Topic: Demand calculations in a residence

User: Luis De Castro, Location: Miami Fl.

Asked on: Friday, August 23, 2024 at 1:19 pm EDT
Answered on: Thursday, March 6, 2025 at 1:33 am EST

Question: Im worKing in the installation of a 65 kw emergency generator, the existing plans dont match existing field conditions, I asked the Power Co the give me highest kilowatt/hour demand in a month and they tell me is 9,039 kiloiwatts /hours . i wsnt to convert to kvas. Which calculation I can use. The way I did is divde that figure into 720n hours AND a pf OF .8, I came out with 82 amps adding 1.25 for safety?

Okay, let's break down how to convert your kilowatt-hour (kWh) energy consumption into kVA and then calculate the approximate amperage. Your approach is partially correct, but we need to be precise about the terminology and steps.

Understanding the Terms kW (Kilowatt)

Instantaneous
real power demanded at a particular moment. This is what powers the actual work.

kWh (Kilowatt-hour)

A unit of energy. It's the amount of power used over a period of time (typically an hour). It's what the power company bills you for.

kVA (Kilovolt-Ampere)

Apparent power. It represents the total power supplied by the utility, including both real power (kW) and reactive power (kVAr).

Power Factor (PF)

The ratio of real power (kW) to apparent power (kVA). PF = kW / kVA. A lower power factor means more reactive power is required to deliver the same amount of real power. A power factor of 0.8 is common, especially for commercial/industrial facilities.

The Problem with Your Approach


Using the kWh figure directly to calculate instantaneous kVA is not accurate. The 9,039 kWh is the total energy consumed in a month. It doesn't tell you the peak demand at any given moment, which is what's relevant for sizing a generator.

Here's a Better Approach to Estimate kVA Demand1. Get Peak kW Demand (If Possible)

The best way to determine the correct generator size is to get the peak kW demand from the utility. This is the highest kW the facility drew at any point in the billing period. Insist that they provide you with the MAX kW in that month. This is what you need to find the right generator size.2.

Estimate Peak kW Demand (If Peak is Unavailable)

Without the actual peak kW demand, you'll have to estimate. Dividing the total kWh by the number of hours in the billing period only gives you the average kW demand, and the peak demand will likely be significantly higher. This average kW demand would be:9,039 kWh / 720 hours = 12.55 kW (average)

Important

Since you want the peak kW demand, you cannot use this method. The best way is to ask for the peak.3.

Calculate kVA Demand

Once you have the peak kW demand, you can calculate the peak kVA demand using the power factor:kVA = kW / PFFor example, if the peak kW demand is 40 kW, and the power factor is 0.8:kVA = 40 kW / 0.8 = 50 kVA4.

Generator Sizing

When selecting a generator, you'll want the generator's kVA rating to be equal to or greater than the calculated peak kVA demand. In reality, you probably need to provide more information than just the peak power demand. You need to provide a detailed load analysis on the equipment to be energized by the generator.

Example Calculation (If you had Peak kW)

Let's assume the power company did provide you with the peak kW demand for the month, and it was 60 kW.1.

Peak kW Demand

60 kW2.

Power Factor

0.83.

Calculate kVA

kVA = 60 kW / 0.8 = 75 kVA

Calculating Amperage (Once you have kVA)


The formula for calculating amperage depends on the voltage and phase of your electrical system. Assuming a three-phase system:Amps = (kVA 1000) / (√3 Voltage)Example: kVA = 75 kVA Voltage = 480 Volts (typical for commercial) Amps = (75 1000) / (1.732 480) = 90.2 Amps (approximately)Applying Safety Factors

It is good practice to apply a safety factor. However, simply adding 1.25 is not correct.
NEC (National Electrical Code)

The NEC requires you to size the generator based on the connected load, following specific rules for different types of equipment.

Motor Starting

Motors can draw a significantly higher current during startup (inrush current). The generator needs to be sized to handle this.


Future Expansion

Consider future load increases when sizing the generator.

Generator Derating

Some generators are derated for altitude or temperature. Check the generator's specifications.

In Summary
1. Get the peak kW demand from the power company. This is crucial.2. Calculate kVA demand using the peak kW and power factor (kVA = kW / PF).3. Use the kVA to calculate amperage based on your system voltage and phase.4. Follow the NEC and generator manufacturer's recommendations for proper sizing and safety factors. A load analysis is essential.Important Considerations Code Compliance

Make sure your generator installation complies with all applicable electrical codes (NEC, local codes).

Professional Advice

Consult with a qualified electrical engineer or contractor experienced in generator installations. This is essential for ensuring safety, code compliance, and proper system performance.


Load Analysis:
A detailed load analysis is necessary to properly size the generator and account for all connected loads, including motor starting requirements.Do not proceed without the peak kw data, and contacting a professional is recommended Flag for review