Topic: Fire Alarm Design in Existing Mixed Use Building

User: Tainted, Location: New York

Asked on: Thursday, August 22, 2024 at 9:51 pm EDT
Answered on: Thursday, March 6, 2025 at 1:32 am EST

Question: In New York City I am working on a very complex existing mixed use 3 section building, they share all utilities with each other. The commercial space and residential building share the same sprinkler service and fire pump. Each section of the building has one commercial store on the 1st floorSection 1 and 3 of the building has no fire alarm control panel that monitors the commercial space but has a pull station in residential lobby door from the existing old non-addressable fire alarm located in section 2 of the building.Section 2 of the building has an old non-addressable illegal fire alarm panel that monitor the residential portions and it is not up to code and I am replacing it. There is a separate legal fire alarm panel that monitors the commercial space in this section only.I found this bulletin which tells us how to deal with situations like this:https://www.nyc.gov/site/fdny/news/b1215/office-technology-management-bulletin-12-1-2015#/0In advisory #2 it says "Interconnect fire alarm systems for alarm activation, may comprise one system with multiple fire alarm panels(FCC’s) for separately designed and/or demised occupancies"What do they mean when they say "may comprise of one system with multiple fire alarm panels"? Aren't multiple fire alarm panels more than one system? How can one system comprise of multiple fire alarm panels?I am doing the design for only residential portion of the 3 section building. I honestly don't know if I am obligated to do the commercial spaces.

You've hit on a common point of confusion with fire alarm systems in interconnected buildings. Let's break down what the FDNY bulletin is likely trying to convey and how it applies to your project

Understanding "One System with Multiple Fire Alarm Panels"
The Key Concept: A Single, Coordinated Fire Alarm System The bulletin is emphasizing that even though you have physical panels in different locations, all the panels can be programmed to act in a synchronized fashion as one system for overall fire protection. Multiple Panels, Unified Operation

The bulletin indicates that all 3 commercial spaces and residential should be part of the overall fire alarm system. This means when one panel detects a fire (from any device in the sections/occupancies), it can trigger alarms, notifications, and other actions across the entire complex, as needed by code and the building's fire safety plan.

The "System" vs. "Panel" Distinction



Panel

The physical piece of equipment that receives signals from detectors, initiates alarms, and controls outputs.

System

The entire network of panels, devices (detectors, pull stations, horns, strobes, etc.), wiring, programming, and monitoring that work together to provide fire protection. One
system can use multiple fire alarm control panels (FACPs/FCC's) to achieve comprehensive coverage, especially in large or complex buildings.

Why Use Multiple Panels in One System?
Addressable system Limitations

A single fire alarm control panel (FACP) typically has limitations in the number of devices it can support. By using multiple panels, you can accommodate the total number of fire alarm devices present in the entire complex.

Wiring Distances and Topology

The building layout might require multiple panels to minimize wiring distances, simplify installation, and improve signal integrity. (especially in non-addressable)


Phased Installation

With multiple panels it facilitates phased installation as you are only replacing the residential section 2 panel only.

Compartmentalization

Depending on the building's construction and occupancy separations, having separate panels allows for more targeted alarm responses. For instance, an alarm in the commercial space in Section 1 might trigger a general alarm in Section 1 and Section 2 but only a specific alert for the fire department to minimize disruption in Section 3.

Your Situation and the Bulletin


Legal Responsibility

Your scope of work is limited to the residential portions. However, given the shared utilities and the FDNY's encouragement of system interconnectivity, you should have the design reviewed by the building owner or managing agent to discuss upgrading the commercial portions and potentially coordinate with the contractor responsible for that work.2.

Addressing the Existing Issues

The fact that Section 1 and 3's commercial spaces have no fire alarm control panel is a code violation. It is possible the existing commercial fire alarm is an illegal fire alarm.3.

Panel Replacement

Your replacement of the residential panel in Section 2 is an opportunity to address this. It might involve:
Installing a new addressable fire alarm control panel in Section 2 that can communicate with the other sections of the building. Extending the fire alarm system into Section 1 and 3's commercial spaces. Implementing a system that meets current code and the FDNY's preferences.

Recommendations


Consult with a Qualified Fire Alarm Professional and the FDNY

Engage a licensed and experienced fire alarm designer/engineer in New York City, and schedule a meeting with the FDNY to discuss the project and the FDNY's expectations. The FDNY will have the final say on what's acceptable.2.

Review the Building's Fire Safety Plan

Understand the existing fire safety plan for the building. This document outlines how the building's fire protection systems are supposed to operate.3.

Communicate with Building Management/Owners

Clearly communicate the code deficiencies and the potential solutions to the building management or owners. Emphasize the benefits of a fully integrated fire alarm system in terms of life safety and property protection.4.

Consider an Addressable System

If feasible, recommend an addressable fire alarm system. Addressable systems offer greater flexibility, precise location of alarms, and enhanced monitoring capabilities.5.

Scope Clarification

If the building owner is not planning on upgrading the commercial spaces, it is important to have a clear scope of work that outlines that you are not responsible for bringing those spaces up to code, as those spaces need to be brought to code.6.

Document Everything

Keep thorough records of all communications, design decisions, and approvals from the FDNY.

In summary, the FDNY is likely advocating for a unified fire alarm approach where multiple panels work in concert as a single, cohesive system. While your immediate scope is the residential replacement, the larger building context and the FDNY's guidance necessitate a holistic evaluation and coordinated solution to ensure the entire building is properly protected.