User: PeterW, Location: Washington DC
Asked on: Friday, August 23, 2024 at 9:55 am EDT
Answered on: Thursday, March 6, 2025 at 1:32 am EST
Question: We are looking at a 480V switchgear with three (3) 2000A sources that all feed the same 6,000A bus. Each 2000 A breaker is fed from its own source. There are no tie breakers and (5) loads breakers with various loads to the building. There is an existing 4,000A spare. I don't believe that we can add any power to this source because of 705.12(B)(3)(1). Thoughts?
You're right to be concerned about 705.12(B)(3)(1). Let's break this down and see why it's likely preventing you from adding more generation.
Understanding 705.12(B)(3)(1): The 120% Rule
This section of the NEC (National Electrical Code) addresses the overcurrent protection of busbars when multiple sources (like your three 2000A sources, and potentially a new one) are connected. It limits the combined rating of overcurrent devices protecting the busbar from the sources to 120% of the busbar's ampacity.
Applying the Rule to Your Switchgear Busbar Ampacity
Your busbar is rated for 6000A.
120% Limit
120% of 6000A = 7200A
Existing Source Protection
You have three 2000A breakers feeding the bus, totaling 6000A.
Remaining Capacity
7200A (limit) - 6000A (existing) = 1200A
The Problem
The 120% rule limits the sum of the overcurrent devices for all the incoming sources to 7200A. You're already at 6000A. This leaves you with only 1200A, which may not even be enough for your existing spare breaker.
What about the Spare 4,000A breaker?
This is where things get even trickier. You can't just put a breaker on that spare and feed it without exceeding the 120% rule. Remember, the breaker protects the _source_, not the load. The fact that you have a 4000A spare slot doesn't mean you can supply 4000A of power from the bus without exceeding 7200A, which is a problem.
Why 705.12(B)(3)(1) is Relevant Here
Even if the spare breaker is intended to only serve loads, you still can't add a source without meeting the 120% rule.
Possible Solutions (and Considerations)
Adding more generation is tricky, but not impossible. Here are some options, all of which would require a very careful engineering study and potentially significant modifications:1.
Reduce Existing Source Protection
Could you safely reduce the size of one or more of the existing 2000A breakers? This is
unlikely to be feasible without significantly impacting your existing system, but it's something to investigate. For instance, can you verify that the existing source can be sufficiently protected with 1600A breaker instead of a 2000A breaker?2. Replace the Busbar
A more costly option, but replacing the busbar with one of a higher ampacity (e.g., 8000A or 10,000A) would increase the 120% limit. This likely requires replacing the entire switchgear, which is very expensive and time consuming.3.
Modify the Switchgear Configuration
This is very site and system specific. Consider the following:
Tie Breakers
Adding tie breakers and splitting the bus into sections might allow you to isolate the new source to a section without violating the 120% rule on the entire bus. But you would still have to evaluate each of the sections individually.4.
Load Shedding or Demand Response
Implement load shedding or demand response schemes that reduce the amount of load on the bus when the new source is injecting power. This is a control strategy, not a hardware fix.
Important Caveats Engineering Study is Mandatory
You must have a qualified electrical engineer perform a thorough study before making any changes. This study needs to: Verify the actual load profile of the existing feeders and connected loads. Perform a short-circuit analysis to ensure that the switchgear and all protective devices can handle potential fault currents with the new source connected. Calculate the coordination between all overcurrent protective devices. Consider any utility requirements.*
Local Codes and Utility Interconnection Requirements
Your local electrical codes and the utility's interconnection requirements may have even stricter rules than the NEC. Always check with the local authorities.
In summary, your initial assessment is very likely correct. Due to NEC 705.12(B)(3)(1), adding a new source is going to be very difficult and likely require significant modifications to the switchgear or a complete replacement. Flag for review