Topic: 2020 NEC: is there any minimum amp rating requirements for feeder breakers of a residential condo?

User: fandi, Location: Los Angeles

Asked on: Thursday, August 22, 2024 at 5:16 pm EDT
Answered on: Thursday, March 6, 2025 at 1:31 am EST

Question: Hello All,The main panel that feeds the entire condo is being replaced with new but the subpanels of the condo units are existing. In 2020 NEC, is there any minimum amp rating requirements for the new feeder breakers at the new main panel of an existing residential condo?Thank you.

Okay, let's break down the requirements for feeder breaker sizing in this scenario under the 2020 NEC, focusing on the specific nuances of a condo building with existing subpanels.

Key Considerations & Relevant NEC Sections



Existing Installation

Because you're working with an existing installation, the NEC permits you to keep the existing subpanels if they are safe and in good working condition. However, the
new feeder to those panels must be appropriately sized to handle the load.

Load Calculation (Article 220)

This is the core element. The NEC requires you to perform a load calculation to determine the minimum feeder ampacity. You cannot simply match the existing breaker size unless that size is demonstrated to be adequate by a proper load calculation.

Demand Factors

For dwelling units (like condos), the NEC allows you to apply
demand factors (reductions) to some loads. These are found in Article 220, specifically Part III. These factors recognize that not all appliances and loads will be operating at their maximum simultaneously.

125% Rule (210.20(A))

for continuous loads such as EV Chargers, the branch-circuit, feeder, and service conductors and overcurrent protection shall have an ampacity not less than 125% of the continuous load.

Feeder Conductor Ampacity (215.2)

The feeder conductors must have an ampacity
not less than the calculated load per Article 220.

Overcurrent Protection (240.4)

The feeder overcurrent protection (the breaker) must protect the feeder conductors. Typically, you choose a breaker size that is the next standard size above the ampacity of the conductors, unless specific exceptions apply (e.g., tap rules, motor circuits). Note: Be mindful of conductor ampacity limits found in Table 310.16 and correct for termination temperature ratings, as necessary.

Steps to Determine Minimum Feeder Breaker Size


Gather Information for Each Condo Unit



Subpanel Rating

Note the ampacity rating of the existing subpanel. This does
not dictate the feeder breaker size but gives you an upper limit if the subpanel is small.

Appliance Inventory

A comprehensive list of all appliances (ranges, ovens, cooktops, water heaters, HVAC equipment, dishwashers, disposals, washing machines, dryers, etc.). Note their nameplate ratings (volts, amps, watts).

General Lighting and Receptacle Load

You'll need to estimate the general lighting and receptacle load. This is typically done based on the square footage of the condo unit (see 220.12 and Table 220.12). There is a minimum VA/square foot requirement.


Fixed Appliance Load

This includes things like built-in microwaves, garbage disposals, etc. that are not part of the general receptacle load.

Heating and Air Conditioning

Get the nameplate data from the HVAC equipment.


Electric Vehicle (EV) Charger

Determine the ampacity and whether it is a continuous load2.

Perform Load Calculation (Article 220)



General Lighting and Receptacle Load (220.12)

Calculate the VA based on square footage.


Small Appliance and Laundry Circuits (220.14(H))

Add 1500 VA for each 20-amp small appliance circuit (kitchen countertop receptacles) and 1500 VA for the laundry circuit.

Fixed Appliances (220.14)

Add the nameplate VA of fixed appliances.


Ranges and Ovens (220.55)

This section has specific rules for calculating the demand load of electric ranges and ovens. Table 220.55 is often used.

Heating and Air Conditioning (220.82)

Calculate the larger of the heating or cooling load. There are different methods depending on the type of HVAC system.


Electric Vehicle (EV) Chargers (625.41)

Determine the load from the EV Charger, which is considered a continuous load if rated for 3 hours or more.

Apply Demand Factors (Article 220, Part III)

This is where you can reduce the calculated load based on the number of units and the types of loads. For example, you can apply demand factors to ranges and dryers when there are multiple units.3.

Calculate Total Calculated Load (in Amps)

Sum up all the individual load components (after applying demand factors). Divide the total VA by the voltage (typically 240V for a single-phase dwelling unit). This gives you the total calculated load in amps.4.

Determine Minimum Feeder Conductor Ampacity (215.2)

The feeder conductors must have an ampacity equal to or greater than the calculated load.5.

Select Feeder Overcurrent Protection (240.4)

Choose a standard breaker size that protects the feeder conductors. The breaker size is usually the next standard size above the conductor ampacity (unless an exception applies).6.

Consider Subpanel Ampacity

The feeder breaker size cannot exceed the ampacity rating of the existing subpanel. If the calculated load requires a breaker larger than the subpanel rating, you may need to upgrade the subpanel as well.

Example (Simplified)

Let's say, after performing a load calculation for one condo unit, you determine the total calculated load to be 85 amps. You would need feeder conductors with an ampacity of at least 85 amps. You would likely use a 90 amp breaker (the next standard size above 85 amps) to protect the conductors, provided the wire ampacity allows.

Important Considerations



Accessibility

Ensure that the new main panel and all overcurrent devices are readily accessible (as defined by the NEC).


Working Space

Provide adequate working space around the new main panel (110.26).

Labeling

Properly label all circuits at the new main panel.


Local Codes

Always check with the local electrical inspector for any local amendments or requirements that may differ from the NEC. The local AHJ (Authority Having Jurisdiction) has the final say.

Professional Expertise

This type of work
requires* a qualified and licensed electrician who is familiar with the NEC and local codes. Do not attempt this work yourself unless you are properly qualified.

In summary, there is no single minimum amp rating requirement for the feeder breakers without performing a load calculation. The minimum size is driven by the calculated load of each condo unit, as determined by Article 220 of the NEC, ensuring that the feeder can safely handle the expected load.
Disclaimer: This information is for general guidance only and should not be considered a substitute for professional advice from a qualified electrician and/or electrical engineer. Always consult with a licensed professional to ensure compliance with the latest NEC and local codes. Flag for review