Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Bonding of 200 amp residential meter/main combo and sub/secondary/extension panel

User: Los11romero, Location: New Mexico, USA

Asked on: Friday, August 23, 2024 at 2:16 pm EDT
Answered on: Thursday, March 6, 2025 at 1:34 am EST

Question: To Bond, or not to Bond…..So, can anyone clarify this with a code reference? I know that in a commercial setting it is possible and legal to have a main breaker panel sub-feeding a secondary mlo panel which would mean that they share the disconnect switch therefore one is an extension of the other and essentially they are the same panel with multiple cans.Now, in a residential setting using an overhead feed 200 amp meter/main combo that utilizes the feed thru lugs to feed a second 200 amp panel fed with 4/0 al SER cable, would it not be necessary to bond grounded and grounding in BOTH panels? Based on the sub-feed cable being technically an extension of the main panels busbar.

Okay, let's break down the bonding requirements in your scenario, referencing the National Electrical Code (NEC). This can get tricky, and local interpretations can vary, so always consult your local Authority Having Jurisdiction (AHJ) for final say.

Understanding the Key Concepts Service Equipment

This is the point where power enters the building. In your case, the meter/main combo is
service equipment.

Separately Derived System

A separately derived system is a source of power that is not electrically derived from the service. A generator or transformer would be examples.

Main Bonding Jumper (MBJ)

Connects the grounded (neutral) conductor to the equipment grounding conductors (the metal enclosure) at the
service equipment.

Grounding Electrode Conductor (GEC)

Connects the service equipment to the grounding electrode system (ground rods, water pipe, etc.).

Subpanel

A panel fed from another panel (either service or another subpanel). Subpanels should
not have the neutral and ground bonded together.

Feed-Through Lugs

Lugs that allow you to extend the busbar from the main panel to another panel.

Your Specific Scenario: Residential Overhead Feed with Feed-Through Lugs


You have:1. A 200A meter/main combo (service equipment) with feed-through lugs.
2. A second 200A panel fed from the feed-through lugs using 4/0 Al SER cable.

NEC Analysis Panel #1 (Meter/Main Combo)

This is
service equipment.

Bonding

The grounded (neutral) conductor must be bonded to the enclosure using the Main Bonding Jumper (MBJ). The Grounding Electrode Conductor (GEC) connects to this location as well.

NEC 250.24(C) and 250.28
Rationale

This is the point where the electrical system is intentionally grounded, providing a low-impedance path for fault current back to the source, tripping the breaker and clearing the fault.


Panel #2 (Fed from Feed-Through Lugs)

This is the crux of the issue. Is it a subpanel or an extension of the service equipment?



Arguments for Bonding in BOTH Panels

You could argue that, because the second panel is directly fed from the feed-through lugs, it's essentially an extension of the main panel's busbar. In this interpretation, it's all considered service equipment. If this is your case, the second panel would need to be bonded again with a MBJ.

NEC 250.24(A)(5) states "A grounded conductor shall be installed with each service."

Arguments Against Bonding in Panel #2

The more common and preferred interpretation is that the second panel is a subpanel.

NEC 250.32(A) states "For a detached building or structure, the grounding electrode(s) required by Part C of this article shall be connected to the building or structure disconnecting means."
If it is a subpanel, then you do not bond the grounded (neutral) conductor to the enclosure in the second panel. This would create parallel paths for neutral current and potentially dangerous circulating currents on the grounding system. The 4/0 Al SER cable contains a grounding conductor that provides the grounding path back to the main panel. In this case, you would need to drive ground rods and connect a grounding electrode conductor to the grounding bar in the second panel.

NEC Sections to Reference

Article 100: Definitions (Service Equipment, Grounded Conductor, Grounding Conductor)


Article 250: Grounding and Bonding (This entire article is crucial) 250.24 Grounding Service-Supplied Alternating-Current Systems. 250.28 Main Bonding Jumper and System Bonding Jumper. 250.30 Grounding Separately Derived Alternating-Current Systems. 250.32 Grounding at Separate Buildings or Structures. 250.142 Use of Grounded Circuit Conductor for Grounding Equipment This section explains where you can and cannot use the neutral for grounding. In general, you cannot at subpanels.

Conclusion and Recommendation


The MOST COMMON interpretation is that the second panel is a SUBPANEL. This means you would not bond the neutral and ground in the second panel. You need to provide a four-wire feed (two hots, a neutral, and a ground) to the second panel. Drive ground rods at the second panel and connect them to the grounding busbar.

Why is this important?Bonding the neutral and ground in a subpanel creates a parallel path for neutral current. This can lead to: Nuisance tripping of GFCI devices. Overheating of grounding conductors. Stray voltage on metal parts, creating a shock hazard.

Crucial Step: Consult Your Local AHJ!This is a complex issue. The correct interpretation depends on local codes and how your AHJ views the installation.

Contact your local electrical inspector
before you start the work. They have the final say. Show them your plan and ask specifically about bonding requirements for a panel fed from feed-through lugs in a residential service. Their guidance will ensure a safe and code-compliant installation.

In summary: While the argument can be made to bond both, the overwhelming consensus is that with the second panel being fed with 4-wire SER cable, it is a subpanel and therefore grounded and grounded only at the first panel (Service equipment). Check with local AHJ
* Flag for review

Previous Question Next Question