Topic: Classified roof feeds

User: Shockedby277v, Location: Michigan

Asked on: Saturday, August 24, 2024 at 8:52 am EDT
Answered on: Thursday, March 6, 2025 at 1:36 am EST

Question: Here is a scenario. Warehouse with half being a classified area. We will say class-1 div-1. On the roof there are 3 exhaust fans and 3 RTU's.Do the exhaust fans require to be classified equipment?Do the RTU's require to be classified?Can the feeds for both be ran through the roof at the unclassified area, ran across the roof above the classified are to feed these units and treated as unclassified raceways and wiring?

Okay, this is a frustrating situation, and you're right to be concerned. Let's break down the problem and explore some potential solutions. You've already done some good things, but clearly, something more is needed.

Understanding the Problem Recurring Damage

The fact that this is happening
repeatedly after installing SPDs points away from random isolated events and more toward a systemic issue.

SPD Failure

The SPDs are sacrificial devices. They're designed to take the hit, and then they're done. The fact that the Siemens BoltShield tripped and the 100kA SPD on Unit 1 failed confirms they protected against overvoltage, but they were overwhelmed. A 35kA SPD at the panel may not be large enough for your situation if you are experiencing surges over that value.

Limited Protection

The fact that one unit survived while the other did not indicates the surge found its way to Unit 1 via another source, either through the wiring or even some other path such as a communication line.


Location, Location, Location

Being in a rural area with a farmhouse significantly increases the risk of power quality issues. Utility infrastructure in rural areas tends to be older, less maintained, and more susceptible to voltage fluctuations and surges. The fact that Unit 2 survived may be due to distance between the units and the electrical panel.

Grounding

You say it's "well grounded," but let's verify this.

Troubleshooting and Investigation - Priority Actions
1. Contact the Utility Company Immediately

This is your
top priority.

Report the Problem

Tell them you're experiencing repeated power surges that are damaging your equipment. Be specific about the dates, times, and the nature of the damage.

Request an Investigation

Ask them to investigate the power quality on their side of the meter. Specifically request that they check for:


Voltage fluctuations

Are there frequent voltage sags or swells?

Harmonic distortion

This can damage sensitive electronics.


Faulty equipment

Could a failing transformer, capacitor bank, or other utility equipment be the source of the surges?

Loose neutral

This is a common cause of voltage imbalances and surges. It can lead to significantly overvoltage on some circuits while others are undervolted.


Document Everything

Keep a detailed log of your communications with the utility, including dates, times, names of representatives, and the outcome of their investigations.2.

Grounding System Assessment (Verify, Verify, Verify)

Don't just assume it's good. Professionally verify the grounding system.

Ground Rods

How many ground rods do you have? Are they properly spaced and connected? Consider adding more ground rods to create a better grounding grid.


Ground Wire Size

Is the ground wire from the service entrance to the ground rods the correct size?

Bonding

Are all metal parts (metal water pipes, gas pipes, etc.) properly bonded to the grounding system?


Ground Resistance Test

Have a qualified electrician perform a ground resistance test to measure the effectiveness of your grounding system. Ideally, it should be 5 ohms or less.

Impedance Test

Have a qualified electrician perform an impedance test to verify your ground.3.

SPD Upgrade (Panel Level)

35kA is inadequate for your described situation. Upgrade it
immediately.

Higher Surge Capacity

Install a

much
larger whole-house SPD at your main electrical panel. Aim for at least 100kA per phase (or even higher, like 200kA). Consider a surge counter model to track how often it’s doing its job. Hardwired vs. Plug-in

Hardwired SPDs generally offer better protection than plug-in models.


Proper Installation

Ensure the SPD is installed as close as possible to the main breaker with the shortest possible lead lengths (wire between the SPD and the breaker). This minimizes inductance, which can reduce the SPD's effectiveness.4.

Layered Protection

Think of surge protection as a multi-layered defense.

Service Entrance

Large SPD at the main panel (as above).


Subpanels

Consider SPDs at any subpanels, especially if the mini-splits are fed from a subpanel.

Point-of-Use

SPDs at the mini-split disconnects are good, but make sure they are adequately sized and

high quality
. Dedicated Surge Strips

Use high-quality surge protector power strips for any sensitive electronics connected to the same circuits as the mini-splits.5.

Neutral-Ground Bonding

Verify that your neutral-ground bond is only at the service entrance panel. There should not be any other neutral-ground bonds downstream.6.

Wiring Review

Have a qualified electrician review the wiring to the mini-splits.

Dedicated Circuits

Ensure each mini-split has its own dedicated circuit.


Proper Wire Size

Verify the wire size is adequate for the load.

Tight Connections

Check all connections for tightness, both at the panel, disconnect, and the mini-split unit itself. Loose connections can cause voltage drops and other problems.


Conduit

Consider running the wiring in conduit to provide additional physical protection and shielding.7.

Lightning Protection System (If Applicable)

If you suspect lightning is a possibility, consider installing a professional lightning protection system for your house and outbuildings. This is a significant investment but may be necessary if lightning is a recurring threat.8.

Monitor Voltage Regularly

Get a voltage monitor and log. This helps you correlate spikes and surges.

Important Considerations



"Farmhouse in the Middle of Nowhere" Implications

The quality of power in rural areas can be significantly lower than in urban areas. Longer distribution lines, older equipment, and exposure to the elements can all contribute to power quality problems.


Documentation is Key

Keep meticulous records of everything: dates, times, events, conversations with the utility, repairs, and expenses. This documentation will be invaluable if you need to file a claim with the utility company or your insurance company.

Professional Help

Don't hesitate to hire qualified electricians, HVAC technicians, and potentially even a power quality consultant to help you diagnose and resolve this issue.

WWLFD (What Would Larry Fine Do?)


Larry Fine, being the meticulous and safety-conscious Stooge, would likely:1. Thoroughly investigate

He wouldn't just slap a band-aid on the problem. He'd meticulously check everything, from the utility connection to the grounding system.2.

Consult experts

He wouldn't be afraid to ask for help from qualified professionals.3.

Over-engineer

He'd probably install
multiple* layers of surge protection, just to be sure.4.

Document everything

He'd keep detailed records of all his findings and actions.5.

Wear safety glasses

Even for seemingly simple tasks, because you never know when Moe might be around with a hammer!

In Summary


This is a complex problem that requires a multi-faceted approach. By working with the utility company, verifying your grounding system, upgrading your surge protection, and seeking professional help, you can significantly reduce the risk of future damage to your mini-splits and other electronic equipment. Good luck! Flag for review