Topic: 3 phase power in old apartment building, no ground.

User: ABR, Location: Puerto Rico

Asked on: Friday, August 23, 2024 at 9:01 pm EDT
Answered on: Thursday, March 6, 2025 at 1:35 am EST

Question: Hello,To start, I would like to state that I am a GC, not an electrician. We are working on an apartment remodel and found a situation where the there is no ground. It is an old style, two wire building where all the plugs had been changed to three holes (without any grounding). The panel is 3 phase because the old HVAC air handler ran on 3 phase power. There is no way to provide a mechanical ground.The existing solid copper wiring is in bad shape (we found some outlets jumped with speaker wire laid under tile). Some of the existing EMT is usable but a lot is not; some wires are just stuck in the conduits and there is no way to get them to move. The easiest option is to run new conduit along the ceiling (all concrete construction) and cover it with a gypsum false ceiling. I was reading through the NEC and cannot decide what the proper conduit would be (we even considered NMC without conduits).It seems that ungrounded and unbonded EMT is just a bead idea, which leaves PVC for the new runs. That seems fine since the ceiling space shouldn't be subject to physical damage (though not sure 1/2" gypsum is really much protection). I also suggested to the electrician that we change the panel and add GFCI/AFCI combo breakers.Any feedback on this solution would be appreciated. Does the PVC conduit (back to the main panel, where they're being replaced) with GFCI/AFCI breakers and stranded copper wire seem like the best solution in this scenario? Normally I would just let the electrician do his thing, but I thought I would ask since I don't see an ideal solution here.Thank you.

Okay, this is a complex situation, and you're right to be asking questions. Here's a breakdown of the issues and considerations for your approach, along with recommendations

Understanding the Problem:
Ungrounded System is Dangerous

Replacing 2-prong outlets with 3-prong without a ground creates a serious shock hazard. This is a common, but

extremely illegal
practice. Someone could be seriously hurt or killed.
Old Wiring & Damage

The fact that the wiring is deteriorated and has been tampered with (speaker wire!) confirms that a complete rewire is the safest and most responsible approach.

3-Phase Panel

While the HVAC used 3-phase, the apartment's general lighting and receptacles are almost certainly running off a single phase. The panel itself doesn't necessarily dictate your wiring approach, but it
does mean you need a qualified electrician to safely disconnect the old 3-phase equipment and properly reconfigure the panel if needed.

Conduit Obstructions

The inability to pull new conductors through existing conduit renders much of it useless.

Evaluating Your Proposed Solution



New Conduit Run on Ceiling

This is a common and acceptable solution for renovations when existing pathways are unusable. Covering it with a dropped gypsum ceiling is a good way to conceal and protect it.


PVC Conduit

This is a viable option IF the installation meets all the requirements. We'll get into the code requirements below.

GFCI/AFCI Combo Breakers

This is
absolutely essential in this scenario. GFCI protection is crucial to mitigate the shock hazard from the lack of grounding. AFCI protection provides fire safety.

NEC Considerations and Recommendations


Rewiring is the Best Solution

This is paramount. You've already identified this, but I want to emphasize it. Don't try to patch the existing wiring. A complete rewire is the only way to ensure safety and code compliance.2.

EMT Conduit

It is a safe, code-compliant, and reliable choice. The EMT provides a continuous ground path from the metal device box back to the panel. The conductors can be pulled after the conduit system is installed.3.

PVC Conduit

PVC is permissible, but it has limitations. Specifically Article 352.12 Uses Not Permitted:


(C) Physical Damage.
Unless identified for the use, PVC conduit shall not be used where subject to physical damage. (D) Ambient Temperatures. Unless marked to indicate the temperature, PVC shall not be installed where subject to ambient temperatures exceeding 50°C (122°F).Also you must meet Article 352.60: 352.60 Grounding. Where equipment grounding conductors are installed in PVC conduit, they shall be installed in accordance with 250.130(C).
4. Grounding Electrode Conductor

Ensure the main panel has a proper grounding electrode conductor connected to a grounding electrode system (e.g., ground rod, water pipe). This is critical for the overall system's safety.5.

GFCI Protection (NEC 210.8)



Receptacles

GFCI protection is required for all 125V, 15A and 20A receptacles in bathrooms, kitchens, garages, and outdoor locations. Consider GFCI protecting
all receptacles, even if not strictly required, for enhanced safety in an ungrounded system.

Breaker vs. Receptacle GFCI

You can use GFCI breakers or GFCI receptacles (or a combination). GFCI breakers provide whole-circuit protection, while GFCI receptacles only protect the downstream outlets on that branch circuit. The choice depends on the specific circuit layout and your budget.6.

AFCI Protection (NEC 210.12)

AFCI protection is generally required for branch circuits supplying outlets or devices in dwelling units (bedrooms, living rooms, etc.). AFCI breakers provide protection against arc faults, which are a leading cause of electrical fires.7.

"Bootleg" Ground

Absolutely prohibit the electrician from creating a "bootleg" ground (connecting the ground terminal of the receptacle to the neutral wire). This is extremely dangerous and violates code.8.

Proper Wiring Methods

Ensure all wiring methods (splicing, connections, etc.) are done correctly and in accordance with NEC. Use appropriate wire connectors rated for copper.9.

Existing EMT

If you want to try to reuse the existing EMT, you'll need to address the issue of the stuck wires. Try lubricant, fish tape, or even a vacuum/blower to assist. If you absolutely cannot get the old wires out, abandon the conduit in place and run new conduit.10.

Documentation and Inspection

Get the electrical work properly inspected by the local building department. This is important for safety and for potential future real estate transactions.

In summary, I would recommend a full rewire using EMT conduit to ensure a continuous, safe ground path. Then GFCI/AFCI breakers at the panel would be the next best alternative.
Important Notes



Permits and Inspections

This work requires a permit and inspection by your local building authority. Don't skip this step.


Qualified Electrician

This is not a DIY job. You need a licensed and experienced electrician who understands NEC requirements and can properly design and install the wiring.*

Liability:
As the GC, you are ultimately responsible for ensuring that the work is done safely and to code. Don't cut corners or allow unsafe practices.By taking these steps, you can significantly improve the electrical safety of the apartment and protect its occupants. Good luck with the project! Flag for review