements are per NEC.The step down (480-208, 3PH) transformer GEC is sized per NEC 250.102(C)(1) of the secondary, supply side OCPD.The secondary feed to the 208 panel is sized for GEC per NEC 250.102(C)(1) as well, not EGC as it typically would be sized for.For example, 175A breaker from 480 panel to transformer. Secondary OCPD (208 panel) is sized at 400A. Ground on transformer is sized #1/0 per NEC 250.102(C)(1). The secondary to the 400A, 208 panel is sized with #1/0 gnd. instead of #3.If any of this is incorrect, please let me know. This is my understanding currently. I have usually sized secondary per EGC requirement, not GEC, and have also seen it this way on many electrical plans. However, I recently got dinged by the building department for not sizing the secondary feeder ground as GEC and would like a clear answer on why.Thank you!

Okay, let's break down the grounding requirements for your 480V-208V transformer and clear up the confusion. You're very close to understanding it, but some nuances in the NEC are causing the conflict. The inspector is technically correct, but the "why" can be better explained.

Here's the breakdown, using your example



1. Transformer Grounding Electrode Conductor (GEC)



Location

This is the conductor that connects the transformer's neutral point (X0 bushing on a typical delta-wye transformer) to a grounding electrode (ground rod, building steel, etc.).


NEC Section

250.30(A)(6)

Sizing

This is sized based on the

secondary conductors
of the transformer, not the primary protection. Specifically, the derived ungrounded conductors based on Table 250.102(C)(1). Your example

You have a 400A OCPD, therefore you will size the GEC to 1/0 AWG.

2. Grounding Electrode (Electrode System)



NEC

250.50 and 250.52


Examples

Building steel (effectively grounded), a ground ring, a concrete-encased electrode (Ufer ground), a ground rod, etc. Local codes often specify which are acceptable or required.

Important

You
must connect the transformer's neutral (X0) to a grounding electrode or electrode system. This is what creates the "separately derived system."

3. Supply-Side Bonding Jumper (SSBJ)



NEC Section

250.30(A)(1)

Definition

This conductor connects the transformer's neutral point to the transformer enclosure and to any other equipment likely to become energized. Often a bare or green conductor inside the transformer itself, connecting the neutral bushing to the enclosure ground lug.


Sizing

Sized according to Table 250.102(C)(1) based on the derived ungrounded conductors of the transformer.

Your Example

In your example, you have a 400A OCPD, therefore you will size the GEC to 1/0 AWG.

4. Feeder to the 208V Panel (including the grounding conductor)



NEC 250.30(A)(1)

Requires an equipment grounding conductor to be run with the circuit conductors from the separately derived source (transformer) to the first disconnecting means or overcurrent device (your 400A panel). The size of this EGC is determined by Table 250.122, based on the OCPD protecting the circuit conductors. This does not refer to the transformer GEC but to the grounded EGC from the transformer to panel board.

NEC Section for EGC Sizing

250.122


Sizing

This is where the confusion often arises. This conductor is acting as the

Equipment Grounding Conductor (EGC)
for the feeder. It is sized according to Table 250.122, based on the rating of the overcurrent protection device protecting the feeder conductors (your 400A breaker). Your example

For a 400A overcurrent device, Table 250.122 requires a

#3 AWG copper
EGC. This is where you are typically accustomed to sizing the secondary ground.The Point of Confusion and Why the Inspector is (Technically) Correct

The building department is likely looking at the

"or larger"
language in 250.30(A)(1). It states that the feeder's EGC must be sized according to 250.122 or not smaller than the GEC required by 250.30(A)(6). In your example, the GEC required by 250.30(A)(6) is #1/0 AWG, based on Table 250.102(C)(1) for the secondary conductors. The EGC required by 250.122 for the 400A feeder is #3 AWG. Therefore, because the GEC size is larger, it must be used as the minimum size for the feeder to the panel.Summary and Clarification1. Transformer Grounding Electrode Conductor (GEC)

Size based on the
secondary conductors per Table 250.102(C)(1) per NEC 250.30(A)(6). Connects to the grounding electrode system.
2.


Supply-Side Bonding Jumper (SSBJ)

Size based on the
secondary conductors per Table 250.102(C)(1). Bonds the neutral to the transformer enclosure.
3.


Feeder EGC to the Panel

Normally, size according to Table 250.122, based on the overcurrent protection device.

However,
250.30(A)(1) requires the feeder EGC to be no smaller than the GEC from the transformer.4. The Inspector's View

The inspector is requiring you to follow the more stringent requirement of NEC 250.30(A)(1), ensuring that you use at least the same size conductor as the GEC for the feeder EGC.

In your example, here's the CORRECT sizing



Transformer GEC

#1/0 AWG (Based on 400A Secondary OCPD - Table 250.102(C)(1) and 250.30(A)(6))

Supply-Side Bonding Jumper

#1/0 AWG (Based on 400A Secondary OCPD - Table 250.102(C)(1) and 250.30(A)(1))


Feeder EGC to 208V Panel

#1/0 AWG (Because it must be no smaller than the GEC, even though Table 250.122 only requires #3 AWG)

Key Takeaways

The NEC is trying to ensure a robust ground fault current path from the 208V panel back to the transformer. While it might seem redundant to use a larger EGC than required by Table 250.122, 250.30(A)(1) is a clear directive.*

Always check with your local building department or engineer of record for specific interpretations and requirements in your area.


I hope this detailed explanation helps clarify the situation and provides you with a solid understanding of the NEC requirements. Let me know if you have any more questions! Flag for review

Previous Question Next Question