Topic: EVSE Terminals

User: TwistLock, Location: California

Asked on: Saturday, August 24, 2024 at 10:14 pm EDT
Answered on: Thursday, March 6, 2025 at 1:38 am EST

Question: Picked up a clients EVbox EVSE today (Benz version). The line terminals are push in. Seems a little sketchy for continuous use equip .. no?There’s no wire range listed just says use 4awg.I spoke with EVbox’s weak sauce support and they said stranded is fine to insert without ferrule, though they have no documentation about using smaller gauges than 4awg, other than to say “…the engineer said it should be fine”.I released one of the factory assembled push in terminals going to the J1772 and noted they used a crimped ferrule (about the diameter of a solid #10 fwiw).Just wondering if these push in terminals are the trend, or just the cheapest way to manufacture.In my case I can only give customer 24a and will be inserting #10 stranded lol - so (I guess) I’m not too worried about overheating.

You've hit on a few key concerns and inconsistencies with the EVbox's design and support. Here's a breakdown of your issues and some potential solutions and considerations

Your Concerns are Valid:
Push-in Terminals for High-Current EVSEs

Push-in terminals are indeed less common and generally viewed with more skepticism than screw-down or lug-based connections for continuous high-current applications like EV charging. The reliance on spring pressure alone to maintain a secure connection over years of thermal cycling and vibration is a point of concern.


Lack of Wire Range and Clear Documentation

The absence of a published wire range is a red flag. This is a fundamental specification that manufacturers must provide for safe and compliant installation. Saying "4 AWG only" and then vaguely "it should be fine" for smaller gauges is unacceptable from an engineering and liability standpoint.

Stranded Wire and Ferrules

While stranded wire
can be used in push-in terminals, ferrules are almost always recommended, especially for larger gauge wires. Ferrules prevent fraying of the strands, provide a more uniform contact area, and reduce the risk of corrosion. The fact that EVbox uses ferrules internally on the lower-current J1772 wiring is telling.

Engineer Says vs. Written Specification

"The engineer said" is not a substitute for documented and tested specifications. This puts you, the installer, in a precarious position if there's ever a problem.

Your Situation and Options


Mitigating the Risk with #10 AWG at 24A



Ferrules are a Must

Given the situation,
always use properly sized ferrules on your #10 stranded conductors before inserting them into the push-in terminals. Use a quality crimper designed for ferrules.

Torque Testing (If Possible)

Try lightly pull on the wires (after de-energizing, of course) to ensure they are securely connected.

Thermal Monitoring

After commissioning, use a thermal camera or non-contact thermometer to monitor the temperature of the terminals under load. Check them after the first few charging sessions and periodically thereafter. Look for any signs of overheating (excessive heat compared to other components).


Regular Inspections

Advise your client to have the EVSE inspected periodically (e.g., annually) by a qualified electrician.2.

Documentation is Key



Document Everything

Meticulously document your installation, including:
Date of installation EVbox model number Your rationale for using #10 AWG (reduced amperage requirement) The use of ferrules, the brand and model of ferrule and crimper used Photos of the wiring and terminals before and after installation. Records of thermal monitoring. Your conversation with EVbox support (include the name of the person you spoke with and the date).

Cover Your Ass(ets)

This documentation will be invaluable if there are ever any issues.3.

Escalate with EVbox (Further Attempts)



Demand Written Confirmation

Insist on getting written confirmation from EVbox (email) that #10 AWG with ferrules is acceptable for a 24A load, referencing your specific model and circumstances. If they refuse, that's a very strong indication that they are not confident in their product's performance under these conditions.

Go Higher Up

If you're getting the runaround from Tier 1 support, ask to speak to a senior engineer or a supervisor.


Safety Concerns

Frame your concerns in terms of safety and liability. This might get their attention.4.

Alternative EVSE (If Possible)



Suggest a Different Model

If your client is open to it, explore other EVSE brands that use more robust connection methods (screw-down terminals, lugs) and have clear documentation for a range of wire gauges.


Justification

Explain that the EVbox's lack of clear documentation and reliance on push-in terminals is a potential safety risk.5.

Code Compliance



Local Inspectors

Consult with your local electrical inspector about the acceptability of this installation. They may have specific requirements or concerns about push-in terminals in this application.


NEC

While the NEC doesn't specifically prohibit push-in terminals for EVSEs, it emphasizes the importance of using listed and labeled equipment according to the manufacturer's instructions. If EVbox's instructions are vague or contradictory, it puts the installation in a grey area.

Are Push-in Terminals a Trend?


Push-in terminals are used in some electrical devices, especially in lower-current applications (lighting fixtures, receptacles, etc.). However, for high-current applications like EV charging, they are not the dominant trend. Screw-down terminals and lugs are still the preferred methods for robust and reliable connections.

In Summary:

You're right to be concerned. The EVbox's design and lack of clear documentation are less than ideal. Mitigate the risks by using ferrules, documenting everything, and attempting to get written confirmation from EVbox. If possible, explore alternative EVSEs with more robust connection methods. Safety should always be the top priority. Flag for review