User: jjwitty, Location: Indianapolis
Asked on: Monday, August 26, 2024 at 11:31 am EDT
Answered on: Thursday, March 6, 2025 at 1:40 am EST
Question: Need some guidance for a service feed for a motor control panel.The 480 panel will feel 9, 3p, 18hp motors and 9, 3p, 5hp motors. Each motor will have 120v control circuit, and the 5hp motors will have a temperature controller.The 15hp motors are used for pumping oil in/out, the 5hp motors are used to heat up the oil.Here is the tricky part:The motors cannot all run at the same time. Only one blender is able to pump at once, and all heat exchangers won't be used at once. What is the minimum service feed we can add for this panel? The contractor we first talked to wants to add a 200 amp service, which would align with the scenario of all motors running at once. That would require a 500' run from our main MCC. Another option is underrating the panel and feeding out of a subpanel, but this needs to be within code.What is code for the minimum usage? We have existing panels with up to 20 motors on a 100 amp circuit.
Okay, let's break down the process for determining the minimum service feed for your motor control panel, considering the non-simultaneous operation of your motors. This requires a calculated load approach.1. Understanding the Code (NEC - National Electrical Code) Article 430 (Motors, Motor Circuits, and Controllers)
This is the most critical article.
Article 220 (Branch-Circuit, Feeder, and Service Calculations)
Provides the general methods for calculating electrical loads.
Article 310 (Conductors for General Wiring)
Determines ampacity and sizing of conductors.
Key Concepts from Article 430 (Simplified)
Largest Motor
The largest motor's full-load current (FLA) is a primary driver of your calculations. You use a percentage of its FLA for feeder sizing.
Secondary Motors
The FLAs of the remaining motors are added at 100%.
Control Circuit
The voltage will need to be factored into the calculation.
Duty Cycle
Your application has an intermittent duty cycle. This MUST be considered.
Overcurrent Protection
Fuses or circuit breakers must protect the conductors based on the calculated load.
Motor Nameplate
This is where you get the FLA.
2. Gathering the Necessary Data Motor Nameplate Data
You must have the following from the motor nameplates: Horsepower (HP) - You have this. Voltage (V) - You have this (480V). Full-Load Amps (FLA) - This is critical! Look this up for each motor if it's not on the nameplate. Tables 430.250 in the NEC provide typical FLA values for 3-phase motors at 460V. However, always prioritize the nameplate data.
Service Factor (SF) - If it's greater than 1.0, it influences the calculation.
Control Circuit Load
Determine the VA (volt-amperes) or watts of each 120V control circuit. This information is crucial. A safe estimate is 100VA per control circuit, unless you know better.
Temperature Controller Load
Get the VA or watts of each temperature controller.
3. Performing the Load Calculations (Step-by-Step)
Step 1: Determine the Largest Motor. You have nine 18HP motors. These are the largest.
Step 2: Calculate the FLA of each motor. 18HP Motors (9 total)
Use NEC Table 430.250 (or the nameplate) to find the FLA for a 460V, 18HP, 3-phase motor. Let's assume, for example, the FLA is 22 amps (this could be higher or lower depending on the motor's design, so check the table).
5HP Motors (9 total)
Use NEC Table 430.250 (or the nameplate) to find the FLA for a 460V, 5HP, 3-phase motor. Let's assume, for example, the FLA is 6.7 amps (again, verify this!).
Step 3: Apply the Largest Motor Factor. According to NEC 430.24, you use 125% of the largest motor FLA for feeder sizing. In your case, that's 1.25 22 amps = 27.5 amps.
Step 4: Calculate the Remaining Motor Load. Since only one 18HP motor can run at a time (one blender), you do not include the other 8 in this calculation. They are not simultaneous loads. You need to determine the maximum number of 5HP heaters that will operate simultaneously. Let's assume, for example, that a maximum of 3 heaters can run at once. Therefore, you include the FLA of only 3 5HP motors in this step. That's 3 6.7 amps = 20.1 amps.
Step 5: Sum the Motor Loads. Add the adjusted largest motor load to the remaining motor load: 27.5 amps + 20.1 amps = 47.6 amps.
Step 6: Calculate the Control Circuit Load. You have 18 motors with control circuits. Assume each is 100VA at 120V. That's 18 100VA = 1800VA. Convert VA to amps at 480V, 3-phase: Amps = VA / (Voltage sqrt(3)) = 1800VA / (480V 1.732) ≈ 2.17 amps.
Step 7: Calculate the Temperature Controller Load. You have 9 temperature controllers. Assume each is 50VA (check their specs!). That's 9 50VA = 450VA. Convert VA to amps at 480V, 3-phase: Amps = VA / (Voltage sqrt(3)) = 450VA / (480V 1.732) ≈ 0.54 amps.
Step 8: Sum All Loads. Add the motor load, control circuit load, and temperature controller load: 47.6 amps + 2.17 amps + 0.54 amps = 50.31 amps.
Step 9: Consider Future Expansion (Optional, but Recommended). Add a safety margin of 25% or more to the calculated load. This will help if you add motors later. 50.31 amps 1.25 = 62.89 amps.
Step 10: Determine Minimum Feeder Ampacity. Your minimum feeder ampacity, based on this example, would be approximately 63 amps (rounding up).
Step 11: Select Feeder Conductor Size. Use NEC Table 310.16 to select the appropriate conductor size based on the ampacity required and the conductor insulation type (e.g., THHN, THWN). Make sure to consider the ambient temperature and derating factors if necessary (see NEC 310.15). You'll likely need at least #4 AWG copper or #2 AWG aluminum conductors.
Step 12: Select Overcurrent Protection Device (Breaker or Fuses). The overcurrent protection device should protect the conductors. You can use a standard size breaker larger than the calculated ampacity, but it must not exceed the conductor ampacity. A 70 amp breaker should be acceptable for this application.
Step 13: Consider Voltage Drop. With a 500' run, voltage drop will likely be a concern. NEC 215.2(A)(1) recommends voltage drop on feeder conductors not exceed 3% for power, heating, and lighting loads, or 5% total. You'll need to calculate the voltage drop based on the conductor size, load, and distance. A larger conductor may be required to mitigate voltage drop. There are online voltage drop calculators to assist.
Important Considerations and Caveats
Verify Motor FLA
This is the most important step. Never rely solely on the typical values in the NEC tables. Always use the motor nameplate data.
Simultaneous Operation
The entire calculation hinges on your accurate assessment of which motors can and cannot run at the same time. If there's a chance more heaters could run simultaneously, adjust the calculation accordingly. Err on the side of caution.
Demand Factors
NEC 220.20 allows demand factors to be applied under certain circumstances. However, these are typically used for entire building loads, not individual motor control panels. I would not recommend applying demand factors in this case.
Short-Circuit Current Rating (SCCR) of the Panel
Make sure the SCCR of your motor control panel is sufficient for the available fault current at its location. This is a critical safety requirement. The contractor should be able to help you with this calculation.
Local Codes and Regulations
Always comply with all applicable local codes and regulations.
Professional Review
This is a complex calculation.
It is strongly recommended to have a qualified electrical engineer review your calculations and design to ensure code compliance and safety.
Regarding the 200 Amp Service
The contractor's initial suggestion of a 200 amp service is likely based on a "worst-case" scenario of all motors running simultaneously. While this is a conservative approach, it may be unnecessary and costly given your operating constraints. However, it's safer than undersizing.
Regarding Underrating the Panel
You can not intentionally underrate the service feed to the point where it violates the NEC. The calculated load must be supported by the feeder conductors and overcurrent protection. Using a subpanel may be an option if the subpanel is properly sized and the feeder to that subpanel can handle the calculated load.
Next Steps
Gather Motor Nameplate Data
Get the FLA for each motor.2.
Verify Simultaneous Operation
Double-check the operating scenario to be 100% sure of which motors can run at the same time.3.
Calculate the Load
Follow the steps outlined above.4.
Consult with a Qualified Electrical Engineer
Have your calculations reviewed by a professional engineer.
In summary, with careful planning and a thorough understanding of the operating conditions, you can likely reduce the size of the service feed needed for your motor control panel. The example calculation shows that you can likely use a 70 amp breaker, with #4 AWG conductors. This may be the minimum feed allowed, but consulting with a qualified professional is required.* Flag for review