Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Grounding Electrode Size

User: dvcraven052256, Location: St. Louis, missouri

Asked on: Monday, August 26, 2024 at 9:57 am EDT
Answered on: Thursday, March 6, 2025 at 1:39 am EST

Question: I have a 1600 amp service. If connection is to a ground rod only does the GEC required to sized per 250.66 and not #6 cu. as permitted if connecting to rod or pipe.

Yes, you are correct. If your 1600 amp service is connected only to a ground rod (or rods), the Grounding Electrode Conductor (GEC) must be sized according to NEC 250.66. The exception allowing a #6 copper conductor applies only when the electrode is a rod, pipe, or plate and is the only electrode present.Here's the breakdown: 250.66

This section provides the general rule for sizing the GEC based on the size of the service-entrance conductors. You'll need to look at the size of your service entrance conductors to determine the required GEC size.


250.66(A) Exception

This is the exception you are referring to, and it states: "If the grounding electrode conductor is connected to a ground rod, ground pipe, or plate electrode as permitted in 250.52(A)(5) or (A)(7), that portion of the conductor that is the sole connection to the grounding electrode shall not be required to be larger than 6 AWG copper wire or 4 AWG aluminum wire." The critical word is "sole". If you have other grounding electrodes (like a metal water pipe or building steel) that are also part of your grounding system, this exception does not apply.

In your case

You specifically state the connection is only to a ground rod. Even though it's only to a ground rod, because your service is 1600 amps, the GEC will almost certainly need to be larger than #6 copper, as determined by 250.66 and using the service entrance conductor size.

Important Considerations



Other Grounding Electrodes

Does your building have any other available grounding electrodes as described in 250.52(A), such as a metal water pipe (with specific requirements), building steel, or a concrete-encased electrode (rebar)? If so, these need to be bonded together according to NEC 250.50 to form a complete grounding electrode system. Connecting all these electrodes will affect how you run and size your GEC.


Local Amendments

Always check with your local electrical inspector. Municipalities can have amendments to the NEC that affect grounding requirements.

In summary,
with a 1600 amp service and only a ground rod electrode, you must size the GEC according to 250.66, which will likely require a conductor larger than #6 copper. Make sure all grounding electrodes are properly bonded and that the connection is made properly per code. Consult with a licensed electrician to ensure your grounding system meets all applicable code requirements. Flag for review

Previous Question Next Question