User: am1954, Location: NY
Asked on: Monday, August 26, 2024 at 12:18 pm EDT
Answered on: Thursday, March 6, 2025 at 1:40 am EST
Question: Hey all,We have a scenario where we want to do our interconnection inside a trough located below the building's service disconnect. Due to odd layout of equipment/conduit the trough would end up containing: 1. PV Service Conductors 2. Building Service Conductors 3. The fused feeders from the loadside of the buildings disconnect. So a set of fused feeders in the same trough as un-fused service conductors Think there is anyway we can justify that or no? Thanks for any thoughts...
You've described a situation that's generally problematic and likely violates several sections of the National Electrical Code (NEC). Here's a breakdown of the issues and potential (unlikely) justifications
Core Problems & NEC Violations:
1. NEC 230.7: Other Conductors in Raceway or Cable
This is the biggest hurdle. Generally, service conductors cannot be in the same raceway or cable as other conductors. The intent is to keep the high fault potential of service conductors isolated from other circuits.
2. NEC 230.8: Raceways to Enclose Service Conductors
Even if you could somehow get past 230.7, the raceway (in this case, a trough) containing service conductors must only contain service conductors.
3. Fire Hazard
Combining unfused service conductors with fused feeder conductors dramatically increases the risk of a catastrophic fault. A fault in the building's fused feeders could easily escalate into a major arcing fault involving the entire service, potentially exceeding the interrupting rating of the fused disconnect.
4. Working Space and Access (NEC 110.26)
While not directly related to conductor mixing, packing this many conductors into a trough often creates problems with working space around the service equipment.
Attempted Justifications (Highly Unlikely to be Approved by an AHJ)
Here's where you might try to justify it, but be prepared for serious pushback from your Authority Having Jurisdiction (AHJ).
A. Exception to 230.7 (Not Applicable Here)
There are very limited exceptions to 230.7, primarily dealing with grounding conductors or control wiring specifically related to the service equipment. Your situation doesn't fit.
B. "Separation by Barriers"
You might argue that physically separating the service conductors from the feeders with a substantial, approved barrier within the trough could provide equivalent safety. This is a very long shot. The barrier would have to be demonstrably robust, non-combustible, and rated for the available fault current. It would also have to be sealed to prevent arc-over. Even if you could build such a barrier, the AHJ would likely still reject the arrangement due to the overall congestion and potential maintenance difficulties.
C. Engineering Justification (Rare)
In rare cases, an engineer can provide a detailed, documented analysis demonstrating that the proposed installation meets or exceeds the safety requirements of the NEC, even if it technically deviates from the code. This would require extensive fault current calculations, arc flash studies, and a compelling argument that the proposed installation is safer than a more conventional approach. This is extremely difficult and expensive to achieve and rarely successful.
What to Do Instead
Re-evaluate the Layout
This is the most important step. The layout is clearly creating this problem. Can you relocate the service disconnect, trough, or other equipment to allow for proper separation of service and feeder conductors? Consider using a larger trough, or separate troughs, to achieve the necessary segregation.2.
Separate Service Entrance
Consider bringing the PV service to a separate service entrance location, away from the building's main service. This might require a separate meter and disconnect.3.
Use of Auxiliary Gutters
Use of auxiliary gutters can sometimes help, but the same rules regarding mixing service and feeder conductors still apply.4.
Consult with the AHJ Early
Before proceeding with any design based on a potential code deviation, consult with your local AHJ (building inspector, electrical inspector). Get their feedback on the proposed installation and any justification you might offer. It's better to know upfront that your plan won't be approved.
In Summary:
Mixing unfused service conductors with fused feeders in the same trough is almost certainly a code violation and a safety hazard. The burden of proof is on you to demonstrate, with extremely rigorous documentation, that your proposed installation is at least as safe as a code-compliant solution. The far more practical and cost-effective approach is to re-engineer the layout to keep service and feeder conductors separate.Get the AHJ's input before* investing significant time and resources. Good luck! Flag for review