Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: RTU with MOP (Fuse Size) vs NEC 110.3B

User: arc_flashed, Location: FL, United States

Asked on: Thursday, August 22, 2024 at 4:50 pm EDT
Answered on: Thursday, March 6, 2025 at 1:31 am EST

Question: I have a situation where customer has an existing distribution panel that is all circuit breakers. They have ordered new roof top air units for cooling and I just received a screen shot of the electrical requirements. The max overcurrent is listed as "MOP (Fuse Size)". I have asked if they can provide a picture of the unit nameplate but I do not believe they have any of the units yet.My question is, would using the existing breaker panel violate NEC 110.3(B) based on the information given by the vendor paperwork?This was their plan all along and I want to be sure before I say anything about needing fused disconnects.

Okay, let's break down this situation and address your concerns about NEC 110.3(B).

Understanding the Situation You're installing new rooftop HVAC units. The vendor specs state "MOP (Fuse Size)" for overcurrent protection. The existing panel is all circuit breakers. The customer wants to use the existing panel (with breakers) to feed the new units. You're concerned about NEC 110.3(B) compliance.

NEC 110.3(B) - The Key Rule

NEC 110.3(B) states:
"Listed or labeled equipment shall be installed and used in accordance with any instructions included in the listing or labeling."In simple terms: If the equipment is listed (and almost all modern electrical equipment is), you MUST follow the manufacturer's instructions for installation and use.

Analysis of Your Situation

Here's how NEC 110.3(B) applies to your case:1. Manufacturer's Instructions (The "MOP" Spec)

The vendor providing the "MOP (Fuse Size)" specification is essentially giving you an instruction for overcurrent protection. "MOP" typically stands for

Maximum Overcurrent Protection
. While it
doesn't explicitly forbid breakers, it does specify a fuse size for maximum protection.2. Violation Potential



If the manufacturer specifies a
fuse size for maximum overcurrent protection, using a circuit breaker might violate NEC 110.3(B) UNLESS you can demonstrate that the circuit breaker provides EQUIVALENT or BETTER protection than the specified fuse size. This is where it gets nuanced.3. Why Fuses Are Sometimes Preferred by Manufacturers



Precise Coordination

Fuses can be more easily coordinated with the motor's starting characteristics to prevent nuisance tripping during inrush current, while still providing adequate overcurrent protection.

Specific Motor Protection

Some motors (especially those with thermal overload protection integrated) are specifically designed to be protected by fuses with certain time-delay characteristics.


UL Listing/Compliance

The rooftop unit's UL listing (or other listing agency) may be based on the fuse being used as the overcurrent protective device. If the tested configuration uses a fuse, that's what's required to maintain the listing.

Available Short Circuit Current Rating

If the available short circuit current is higher than the breaker AIC rating, fuses may be required.

Your Next Steps - Critical Actions
1. GET THE NAMEPLATE! This is the most important thing. You need the full nameplate information from the rooftop units. The nameplate will have specific overcurrent protection requirements that are binding under NEC 110.3(B). Do not proceed further without this.2. Review the Nameplate Data Carefully

Look for the following on the nameplate:


"Maximum Overcurrent Protection" (or similar wording) - AND the type of overcurrent device allowed (fuse, breaker, HACR breaker, etc.).
Minimum Circuit Ampacity (MCA)

This determines the minimum size of your conductors.


Short Circuit Current Rating (SCCR)

This information is critical for understanding how to achieve the required SCCR and to be code compliant.

Any Notes or Restrictions

The nameplate might have specific requirements or limitations.3.

If the Nameplate Confirms "Fuse Only"

If the nameplate states
only a fuse size for maximum overcurrent protection, using a breaker without written approval from the manufacturer will likely be a violation of NEC 110.3(B).
4.


Consider a Variance/Engineering Justification (If Breakers Are Desired)

If you
really want to use breakers (and the nameplate seems to allow it, or is unclear), you need to demonstrate through engineering analysis that the selected circuit breaker provides equivalent or superior protection to the specified fuse. This might involve:

Coordination Study

A professional engineer can perform a coordination study to show that the breaker will trip properly under both overload and short-circuit conditions, and that it's coordinated with the motor's starting characteristics.

Manufacturer Documentation

Obtain documentation from the breaker manufacturer showing that the selected breaker is suitable for motor protection and meets or exceeds the performance of the specified fuse.


AHJ Approval

Ultimately, the Authority Having Jurisdiction (AHJ - the electrical inspector) has the final say. You'll need to present your justification and get their approval.5.

Communicate with the Manufacturer

Talk to the manufacturer of the rooftop units. Explain your situation and ask if they have any specific reasons why fuses are required. They might have a list of approved breakers or a written statement allowing breakers under certain conditions. Get this in writing.6.

Consider Fused Disconnects

If the nameplate clearly requires fuses, the easiest and most code-compliant solution is to install fused disconnects adjacent to the rooftop units. These disconnects would be fed from the existing breaker panel.

In Summary


You are right to be concerned. It's highly likely that installing the units using the existing breakers may be a violation of 110.3(B). The key is the manufacturer's instructions as given on the equipment nameplate. Get the nameplate info, review it carefully, and talk to the manufacturer. If fuses are required, install fused disconnects. If you want to use breakers, you'll need a strong justification and likely AHJ approval. Flag for review

Previous Question Next Question