Topic: Open Ground

User: SaltyDog, Location: 29148

Asked on: Saturday, August 24, 2024 at 4:51 pm EDT
Answered on: Thursday, March 6, 2025 at 1:37 am EST

Question: I have an existing yard outlet 100 feet from the panel that shows an open ground. It is fed by a two wire (No ground) cable and installed in a PVC box. How can I ground it and install a GFCI outlet in the PVC box?

Okay, let's address grounding that outdoor outlet with an open ground using GFCI protection. Given the situation, here's a breakdown of options and considerations, prioritizing safety and code compliance

Understanding the Situation and Limitations
Open Ground

This is a potentially dangerous situation. A ground wire is a critical safety feature, providing a low-resistance path for fault current back to the source, allowing a circuit breaker to trip quickly in case of a short circuit. Without it, metal parts of appliances or tools connected to the outlet could become energized, posing a shock hazard.


Two-Wire Cable (No Ground)

This is an older wiring method that is no longer permitted in most new installations. Upgrading the cable is the best practice and the NEC requires it be replaced when practical.

GFCI Outlet

A Ground Fault Circuit Interrupter (GFCI) is designed to detect small imbalances in current between the hot and neutral wires, indicating a leakage to ground. It will quickly trip the circuit, protecting against electric shock. However, a GFCI
doesn't create a ground. It only detects ground faults.

PVC Box

PVC is non-conductive. It's a good choice for outdoor locations as it won't corrode. However, it provides no grounding path itself.

Acceptable Options (with caveats and ranked in order of preference)


Run a New 3-Wire Cable (Best Practice)



How

The ideal solution is to replace the existing two-wire cable with a new three-wire cable (hot, neutral,
and ground) from the panel to the outdoor outlet location.

Advantages

This provides a proper, code-compliant ground, offering the highest level of safety.

Disadvantages

This involves the most work and expense, potentially requiring trenching, conduit installation, and working within the electrical panel.


Considerations

Before doing this, verify that your electrical panel has available breaker slots and sufficient capacity. Also, check your local codes for requirements regarding burial depth, conduit types, and permitted wiring methods.2.

Grounding Electrode Rod (Supplemental Ground)



How

Drive a grounding electrode rod (usually copper or copper-clad steel, typically 8 feet long) near the outlet location. Connect a #6 AWG copper wire (or as required by local code) from the ground terminal of the GFCI outlet to the grounding rod using approved connectors (ground clamps). Install a GFCI outlet in the box. Label the outlet "GFCI Protected. No Equipment Ground".


Advantages

Can provide some level of ground fault protection, but it is not a substitute for a properly installed equipment grounding conductor.

Disadvantages

Requires driving a grounding rod. Not a true equipment ground.3.

GFCI Protection with Labeling (Acceptable Minimum, NEC compliant
only if other options are not available)



How

Replace the existing outlet with a GFCI outlet. Crucially, label the outlet cover plate with a sticker that says "GFCI Protected. No Equipment Ground." (These stickers usually come with GFCI outlets). Install a GFCI outlet in the box.

Advantages

Provides a significant level of shock protection by tripping quickly in the event of a ground fault.


Disadvantages

The "ground" terminal of the GFCI outlet will not be connected to anything. Appliances plugged into this outlet will still not have a proper equipment ground. Surge protectors will not function correctly.

NEC Justification

The National Electrical Code (NEC) allows for the use of GFCI protection in place of an equipment ground in certain situations,
especially when retrofitting existing ungrounded circuits. This is because GFCI protection significantly reduces the risk of electric shock, even without a ground wire.

Important

If you extend the circuit from this GFCI outlet (e.g., by plugging in a power strip), the downstream outlets must also be GFCI-protected and labeled as "GFCI Protected. No Equipment Ground."

Steps (assuming you are using the GFCI with Labeling option)


Safety First: Turn Off the Circuit Breaker

Before doing any electrical work, locate the circuit breaker that controls the outlet and switch it to the "OFF" position. Test the wires at the outlet with a non-contact voltage tester to ensure the power is off. Double-check!2.

Remove the Existing Outlet

Carefully remove the old outlet from the box.3.

Identify Wires

Identify the hot (usually black) and neutral (usually white) wires.4.

Connect the GFCI Outlet

Connect the hot wire to the terminal marked "Line" and "Hot" (or similar). Connect the neutral wire to the terminal marked "Line" and "Neutral" (or similar).

Do NOT connect anything to the ground terminal (it will be left unconnected).
5. Mount the GFCI Outlet

Carefully tuck the wires back into the box and mount the GFCI outlet securely.6.

Install the Cover Plate and Label

Install the cover plate and apply the "GFCI Protected. No Equipment Ground" label.7.

Test the GFCI Outlet

After restoring power, test the GFCI outlet by pressing the "Test" button. The "Reset" button should pop out, indicating that the GFCI is working correctly. Press the "Reset" button to restore power to the outlet.

Important Considerations and Warnings



Local Codes

Always consult your local electrical codes and building codes. They may have specific requirements that differ from the NEC. In some jurisdictions, the labeling option might not be permitted.

Qualified Electrician

If you are not comfortable working with electricity,
hire a qualified electrician. Electricity is dangerous, and improper wiring can lead to serious injury, death, or fire.

Testing

After any electrical work, thoroughly test the outlet and any devices connected to it to ensure they are working correctly and safely.

Limitations

Be aware of the limitations of GFCI protection. It protects against shock but doesn't provide a true equipment ground for appliances and tools. Some devices (e.g., surge protectors) may not function correctly without a proper ground.


Future Upgrades

Consider replacing the two-wire cable with a three-wire cable in the future for optimal safety.

In summary, while a GFCI outlet with proper labeling is the minimally acceptable solution in your case, replacing the cable with a three-wire cable is the safest and most code-compliant option.
Always prioritize safety and consult with a qualified electrician if you have any doubts or concerns. Flag for review