Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: split 400a into 2 200a

User: superchief1, Location: philadelphia

Asked on: Monday, August 26, 2024 at 2:17 pm EDT
Answered on: Thursday, March 6, 2025 at 1:41 am EST

Question: I have a building being rebuilt which has a 400a service (cl320 meter) that I want to split into (2) 200a split services to (2) load centers - these are on the same meter which is what we want.We definitely want to split the 400a into (2) 200a load centers which are already wired and are located at opposite ends of the building.There is a 400a service disconnect after the meter which will stay, so everything to be done is after that service disconnect.The current service is split into (2) 200a services via a 400a Cutler Hammer Genswitch ATS which has 4 lugs, but the generator is trash.1. Anyone know if the ATS needs to be replaced with age, as it appears to be industrial quality and in fine condition but I don't know what the age or service life of these is?IF I GET A NEW ATS2. Most new ATSs only have 2 lugs it seems, even in the 400a lines. Anyone know a 4 lug manufacturer?Alternately, what equipment should I investigate to split a 400a split phase service into (2) 200a split phases services if I do it after the ATS?

Okay, let's break down your project and explore the best options.

Understanding the Situation Existing Setup

400A service (CL320 meter) -> 400A service disconnect -> 400A Cutler Hammer Genswitch ATS -> (2) 200A load centers.


Goal

Maintain the (2) 200A split services to the existing load centers after the existing 400A service disconnect.

Key Issue

The existing ATS is old, and potentially unreliable, and you need to split the 400A service into two 200A services.

1. ATS Replacement: Age and Service Life


Whether you
need to replace the ATS depends on a few factors, including safety and code compliance. Age is a Factor

ATS devices do have a service life. Internal components, especially switching contacts and control circuitry, can degrade over time. A very old ATS (20+ years) is likely a good candidate for replacement regardless of how it looks.

Inspection is Critical

A qualified electrician should inspect the ATS thoroughly. They will look for:


Arcing or Burn Marks

Around contacts or wiring.

Loose Connections

A significant cause of heat and failure.


Corrosion

Especially in damp environments.

Mechanical Issues

Proper operation of the transfer mechanism.


Operational Testing

Actually testing the transfer to ensure it switches cleanly and reliably.

Code Compliance

Local electrical codes may require upgrades based on age or the type of building (e.g., if it's now a commercial space). The presence of the trash generator suggests this may not be an emergency system any longer, so it may not even require an ATS if it is only intended to allow manual connection of a generator

Recommendation

Get a thorough inspection of the existing ATS by a qualified electrician. If you are unsure of its performance, it's usually safer and more cost-effective in the long run to replace it. A failing ATS can cause significant damage and create a safety hazard.

2. Options for Splitting the 400A Service


Here are a few options, with pros and cons

Option 1: Replace the ATS with a 400A Disconnect and a Distribution Block

Description

Replace the existing ATS with a simple 400A disconnect switch. After the disconnect, install a suitable distribution block to split the 400A service conductors into two sets of 200A conductors.

Pros

Cost-effective. Simple. Reliable (fewer components).

Cons

No automatic transfer capability (if that's ever desired in the future).

Option 2: Replace the ATS with a 400A Distribution Panel
Description

Replace the existing ATS with a 400A distribution panel with two 200A breakers. This is essentially a small load center.


Pros

More organized than using distribution blocks. Provides overcurrent protection at the point of splitting the service.

Cons

Slightly more expensive than distribution blocks.

Option 3: Using a Junction Box with Split Bolt Connectors
Description

After the 400 amp disconnect, install a large, properly sized junction box. Inside the junction box, use split-bolt connectors (or other UL-listed connectors for this purpose) to splice the 400A conductors into two sets of 200A conductors.


Pros

Can be the most cost-effective in terms of materials.

Cons

Requires careful installation to ensure proper torque on the connectors and secure wiring. Doesn't provide overcurrent protection at the split (which is a code consideration).

Equipment Recommendations and Considerations
400A Disconnect Switch

Look for a heavy-duty, UL-listed disconnect switch rated for 400A. Brands like Square D, Eaton, and Siemens are reliable.


Distribution Blocks

Choose distribution blocks rated for 400A input and 200A output per tap. Verify UL listing and proper conductor size ratings. Inspect and torque all conductors properly using an insulated torque screwdriver.

400A Distribution Panel

Consider a small 400A panel with a main breaker (or main lug only if you already have a 400A disconnect) and two 200A branch breakers. This is often the most organized and code-compliant approach. Make sure the panel is UL-listed for service entrance use.


Conductor Sizing

Ensure all conductors are sized correctly for the 200A loads and meet the National Electrical Code (NEC) requirements. Consider derating factors for ambient temperature and conductor bundling.

Grounding

Maintain proper grounding throughout the system. The grounding electrode conductor (GEC) should be connected to the neutral at the service disconnect.

General Recommendations
Engage a Qualified Electrician

This project requires a qualified and licensed electrician. They will be familiar with local codes and can ensure the installation is safe and compliant.

Permits

Obtain the necessary electrical permits before starting work.


Inspect and Torque

Thoroughly inspect all connections and torque them to the manufacturer's specifications.*

Labeling

Clearly label all panels and circuits.

In summary:
The best approach depends on your budget, space constraints, and long-term goals. I highly recommend getting quotes from a few licensed electricians to discuss these options and determine the most suitable solution for your specific situation. It is more likely than not that replacing the ATS is the best solution. While all of the non-ATS replacement solutions will work, they add components to the system which could require replacing in the future, and the total cost of the disconnect + distribution blocks/panel will likely be similar to an ATS. Flag for review

Previous Question Next Question