Question: Can I use a single phase of a three phase 480 Delta to 240 Delta w/ center taps to provide power for a 120/240V load center? I would use the center tap as my neutral and bond it to ground.
No, you cannot safely and reliably use a single phase from a 480V Delta to 240V Delta (high-leg Delta) transformer and create a 120/240V system by bonding the center tap of one leg. This is due to several critical issues: Voltage Imbalance and High Leg
A delta transformer system does not have a neutral point in the way that a wye system does. When you create a center tap on one phase, the voltage to neutral on the other two phases will be 208V. This is why it is referred to as the "high leg." This is an unacceptable voltage range for standard 120V equipment.
Loading Concerns
Single-phase loads connected to the center-tapped phase would severely unbalance the three-phase transformer. Delta transformers are designed for balanced three-phase loads. Imbalance causes:
Overheating
The transformer windings connected to the heavily loaded phase will overheat, potentially leading to failure.
Voltage Regulation Issues
The voltage on the other phases may become unstable due to the unequal loading.
NEC Compliance
The National Electrical Code (NEC) has specific requirements for grounding and bonding in electrical systems. Attempting to create a 120/240V system from a single phase of a Delta transformer in this way would violate these requirements.
Acceptable Solutions
Use a dedicated single-phase 480V to 120/240V Transformer
This is the safest and most reliable solution. A properly sized single-phase transformer will provide the correct voltage and current for your 120/240V load center.2.
Use a Three-Phase Wye-Connected Transformer
If you need to derive 120/208V power from a 480V source, use a 480V Delta to 208Y/120V Wye transformer. This provides a true neutral point and balanced voltages.
In Summary
Using a single phase of a Delta transformer to derive 120/240V power with a center tap is not a safe or code-compliant method. Use a dedicated single-phase transformer or a three-phase Wye-connected transformer for this purpose. Always consult with a qualified electrician to ensure that any electrical work is performed safely and in accordance with local codes.