Question: I've seen a question come up about removing a bollard from the base and replacing with a 10 foot pole light. I haven't poured bases in years but best I recall, bollards were poured about 18 - 24 inches deep. A 10 foot pole light should be 3 feet, from the charts I've seen. How deep have any of you poured bollards?
You're right to question the swap. Converting a bollard base to a light pole base presents several challenges. Here's a breakdown based on my experience and industry best practices
Bollard Base Depth:
Your assessment of 18-24 inches is typical. Bollards are primarily designed to be a visual deterrent and to withstand low-impact collisions (e.g., shopping carts, accidental bumps). Their depth is sufficient for that purpose, but not for the wind load and structural demands of a 10-foot light pole.
Light Pole Base Depth (and Diameter)
3 feet is a good starting point, but the actual depth depends on several factors
Pole Height and Weight
Taller and heavier poles require deeper and wider footings.
Wind Load
This is a critical factor. Areas with high wind conditions (coastal regions, open fields) require significantly deeper foundations to prevent tipping. Your local building codes will specify the design wind speed.
Soil Conditions
Poor soil (e.g., loose sand, clay) requires a larger and deeper foundation. Soil testing is highly recommended to determine the soil bearing capacity.
Pole Diameter and Anchor Bolt Configuration
The size and configuration of the anchor bolts used to secure the pole to the base influence the base design.
Local Building Codes
These are the ultimate authority. Consult your local building department for specific requirements.
Diameter is Equally Important
A light pole base will also be significantly wider than a bollard base. This is crucial for stability. A typical 10-foot pole might require a base diameter of 18-24 inches, or even more, depending on the factors listed above.
Why You Can't Just "Swap"
Insufficient Depth
The existing bollard base is almost certainly too shallow for a light pole.2.
Insufficient Diameter
The existing bollard base is almost certainly too narrow to provide adequate stability.3.
Load Considerations
A bollard base is not designed to withstand the bending moment caused by wind loading on a 10-foot pole.4.
Anchor Bolt Configuration
Bollards typically don't have a robust anchor bolt system designed for the loads of a light pole. Light poles require precisely placed and embedded anchor bolts to securely connect the pole to the base.
What Needs to Be Done
Remove the Existing Bollard Base Completely
This is the safest and most reliable approach. Trying to modify or build upon the existing base is generally not recommended.2.
Proper Foundation Design
Have a qualified structural engineer design the new light pole foundation. This design must take into account: Local building codes Wind load calculations Soil conditions (soil testing) Pole specifications (height, weight, diameter, anchor bolt configuration)3.
Excavation and Forming
Excavate the area to the required depth and diameter specified by the engineer's design. Create proper forms to contain the concrete.4.
Anchor Bolt Installation
Install the anchor bolts precisely according to the engineer's drawings. Use a template to ensure proper alignment and spacing.5.
Concrete Pour
Pour concrete of the specified strength and allow it to cure properly.6.
Pole Installation
After the concrete has cured, install the light pole according to the manufacturer's instructions, torquing the anchor bolts to the specified value.7.
Electrical Connection
A qualified electrician must make the electrical connection to the light pole, ensuring compliance with all applicable codes.
In summary: Replacing a bollard with a light pole is not a simple "swap." It requires proper engineering design, excavation, a new foundation pour, and careful attention to detail. It's crucial to prioritize safety and compliance with local building codes. Trying to cut corners can lead to a dangerous and unstable installation. I always recommend contacting a civil or structural engineer. They will have the most up-to-date requirements and can design and oversee the entire operation. Flag for review