User: wwhitney, Location: Berkeley, CA
Asked on: Monday, August 26, 2024 at 1:23 pm EDT
Answered on: Thursday, March 6, 2025 at 1:41 am EST
Question: For the 2023 NEC and the 2026 NEC I submitted various PIs to expand the allowances in 705.12(B) on load side interconnections in ways that will not overload the panelboard bus, but which do not fit into any of the existing categories. All of them have been rejected; I think the primary reason has been, to paraphrase, "705.12(B) is complicated enough, let's not add further language for corner cases."However, this time around the CMP basically said "we see what you are trying to do, and it makes sense, but if you want to do that, just use 705.12(B)(6)." So those of you who are engineers [or who can get an engineer to sign off on the design under 2023 NEC 705.12(B)(6), aka 2020 NEC 705.12(B)(5)], can do any of the following:1) Use a panelboard with at most 3 busbar connections, each of which is protected at the busbar ampacity. [Of course, you can do the same thing with a feeder interconnection with 705.12(A), so it's silly that to use a busbar instead of a wire-type feeder you need engineering supervision.]2) Ignore one breaker of the smallest size present when applying 705.12(B)(3). So you can add one breaker for monitoring equipment or whatever to your combiner panels, as long as that breaker is not larger than any other breaker present. This is due to a counting argument--the extra breaker can be either a load or a source, but not both, so if you do the accounting "current in = current out" there's no way to get both sides to exceed the busbar rating due to one extra breaker not larger than any other breaker.3) When you know what is connected to each breaker, label each breaker "source only," "load only," or "source or load." Then as long as the sum of all the sources, or the sum of all the loads, is no more than the busbar ampacity, you know the busbar can't be overloaded.4) Take advantage of a 100% rated OCPD. E.g. if you have a PV-only service entrance with a 200A 100% rated service disconnect/OCPD, then you can connect that to a 200A MLO panel (all such are rated for 200A continuously) connected to (5) 50A breakers, each connected to an inverter with a maximum inverter output current of 40A.Cheers, Wayne
This is a very insightful analysis of the 2023 NEC 705.12(B) and how it can be leveraged, particularly with the encouragement from the CMP to utilize 705.12(B)(6) (formerly 705.12(B)(5) in the 2020 NEC). Your breakdown provides practical applications that are often overlooked and can significantly impact system design and cost-effectiveness. Let's delve into each of your points with some additional context and considerations.
General Commentary
The core problem you're addressing is the often unnecessarily restrictive nature of the 120% rule (and variations) in 705.12(B). While intended to prevent overloading busbars, it frequently penalizes well-designed systems where concurrent operation of sources and loads is inherently limited or can be safely managed. Relying on 705.12(B)(6) shifts the burden of proof to the designer to demonstrate safety, which is a more sensible approach for many scenarios.
Detailed Analysis of Your Points
Panelboard with 3 Busbar Connections Protected at Busbar Ampacity
Explanation
This is a clever interpretation. By ensuring each connection point is protected at the busbar rating, you guarantee that no single input (source or load) can overload the busbar, regardless of other connections.
Practicality
This is highly specialized and likely only relevant in certain factory settings. You would need to find/manufacture a panelboard specifically designed like this.
Limitation
The limitation of "at most 3" connections makes this specific design less practical. If it were "at most N," it would be more useful.
Comparison to Feeder Interconnection (705.12(A))
The point about the disparity between busbar and feeder interconnections is spot-on. The need for engineering supervision for a busbar, when a similar and potentially more risky feeder connection doesn't require it, is indeed questionable.
Code Basis
Because of the ambiguity of the NEC with respect to "busbars," it might not be clear how you are supposed to determine whether each connection is protected at the busbar ampacity. For example, can you just add up all the protection devices connected to each busbar, and if the sum is less than or equal to the busbar rating, you are good? Or does each individual breaker need to be no more than the busbar rating? If the former, then you just created an equivalent of my PI.2.
Ignoring One Breaker of the Smallest Size When Applying 705.12(B)(3)
Explanation
Your "counting argument" is sound. This is a practical way to accommodate small loads (e.g., monitoring equipment, communication devices) without triggering the 120% rule, especially in combiner panels.
Example
A 200A panel with (3) 60A inverters and a single 15A breaker for monitoring equipment. Under 705.12(B)(3), you would normally fail because 60 + 60 + 60 + 15 = 195 > 160 = 1.2 x 200/1.
25. But by ignoring the 15A breaker, you can successfully use this panelboard under 705.12(B)(3).
Clarification
It's crucial to ensure the "extra" breaker is indeed no larger than any other breaker already present. A 20A monitoring breaker in a panel with (3) 60A inverters is still a problem under 705.12(B)(3).
3.
Labeling Breakers as "Source Only," "Load Only," or "Source or Load"
Explanation
This is a smart approach to directly address the fundamental concern of busbar overloading. If you can definitively demonstrate that the sum of source currents or the sum of load currents will never exceed the busbar rating, the 120% rule becomes irrelevant.
Implementation
Requires meticulous load/generation calculations and a clear labeling scheme to ensure the installation matches the design intent. This might involve commissioning procedures to verify the actual load characteristics.
Documentation
Thorough documentation is key to justifying this approach to inspectors and ensuring future modifications don't violate the design assumptions.
Example
You could label all breakers as "Source Only", "Load Only" and create a table/spreadsheet documenting the maximum current that each breaker could possibly source or sink.4.
Taking Advantage of 100% Rated OCPDs
Explanation
Leveraging 100% rated OCPDs is a direct way to increase the available capacity of a panelboard. This avoids the derating required by standard OCPDs (80% continuous use).
Requirement
You must use a panelboard that is rated for continuous operation at its nameplate rating. Many MLO panels meet this requirement.
Limitation
While this technically works, the cost of 100% rated breakers can be a significant factor. It might be more cost-effective to upsize the panelboard in some cases.
Code Basis
This relies on the fact that the busbar rating matches the OCPD rating, which is often not the case when you are not using a 100% rated breaker.
Key Considerations for Utilizing 705.12(B)(6)
Engineering Justification
Documentation is paramount. You need to provide detailed calculations, diagrams, and explanations to support your design and demonstrate that the busbar will not be overloaded under any reasonably foreseeable operating conditions.
Coordination with AHJ
It's crucial to engage with the Authority Having Jurisdiction (AHJ) early in the design process to discuss your proposed approach and ensure they are comfortable with your engineering justification.
Ongoing Monitoring
For more complex systems, consider incorporating monitoring equipment to track busbar currents and verify the design assumptions.
Future Expansion
Design the system with future expansion in mind. Account for potential increases in load or generation and ensure the busbar can handle the additional capacity.*
Safety Factor
While 705.12(B)(6) provides flexibility, it's still prudent to incorporate a reasonable safety factor in your design.
Conclusion:
Your analysis provides valuable insights into how to navigate the complexities of 705.12(B) and leverage the engineering flexibility offered by 705.12(B)(6). By understanding the underlying principles and carefully documenting your design, you can create safer, more cost-effective, and optimized distributed generation systems. Your examples are excellent starting points for thinking outside the box and pushing the boundaries of what's possible within the NEC. Thanks for sharing! Flag for review