Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Grounding Electrode Conductor Size

User: dvcraven052256, Location: St. Louis, missouri

Asked on: Monday, August 26, 2024 at 9:51 am EDT
Answered on: Thursday, March 6, 2025 at 1:39 am EST

Question: If I have a ground rod that is my sole purpose for grounding an electrical service is the GEC sized per 250.66. I know the code says if connecting to an rod or pipe the minimum size can be #6 copper.

You are correct in your understanding of the basic requirements. Let's break it down for clarity and cover a few nuances

General Rule (250.66):

The size of the grounding electrode conductor (GEC) is generally determined by the size of the ungrounded (hot) conductors of the service entrance. You use Table 250.66 in the NEC to find the appropriate GEC size based on the service entrance conductor size.

The Exception for Rod, Pipe, and Plate Electrodes (250.66(A), 250.66(B))



If you are connecting
only to a ground rod, ground pipe, or plate electrode, the sole purpose is to ground the service, the GEC never needs to be larger than #6 AWG copper (or #4 AWG aluminum/copper-clad aluminum).
In summary



If your ONLY grounding electrodes are rod, pipe, or plate, and their sole purpose is to ground the service, use #6 AWG copper (or #4 AWG aluminum/copper-clad aluminum) as your GEC.
You don't need to consult Table 250.66 based on the service entrance conductor size in this specific scenario.

Important Considerations and Clarifications



Multiple Electrodes

If you have
multiple grounding electrodes (e.g., a ground rod AND a metal water pipe), the GEC to the other electrodes (like the water pipe) must be sized according to Table 250.66 based on the size of the service entrance conductors. The only exception that allows a reduced size is specifically for the connection to a rod, pipe, or plate electrode, and ONLY when those are the sole grounding electrodes for the service.

Concrete-Encased Electrode (Ufer Ground)

This exception does not apply to concrete-encased electrodes (Ufer grounds). A GEC connecting to a Ufer ground must always be sized per Table 250.66.

Structural Metal

This exception
does not apply to the grounding electrode connection to the building's metal frame. A GEC connecting to the building's metal frame must always be sized per Table 250.66.

Exothermic Welds

Ensure that connections to ground rods are made with approved methods (e.g., exothermic welds, listed connectors).

Continuous

The GEC must be continuous (no splices) unless spliced by irreversible compression-type connectors listed as grounding and bonding equipment or by the exothermic welding process.


250.53(G)

The supplemental electrode is not required to be connected to the ground ring or to the grounding electrode conductor. This rule is an exception to the requirement that all electrodes be bonded together. This is usually done in higher voltage applications.

250.64(F)

The grounding electrode conductor must be installed in one continuous length.

Why the Exception?


The reasoning behind the #6 AWG (or #4 AWG AL) limit for rod, pipe, and plate electrodes is primarily related to their relatively poor impedance characteristics. After a certain size, increasing the GEC size doesn't significantly improve the electrode's ability to dissipate fault current. The impedance of the earth around the electrode is often the limiting factor.

Example

You have a 200 amp service entrance (typically using #2/0 AWG copper conductors).


Standard Rule (Table 250.66)

If you were using a water pipe as your grounding electrode, Table 250.66 would likely require a #4 AWG copper GEC.*

Rod Electrode Only

Because you are only using a ground rod, and no other grounding electrodes, your GEC only needs to be a #6 AWG copper (or #4 AWG aluminum).

Always consult the latest edition of the NEC for the most up-to-date requirements and consult with a qualified electrician for specific installations.
Electrical codes can be complex and vary by jurisdiction. This information is for educational purposes only and should not be considered a substitute for professional advice. Flag for review

Previous Question Next Question