Question: In NYC I am doing a fire alarm system design for a existing R2 residential portion of the building with 4 separate residential lobbies with no front desk. The building is mixed use, 1st floor has commercial units. The entire building shares the same sprinkler system and has a fire pump and multiple electric services and same block and lot. This building is considered a high rise because it is more than 75 feet tall.I have some questions and because it's considered a high-rise it means that:1) ARCS system must be designed and installed (will try to attempt to get a waiver but FDNY requires certificate of occupancy which the building does not have). What should I do if there is no certificate of occupancy?2) All the fire command stations must be located in the all the 4 lobbies as per NYC BC 911.1 and NYC FC 907.4.1. This will affect the aesthetics of the lobbies and the lobbies doesn't even have a front desk. Is there any alternative? Has anyone had FDNY ever approved just to install remote annunciator at the lobby without a fire command stations in the lobbies?3) It will require a fire command station printers as per NYC FC 907.4.2. Where should this printer be located? In all the lobbies? Again, this will affect aesthetics of the building and the building does not have a front desk!4) Speakers for 1-way voice communication need to be installed in each dwelling unit as per NYC FC 907.5.2.2. This is a huge burden! Apartment owners will not be happy. We need to run new conduits for the speakers into all of the apartments which will damage finishes. Is there any alternative?
Okay, designing a fire alarm system for an existing high-rise R-2 building in NYC with multiple lobbies and no front desk presents some significant challenges, especially regarding the stringent FDNY requirements. Let's break down your questions
Understanding the Landscape:
High-Rise Definition
Because your building is over 75 feet, it triggers the high-rise provisions of the NYC Building Code and Fire Code. This adds a layer of complexity, especially with existing buildings.
R-2 Occupancy
This is crucial. R-2 means residential, primarily multi-family dwellings. The fire alarm requirements are geared towards protecting occupants within their units and providing a means of evacuation or in-place sheltering as dictated by the fire safety plan.
Sprinklered Building
Full sprinkler protection does offer some flexibility in code application, but doesn't eliminate many of the core requirements for a high-rise.
Existing Building
This is key. The code recognizes that full compliance with new construction requirements can be extremely difficult and expensive in existing buildings. You should strongly emphasize this during any negotiations with the FDNY.
Answering Your Questions
1. ARCS System and Certificate of Occupancy
The ARCS Requirement
Yes, a high-rise building typically requires an Auxiliary Radio Communication System (ARCS) to ensure reliable communication for FDNY personnel within the building during an emergency.
The Waiver Attempt
Pursuing a waiver is the right approach. Start the conversation ASAP.
No Certificate of Occupancy
Historical Records
Search extensively for any historical building permits, alteration permits, or documentation that might serve as a de facto C of O. Contact the Department of Buildings (DOB) archives for older records.
Engage a Code Consultant
A code consultant who specializes in NYC fire safety regulations can be invaluable. They have experience navigating these issues with the FDNY and can help build a case for a waiver or identify alternative compliance strategies.
Focus on Safety
Frame your arguments for a waiver around enhancing fire safety in other ways. For example, enhanced fire alarm system design and detection, early warning, improved means of egress.
2. Fire Command Stations in Lobbies
Code Requirements
NYC BC 911.1 and FC 907.
4.1 do typically require a fire command center in high-rise buildings. In residential buildings without a front desk, the lobbies become the default location.
Aesthetic Impact and Alternatives
This is a major hurdle and needs careful negotiation. Here are some options to explore:
Remote Annunciator Panels ONLY
This is a critical point of discussion. Present a formal proposal to the FDNY requesting to install remote annunciator panels in the lobbies instead of full fire command stations. Annunciator panels will allow FDNY to identify the zone in which the fire alarm has been activated but without all the other controls that would be available at a command station. Here's the argument:
Limited Functionality Needed
Argue that a full command station is excessive for unsupervised lobbies. Emphasize that the primary function in a residential building is to notify occupants and facilitate evacuation (or in-place sheltering), which can be achieved with annunciators.
Sprinkler Protection
Point out the full sprinkler system. This reduces the risk of rapid fire spread.
Consolidated Command Center
Could you propose a single fire command center in a secure location (e.g., near the fire pump room, a superintendent's office) that is accessible to FDNY via a Knox Box or similar secure access system? This would need FDNY approval and a clear plan for emergency access.
Minimizing the Footprint
If a fire command station is unavoidable, explore ways to minimize its size and visual impact:
Recessed Mounting
Can the panels be recessed into the wall to reduce protrusion?
Discreet Enclosures
Work with an architect to design an enclosure that blends with the lobby décor.
Documentation is Key
Every proposed alternative needs to be documented in a detailed proposal submitted to the FDNY for approval.
3. Fire Command Station Printer
Location
If a full fire command station is required (even a minimized one), the printer would ideally be located within that station.
Lobby Concerns
Placing a printer in each of the 4 unsupervised lobbies is extremely impractical and invites vandalism.
Alternative
If you get approval for remote annunciators only, argue that a printer is not necessary in the lobbies. If you get approval for a consolidated command center, place the printer there.
4. 1-Way Voice Communication (Speakers in Apartments)
This is a Significant Challenge
You are correct; this is a major concern for building owners and residents. Retrofitting speakers into every apartment unit is disruptive, costly, and can damage finishes.
Alternative Considerations
Evaluate the Fire Safety Plan
How is evacuation or in-place sheltering handled? How would occupants be notified in a fire emergency?
Speak with FDNY Engineers
Seek guidance from an FDNY engineer during the design phase and ask them if the Fire Alarm system can perform a coded signal to the existing horns in all the residential apartments.
Consider a Phased Approach
If voice communication is unavoidable, could you propose a phased implementation, prioritizing certain floors or units first?
Documentation and Justification
Document every attempt to find alternatives, including discussions with the FDNY.
General Strategies and Recommendations
Engage FDNY Early and Often
Don't wait until the design is complete to talk to the FDNY. Schedule a meeting with the relevant plan examiners and fire prevention personnel early in the process to discuss your challenges and proposed solutions. Building a collaborative relationship is critical.
Hire an Experienced NYC Fire Alarm Consultant
This is not a DIY project. You need someone familiar with the NYC Building and Fire Codes, FDNY procedures, and who has a track record of successful approvals.
Document Everything
Keep meticulous records of all meetings, conversations, and correspondence with the FDNY and other stakeholders.
Be Prepared to Compromise
The FDNY may not approve every request. Be prepared to negotiate and find solutions that balance code compliance with practicality and cost.
Focus on Overall Safety
Emphasize how your fire alarm system design will enhance the overall fire safety of the building.
Key Takeaways
Existing High-Rise = Negotiation
Expect to negotiate extensively with the FDNY to find the most practical and cost-effective solutions.
Documentation is Paramount
Thorough documentation is essential to support your arguments and demonstrate your commitment to code compliance.
Engage Experts
A qualified fire alarm consultant and possibly a code consultant are invaluable resources.
Prioritize Safety: Frame your arguments around improving the overall safety of the building for its residents.Good luck with your project! This is a challenging situation, but with careful planning, expert advice, and open communication with the FDNY, you can achieve a compliant and effective fire alarm system. Flag for review