Topic: Article 240 and Grounded Conductors

User: wwhitney, Location: Berkeley, CA

Asked on: Saturday, August 24, 2024 at 4:07 pm EDT
Answered on: Thursday, March 6, 2025 at 1:37 am EST

Question: Say I have a 240V 3P3W corner grounded system, and I use panelboards with just 2 busbars for the ungrounded conductors along with a terminal bar for the grounded conductors. OCPD is appropriately rated 240V to ground.Now I install a 2 pole 40A breaker with (2) #8 Cu ungrounded conductors, a #10 Cu grounded conductor, and a #10 EGC to supply a small panelboard that supplies a 30A 3-phase load plus a 10A 2-wire load supplied between the two ungrounded conductors.Does this comply with the NEC? If not, what code section is violated? [Note that an ungrounded conductor could fault to the #10 grounded conductor and carry 40A without tripping the OCPD, but the same is true of the #10 EGC.]Cheers, Wayne

Okay, let's break down the scenario and see if it complies with the NEC. You're correct that corner-grounded delta systems can present some nuances.

Analysis of the Installation

Here's a step-by-step assessment:1. Corner-Grounded Delta System

You're starting with a 240V 3-phase, 3-wire corner-grounded delta system. A key characteristic of this system is that one of the phase conductors is intentionally grounded.2.

Panelboard and Busbars

You have a panelboard with two ungrounded busbars (since one phase is grounded, you only need busbars for the two ungrounded phases) and a terminal bar for the grounded conductors. This is generally acceptable.3.

2-Pole 40A Breaker

You're feeding a subpanel with a 2-pole 40A breaker. Because you have a corner grounded system, the Voltage rating to ground must match the phase-phase Voltage rating.4.

Conductors



(2) #8 Cu Ungrounded Conductors

These are protected by the 40A breaker, so that's fine.


#10 Cu Grounded Conductor (Neutral)

This is where the big issue lies.

#10 Cu EGC

Adequacy of size depends on the OCPD protecting the circuit.5.

Loads



30A 3-Phase Load

Connected to the subpanel and presumably balanced across the two ungrounded phases and the grounded phase (which acts as the return path).

10A 2-Wire Load

Connected between the two ungrounded phases.

NEC Violations and Concerns


The most significant violations center around the grounded conductor (the equivalent of the neutral in this corner-grounded system):
NEC 250.24(C)(1) (Grounding Conductor): This section requires the grounding electrode conductor connection to the grounded conductor on the supply side of the service disconnecting means. It also addresses the size of the grounding electrode conductor. Although this section is not directly violated with the subpanel, it's relevant because it highlights the importance of proper grounding. The fundamental principle is that the grounded conductor provides a low-impedance path for fault current to return to the source, facilitating the tripping of the overcurrent protective device (OCPD). NEC 250.24(A)(5) (Grounded Conductor Brought to Service Equipment)

This section requires a grounded conductor to be run to the service equipment. This section has implications because it is the purpose of the grounded conductor to carry fault current back to the source.


NEC 215.2(A)(1) (Feeder Conductor Ampacity)

This section relates to the sizing of feeder conductors. Although the ungrounded conductors meet the OCPD rating, the grounded conductor does not.

Why the #10 Grounded Conductor is a Problem
Fault Current Path

In a corner-grounded system, the grounded phase acts as the return path for current. If a fault occurs between one of the ungrounded conductors and the grounded conductor, the resulting fault current needs a low-impedance path back to the source to trip the breaker. A #10 conductor might not be adequate for this purpose, especially under a high fault current condition.


Voltage Drop

Under normal conditions, the grounded conductor will carry the unbalanced current from the 3-phase load. A smaller conductor will experience a larger voltage drop, which could negatively impact the performance of equipment connected to the circuit.

Overheating

A sustained fault or overload could cause the #10 conductor to overheat and potentially create a fire hazard. While it may be true that the EGC could also carry 40A during a fault without tripping the breaker in some fault scenarios, the EGC is intended
only for fault current, not for continuous current carrying during normal operations. The grounded conductor is* intended to carry continuous current under normal operations.

Revised Approach


To comply with the NEC, consider the following:1. Size the Grounded Conductor Appropriately

The grounded conductor must be sized to carry the maximum unbalanced load it is expected to carry, but should not be smaller than what's dictated by the OCPD. Review NEC 250.24(A)(5). If you have a significant unbalanced load, you might need to upsize the grounded conductor.
2.


Consider Local Requirements

Always check with your local electrical inspector for any specific requirements or interpretations of the NEC in your jurisdiction.

In summary, while a corner-grounded delta system can be wired correctly using two-pole breakers and a terminal bar for grounded conductors, the key is to ensure that the grounded conductor is adequately sized to handle fault current and any expected unbalanced load. Your current scenario with the #10 grounded conductor likely violates the NEC due to insufficient ampacity for the potential fault current and continuous load.