Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Transformer GEC bonding

User: Thenooberus, Location: Arizona

Asked on: Friday, August 23, 2024 at 4:11 pm EDT
Answered on: Thursday, March 6, 2025 at 1:34 am EST

Question: Our team is in charge of running ground from building to transformers. We’re using pvc raceways. Running 2awg from the building ground bars to 75 kv transformers. We use 3/4 metal cable gland connectors to enter the transformer. Some argue we should switch to pvc cgb connectors or have to install bond bushings on the metal connectors. In my case do I need a bond bushing? Or switch to pvc cgb?

Okay, let's break down the grounding requirements for your situation and whether you need bonding bushings or PVC connectors.

Understanding the Goal

The primary goal of grounding is to provide a low-impedance path for fault current to return to the source (the transformer). This allows overcurrent protective devices (circuit breakers or fuses) to trip quickly and safely interrupt the fault, minimizing damage and shock hazards. For high-voltage systems, the emphasis on low impedance is even more critical due to the higher potential for arcing and greater energy involved in a fault.

NEC and Grounding Principles Relevant to Your Situation Equipment Grounding Conductor (EGC)

Your 2 AWG conductor is acting as an EGC. It needs to be continuous and effectively bonded to all metal enclosures and equipment along its path.


Grounding Electrode Conductor (GEC)

This connects the grounding electrode system (ground rods, building steel, etc.) to the service equipment (in your case, the transformer). While you're not directly talking about the GEC, it's important to remember that the EGC ultimately needs a connection to the GEC system.

Article 250

This article of the National Electrical Code (NEC) covers the requirements for grounding and bonding. Pay particular attention to the sections related to equipment grounding and bonding of metal enclosures.


Impedance

The lower the impedance of the grounding path, the better. Impedance is resistance to the flow of alternating current and can be caused by loose connections, dissimilar metals, or long runs of conductors.

Bonding vs. Grounding

Grounding is connecting to earth or a conducting body that serves as earth. Bonding is connecting conductive parts together to create an electrically conductive path that has the capacity to conduct safely any fault current likely to be imposed on it. Bonding is essential for preventing voltage differences between metal parts, reducing shock hazards.

Analysis of Your Setup
1. PVC Raceway

PVC is non-conductive, so it doesn't contribute to the grounding path. The 2 AWG conductor provides the grounding path
inside the raceway.2.

Metal Cable Gland Connectors

This is where the potential issue arises.


Code Requirements

NEC 250.92(B) requires the metal enclosures for service raceways and service equipment to be bonded using methods outlined in 250.92(B)(2) through (4).

Fault Current Path

When a fault occurs inside the transformer, fault current will flow through the transformer enclosure, into the metal connector, and
then hopefully into the 2 AWG ground wire.

Potential Impedance

If the metal connector isn't properly bonded to the transformer enclosure, the fault current path could have high impedance.

Arcing

A high-impedance fault path can lead to arcing and sparking at the connector, which is dangerous, damages equipment, and delays the tripping of the overcurrent device.

Do You Need Bonding Bushings or PVC CGBS?
Yes, you need additional bonding if using metal connectors. Here's why, and what your options are: Metal connectors without proper bonding create a discontinuity in the grounding path. They introduce resistance/impedance, which you want to minimize. Bonding Bushings with a Bonding Jumper

This is a common and acceptable method. A bonding bushing is installed on the metal connector where it enters the transformer enclosure. A bonding jumper (a short length of appropriately sized wire) is then connected from the bonding bushing to a grounding point on the transformer enclosure. This bonds the connector to the transformer, creating a low-impedance path. The size of the bonding jumper is determined by NEC Table 250.102(C)(1) based on the size of the ungrounded conductors.

PVC Coated Glands (CGBS)

These are typically made of metal and coated with PVC. The coating prevents corrosion from the metal, but doesn't eliminate the need for bonding.

Properly Listed PVC Coated Glands

These are typically listed for grounding/bonding purposes. They're designed to provide a low-impedance path through the connector body itself. If you are using one that is listed for this purpose, it should eliminate the need for the bonding bushing or jumper.

PVC Connectors

If you use a PVC connector that is a non-metallic type that threads into the transformer with a nut on the outside, then you don't need to bond it. The PVC connector itself creates an insulated break between the conduit and the transformer.

Recommendation


Here's my recommendation:1. Evaluate your current metal connectors

Is it listed for grounding and bonding purposes?2.

If it's not listed, consider PVC connectors or bonding bushings

If you want to stick with metal connectors, install bonding bushings with appropriate bonding jumpers to the transformer enclosure. This is a reliable and code-compliant solution. Make sure the jumper connections are clean and tight. If you want to eliminate the need for bonding jumpers, switch to Listed PVC Coated Glands3.

Torque

Torque all connections according to manufacturer's instructions. A loose connection is just as bad as no connection.4.

Documentation

Document your grounding and bonding methods and keep them with the equipment records.

Important Considerations
Local Codes

Always check with your local electrical inspector or authority having jurisdiction (AHJ). They may have specific requirements that go beyond the NEC.


Transformer Manufacturer Recommendations

Consult the transformer manufacturer's installation instructions for any specific grounding or bonding requirements.*

Qualified Personnel

Ensure that all electrical work is performed by qualified electricians who are familiar with the NEC and local codes.

In summary, while you are running an EGC inside the PVC raceway, the metal connectors introduce a potential weak link in the grounding path. You need to address this by using either bonding bushings with jumpers or Listed PVC Coated Glands
Flag for review

Previous Question Next Question