Topic: Fuse protection of two small motors on same circuit.

User: marine_sparks, Location: seattle

Asked on: Sunday, August 25, 2024 at 4:18 am EDT
Answered on: Thursday, March 6, 2025 at 1:38 am EST

Question: I'm looking at a dual motor system with two 230v, 260 watt single phase motors that always run at the same time. One set of capacitors starts both motors. Protection is by a single external 6a fuse, and thermal protection devices inside each motor. I calculated FLA of each motor at 1.4 amps.Can this single fuse protect each motor from overcurrent?

Let's break down the problem to determine if a single 6A fuse can adequately protect your dual motor system

Understanding the Protection Needed
Overcurrent

Overcurrent is any current exceeding the rated current of a conductor or equipment. This could be an overload (running above rated load but not a short circuit) or a short circuit.


Overload

An overload is a condition where the motor draws more current than its rated current, but not so much that it's an immediate short circuit. This is a common cause of motor failure due to overheating.

Short Circuit

A short circuit is a very high current flow due to a low-resistance path to ground or another phase. It's usually a catastrophic failure.


Fuse Purpose

Fuses are primarily designed to protect against short circuits and high-level overcurrents. They can provide some overload protection, but they are typically not as precise or responsive as dedicated overload protection devices.

Thermal Protection Devices

Thermal protection inside the motors are specifically designed to protect against
overload conditions by sensing the motor winding temperature and tripping if it gets too hot.

Analysis of your Situation
1. Total FLA

Since both motors run simultaneously, the total full load amperage (FLA) of the system is 1.4A + 1.4A = 2.8A.
2.


Fuse Size vs. Total FLA

The 6A fuse is more than double the total FLA of the system (6A / 2.8A = 2.14).
3.


Starting Current (Inrush Current)

Motors draw a significantly higher current (typically 5-7 times FLA) during the starting phase. This is a very brief surge. The fuse
must be able to withstand this inrush current without blowing. A slow-blow fuse is likely needed.4.

Individual Motor Overload Protection

The critical question is:
What happens if ONE motor experiences an overload, but the other motor is running normally?

If one motor is overloaded and drawing, say, 2.5 amps, while the other is drawing 1.4 amps, the total current draw is 3.9 amps. This is below the 6 amp fuse rating. The fuse will not blow. The overloaded motor will continue to overheat until its thermal protection trips. Therefore, if the thermal protection fails in a single motor, the 6A fuse will NOT protect the motor from overload. The overloaded motor could fail before the fuse blows.


ConclusionThe 6A fuse will likely provide short-circuit protection for the
entire system. However, it does NOT provide adequate overload protection for individual motors in this dual-motor setup, especially if their internal thermal protection fails.

RecommendationsTo improve overload protection:1.

Smaller Fuse

A smaller fuse might be more responsive to an overload, but you risk nuisance tripping during motor start-up. You would need to carefully test with different fuse sizes to find the smallest fuse that doesn't trip during starting.2.

Individual Motor Fuses/Circuit Breakers

The
best solution would be to use a separate fuse or circuit breaker for each motor, sized closer to the FLA of each motor. For example, a 3A slow-blow fuse for each motor might provide better overload protection.3.

Motor Starter with Overload Relays

Consider using a motor starter with overload relays for each motor. These relays are specifically designed to trip quickly and reliably on overload conditions.4.

Monitor Motor Temperatures

Implement a system to continuously monitor the temperature of each motor winding. This can provide an early warning of potential overloads and allow for preventative maintenance.5.

Ensure Thermal Overload Protection is Working

Regularly test the thermal overload protection devices inside the motors.

Important Considerations


NEC/Local Codes

Always consult the National Electrical Code (NEC) and your local electrical codes for specific requirements regarding motor protection. The NEC often dictates the required type and size of overcurrent protection devices for motors.

Slow-Blow Fuses

Use slow-blow (time-delay) fuses. These fuses can handle the brief inrush current of the motors during start-up without tripping.


Motor Service Factor

Motors are often designed with a "service factor," which allows them to operate safely above their rated horsepower for short periods. However, exceeding the service factor continuously will significantly reduce the motor's lifespan.

In summary, while your current setup provides some protection, it's not optimal for individual motor overload protection. You should strongly consider implementing one of the recommended solutions to improve the reliability and longevity of your dual-motor system. Consult with a qualified electrician to ensure that your system meets all applicable electrical codes and provides adequate protection for your motors. Flag for review