Topic: Busbar Size

User: NewElec, Location: Arkansas

Asked on: Saturday, August 24, 2024 at 12:47 pm EDT
Answered on: Thursday, March 6, 2025 at 1:36 am EST

Question: I have a 1200A, 3 phase, 3W bus with the following breakers in the SLD; 100A, 100A, 75A, 50A, 100A, 100A. In addition, there is a 200A ATS, 300A Meter, 300A Generator. The new addition would be a 200A breaker. According to 705.12(b), I would need to upsize the busbar. The EE states that is incorrect, but will not explain how that is possible. Can someone explain?

You're right, at first glance, 705.12(B) seems to require upsizing the busbar. Let's break down the code section and then explore scenarios where the EE might be correct (or perhaps overlooking something).

Understanding 705.12(B): Supply-Side Source Connection705.12(B) of the National Electrical Code (NEC) deals with the connection of interconnected electric power production sources (like your generator) on the supply side of the service disconnecting means. Here's the relevant excerpt:"(B) Load-Side Source Connections. One or more sources of electric power production shall be permitted to be connected to the load side of the service disconnecting means of a building or other structure where the sum of the overcurrent devices supplying power to a busbar or conductor shall not exceed the ampacity of the busbar or conductor."The key takeaway is that the sum of the overcurrent devices connected to the busbar cannot exceed the busbar's ampacity.Your Initial Assessment

You correctly identified the problem: Busbar Ampacity

1200A


Breakers

100A + 100A + 75A + 50A + 100A + 100A + 200A (new) + 300A (generator) = 1025A

Meter

300A (The meter doesn't directly contribute to the overcurrent calculation. It's measuring current
through the bus, not supplying it.)

ATS

200A (The ATS also doesn't directly contribute to the overcurrent calculation. It switches the source, but doesn't inherently add to the upstream breaker sum.)Based on this simple addition, 1025A <= 1200A, so the EE could be correct.

Possible Reasons Why the EE Might Think No Upsizing is Needed (and potential counterpoints)

Here are some possible explanations your EE might be using. Remember, the EE is responsible for code compliance, so they need to be able to clearly justify their interpretation. You should politely ask for their specific reasoning and code citations.1.

Diversity/Demand Factors

This is the most likely explanation. The EE might be claiming that not all of the connected loads will operate at their maximum current simultaneously. They might apply a demand factor to the total connected load before comparing it to the busbar ampacity.

How it Works

Demand factors are multipliers (less than 1.0) that reduce the calculated load based on the understanding that not everything is running full blast at the same time. For example, a demand factor of 0.8 applied to the 1025A of calculated load would reduce it to 820A, well below the 1200A busbar rating.


Code Justification

NEC Article 220 (Load Calculations) allows for demand factors in specific situations. The EE needs to identify which sections of Article 220 apply to the specific types of loads connected to the bus. For example, 220.42 covers general lighting, 220.53 covers appliance loads in dwelling units, and so on.

Why It Could Be Wrong

Demand factors
cannot be applied arbitrarily. They must be supported by specific code sections and based on the actual operating characteristics of the loads. If the demand factor is too aggressive and doesn't accurately reflect the real-world load profile, it violates the code. Further, demand factors are not likely to apply to generator capacity as the generator needs to supply 100% of the load.

The Burden of Proof

The EE must demonstrate the validity of the demand factor. They may need to provide load studies, historical data, or other evidence to justify it.2.

Breaker Rating vs. Actual Load

The EE might be claiming that the breakers are sized larger than the actual expected loads. While the breaker can handle that much current, the connected equipment will likely draw much less.

How it Works

For example, a 100A breaker might feed a motor that typically only draws 60A.


Why It Could Be Correct (But Unlikely)

This might be valid if there is documentation that the actual loads are significantly lower than the breaker ratings. However, it's generally bad practice to rely on this. Breakers should be sized appropriately for the connected load and provide overcurrent protection.

Why It Could Be Wrong (And Dangerous)

It's risky because if the equipment is upgraded or replaced with a higher-current device in the future, the breaker will be undersized and could nuisance trip or even fail to protect the circuit. Further, code requires that the breaker protects the wire and is suitable for the load downstream.3.

Generator is Never Online Concurrently with All Loads

This is a more subtle argument. The EE might be saying that the generator will
never be running at the same time as all of the other breakers are fully loaded.

How it Works

The ATS is designed to switch from utility power to generator power, so in an emergency, the generator only powers some of the load downstream and at most, the load downstream of the ATS.

Why It Could Be Correct (Potentially)

If the ATS is setup to only send emergency power downstream, this could reduce the load on the busbar, and thus a smaller breaker on the generator is acceptable.


Why It Could Be Wrong

Even with an ATS, the generator has the ability to backfeed current back to the busbar. The total current in the busbar cannot exceed 1200A.4.

Misunderstanding of 705.12(B)

The EE might be misinterpreting the code section. It's possible they are focusing on a different part of the code or overlooking the requirements of 705.12(B).

How to Address

Politely point out the specific wording of 705.12(B) and ask them to explain how their interpretation differs.
5.


Exception to the Rule

The EE could be trying to leverage an exception or an alternate interpretation.


How to Address

Ask them for a very specific code reference (section number) for the exception they are using. Carefully review that exception to see if it truly applies to your situation.

Steps to Take


Politely Request Clarification

Your first step should be to ask the EE to explain in detail their reasoning, citing specific sections of the NEC that support their position. Say something like, "I understand the busbar sizing requirements under 705.12(B), and I'm concerned that the addition of the 200A breaker and the generator connection will exceed the 1200A rating. Could you please walk me through your load calculations and explain which demand factors you are applying and how those are justified by the code?"2.

Review the Code Yourself

Carefully read Article 220 (Load Calculations) and Article 705 (Interconnected Electric Power Production Sources) of the NEC. Make sure you understand the rules and any applicable exceptions.3.

Document Everything

Keep a record of all communications with the EE, including the dates, times, and the specifics of their explanations.4.

Consult with Another EE (If Necessary)

If you are still unsure or unconvinced by the EE's reasoning, consider seeking a second opinion from another licensed electrical engineer. This is especially important if you have safety concerns.5.

Involve the Authority Having Jurisdiction (AHJ)

If you and the EE cannot agree on the correct interpretation of the code, the ultimate authority is the AHJ (usually the electrical inspector). You can request a formal interpretation from the AHJ. Their decision is binding.

In Summary:


While the EE might be correct if they are using valid demand factors supported by the NEC and documentation of actual loads, the burden of proof is on them to demonstrate that the busbar is adequately sized. Don't be afraid to ask questions and seek clarification until you are confident that the installation meets code requirements and is safe. Flag for review