User: Doc13067, Location: Bucks County/Philadelphia, PA USA
Asked on: Saturday, August 24, 2024 at 1:37 am EDT
Answered on: Thursday, March 6, 2025 at 1:35 am EST
Question: Hey guys, I need the brains on this forum. I put in electric for 2 mini splits and my HVAC pal installed them in 2021. Both got fried this year and we believe it was a surge. He had to replace all major components of both and it cost about the same as entire new units. Before he did that I put SPDs in. A Siemens Bolt Shield 35kA (that’s the only one my supply had in stock, I know it’s low) and two 100kA SPDs that I got from a HVAC place, one on each mini split disco. A month later it happened again!!!! Unit 1 had the board blown and Unit 2 survived. The Siemens boltshield is showing red trip flags and the 100kA on Unit 1 no longer has a lit green LED. Unit 2 still shows a green LED. At least 135,000 amps worth of surge busted through the gates and fried Unit 1 in the last month. The house is very well grounded but it is a farm house in the middle of nowhere (3 inch spiders all around). There is no evidence of lightning damage anywhere but that’s not to say it didn’t occur. My gut tells me this is a utility thing because lightning hasn’t declared war on us in the last 3 years but something certainly could be up with their equipment. Does anyone have any ideas?WWLFD?
Okay, this is a frustrating situation, and you're right to be concerned. Let's break down the problem and explore some potential solutions. You've already done some good things, but clearly, something more is needed.
Understanding the Problem Recurring Damage
The fact that this is happening repeatedly after installing SPDs points away from random isolated events and more toward a systemic issue.
SPD Failure
The SPDs are sacrificial devices. They're designed to take the hit, and then they're done. The fact that the Siemens BoltShield tripped and the 100kA SPD on Unit 1 failed confirms they protected against overvoltage, but they were overwhelmed. A 35kA SPD at the panel may not be large enough for your situation if you are experiencing surges over that value.
Limited Protection
The fact that one unit survived while the other did not indicates the surge found its way to Unit 1 via another source, either through the wiring or even some other path such as a communication line.
Location, Location, Location
Being in a rural area with a farmhouse significantly increases the risk of power quality issues. Utility infrastructure in rural areas tends to be older, less maintained, and more susceptible to voltage fluctuations and surges. The fact that Unit 2 survived may be due to distance between the units and the electrical panel.
Grounding
You say it's "well grounded," but let's verify this.
Troubleshooting and Investigation - Priority Actions1. Contact the Utility Company Immediately
This is your top priority.
Report the Problem
Tell them you're experiencing repeated power surges that are damaging your equipment. Be specific about the dates, times, and the nature of the damage.
Request an Investigation
Ask them to investigate the power quality on their side of the meter. Specifically request that they check for:
Voltage fluctuations
Are there frequent voltage sags or swells?
Harmonic distortion
This can damage sensitive electronics.
Faulty equipment
Could a failing transformer, capacitor bank, or other utility equipment be the source of the surges?
Loose neutral
This is a common cause of voltage imbalances and surges. It can lead to significantly overvoltage on some circuits while others are undervolted.
Document Everything
Keep a detailed log of your communications with the utility, including dates, times, names of representatives, and the outcome of their investigations.2.
Grounding System Assessment (Verify, Verify, Verify)
Don't just assume it's good. Professionally verify the grounding system.
Ground Rods
How many ground rods do you have? Are they properly spaced and connected? Consider adding more ground rods to create a better grounding grid.
Ground Wire Size
Is the ground wire from the service entrance to the ground rods the correct size?
Bonding
Are all metal parts (metal water pipes, gas pipes, etc.) properly bonded to the grounding system?
Ground Resistance Test
Have a qualified electrician perform a ground resistance test to measure the effectiveness of your grounding system. Ideally, it should be 5 ohms or less.
Impedance Test
Have a qualified electrician perform an impedance test to verify your ground.3.
SPD Upgrade (Panel Level)
35kA is inadequate for your described situation. Upgrade it immediately.
Higher Surge Capacity
Install a
much larger whole-house SPD at your main electrical panel. Aim for at least 100kA per phase (or even higher, like 200kA). Consider a surge counter model to track how often it’s doing its job. Hardwired vs. Plug-in
Hardwired SPDs generally offer better protection than plug-in models.
Proper Installation
Ensure the SPD is installed as close as possible to the main breaker with the shortest possible lead lengths (wire between the SPD and the breaker). This minimizes inductance, which can reduce the SPD's effectiveness.4.
Layered Protection
Think of surge protection as a multi-layered defense.
Service Entrance
Large SPD at the main panel (as above).
Subpanels
Consider SPDs at any subpanels, especially if the mini-splits are fed from a subpanel.
Point-of-Use
SPDs at the mini-split disconnects are good, but make sure they are adequately sized and
high quality. Dedicated Surge Strips
Use high-quality surge protector power strips for any sensitive electronics connected to the same circuits as the mini-splits.5.
Neutral-Ground Bonding
Verify that your neutral-ground bond is only at the service entrance panel. There should not be any other neutral-ground bonds downstream.6.
Wiring Review
Have a qualified electrician review the wiring to the mini-splits.
Dedicated Circuits
Ensure each mini-split has its own dedicated circuit.
Proper Wire Size
Verify the wire size is adequate for the load.
Tight Connections
Check all connections for tightness, both at the panel, disconnect, and the mini-split unit itself. Loose connections can cause voltage drops and other problems.
Conduit
Consider running the wiring in conduit to provide additional physical protection and shielding.7.
Lightning Protection System (If Applicable)
If you suspect lightning is a possibility, consider installing a professional lightning protection system for your house and outbuildings. This is a significant investment but may be necessary if lightning is a recurring threat.8.
Monitor Voltage Regularly
Get a voltage monitor and log. This helps you correlate spikes and surges.
Important Considerations
"Farmhouse in the Middle of Nowhere" Implications
The quality of power in rural areas can be significantly lower than in urban areas. Longer distribution lines, older equipment, and exposure to the elements can all contribute to power quality problems.
Documentation is Key
Keep meticulous records of everything: dates, times, events, conversations with the utility, repairs, and expenses. This documentation will be invaluable if you need to file a claim with the utility company or your insurance company.
Professional Help
Don't hesitate to hire qualified electricians, HVAC technicians, and potentially even a power quality consultant to help you diagnose and resolve this issue.
WWLFD (What Would Larry Fine Do?)
Larry Fine, being the meticulous and safety-conscious Stooge, would likely:1. Thoroughly investigate
He wouldn't just slap a band-aid on the problem. He'd meticulously check everything, from the utility connection to the grounding system.2.
Consult experts
He wouldn't be afraid to ask for help from qualified professionals.3.
Over-engineer
He'd probably install multiple* layers of surge protection, just to be sure.4.
Document everything
He'd keep detailed records of all his findings and actions.5.
Wear safety glasses
Even for seemingly simple tasks, because you never know when Moe might be around with a hammer!
In Summary
This is a complex problem that requires a multi-faceted approach. By working with the utility company, verifying your grounding system, upgrading your surge protection, and seeking professional help, you can significantly reduce the risk of future damage to your mini-splits and other electronic equipment. Good luck! Flag for review