Topic: Inverters and 240.87

User: Danielt, Location: VIRGINIA

Asked on: Monday, August 26, 2024 at 11:32 am EDT
Answered on: Thursday, March 6, 2025 at 1:40 am EST

Question: How do inverters comply with 240.87 arc-reduction? Is it built into the inverter? Do AHJs require this? There doesn't seem to be an exception for PV. 2020NEC

You're right to be looking at 240.87 of the NEC and considering its implications for PV inverters. Let's break down how inverters comply (or don't) and the AHJ's role

Understanding 240.87 (Arc Energy Reduction)

240.87 aims to reduce the risk of arc flash hazards during maintenance or troubleshooting work on overcurrent protective devices (OCPDs) rated 1200A or higher. It requires the use of one or more of the following arc energy reduction methods: (1) Zone-selective interlocking

Coordinates tripping of upstream OCPDs based on downstream fault location.


(2) Differential relaying

Detects fault current imbalance and rapidly trips the OCPD.

(3) Energy-reducing maintenance switch

Temporarily reduces the OCPD's instantaneous trip setting during maintenance.


(4) Energy-reducing active current limiting device

Actively limits the fault current during an arc flash event.

(5) Approved equivalent means

A method approved by the authority having jurisdiction (AHJ) that provides equivalent or better arc flash protection.


(6) Installing a main overcurrent protective device using a instantaneous trip setting that is less than the available arcing current.
(7) An arc flash reduction system.Inverters and 240.87: The Challenge

Here's the crux of the issue:
240.87 applies to overcurrent protective devices rated 1200 amps or higher. Individual PV inverters typically do not have OCPDs of this size. The OCPD that is often under scrutiny in PV systems would be the main AC breaker that is 1200 amps or higher. Inverters are not inherently arc flash reduction devices. They do have internal protection mechanisms (overcurrent, overvoltage, etc.), but these are designed to protect the inverter itself and the PV array from damage, not necessarily to actively reduce arc flash hazard for personnel working on the downstream electrical system.

How Compliance is Achieved (or Not) in PV Systems1. It Often Doesn't Directly Apply to the Inverter Itself

Because 240.87 is triggered by OCPD size (1200A+), it is the
main overcurrent device that would be reviewed.2.

System Design Considerations Are Key

When designing a large PV system with a service rated for 1200A or higher, and there are OCPDs protecting that service the system must be carefully designed to:


Reduce available fault current

Careful conductor sizing and minimizing loop impedance can help.

Coordinate OCPD settings

Employing proper selective coordination and time-current curves can ensure the nearest upstream device trips first, limiting the potential arc flash energy.


Utilize Energy Reducing Methods at the Main

If the main OCPD is 1200 amps or higher, that is where one of the 240.87 methods would need to be implimented. Methods like Zone-selective interlocking and differential relaying would be part of the switchgear or panelboard.

The AHJ's Role is Critical
Enforcement and Interpretation

The AHJ has the final say on whether a PV system design meets the intent of the NEC and is safe. They may require additional documentation or calculations to demonstrate arc flash hazard reduction.


Approval of "Equivalent Means"

If a designer proposes a method not explicitly listed in 240.87, the AHJ must approve it as an "approved equivalent means." This requires strong justification and documentation.

Inspections

AHJs will typically inspect the installation to verify that the system matches the approved design and that OCPD settings are as specified.

No Explicit PV Exception (And Why That Matters)


You're correct that there isn't a specific exception for PV systems in 240.87. This absence is significant:
PV Systems Can Still Be Dangerous

High-voltage DC systems and large AC inverters can create significant arc flash hazards if not properly designed and maintained.

The Burden is on the Designer and Installer

They must demonstrate compliance with the
intent of 240.87, even if a direct application is not obvious.

Promotes a Holistic Approach

Thinking about arc flash hazard reduction should be an integral part of the PV system design process, not just an afterthought.

In summary:
While individual PV inverters don't inherently comply with 240.87, it's essential to consider arc flash hazards in the overall PV system design, especially when large service main breakers are involved. Proper system design, OCPD coordination, and communication with the AHJ are crucial to ensuring a safe installation. Flag for review