Topic: Electric Range Load in 220.42 vs 220.84

User: KBot9, Location: NYC

Asked on: Monday, August 26, 2024 at 3:03 pm EDT
Answered on: Thursday, March 6, 2025 at 1:41 am EST

Question: I have an existing multifamily, say 100 units, that wants to upgrade each panel and run electric ranges to eliminate gas. The Service is 3 phase. The Ranges are single phase three wire 220, 8000kW.220.55 says that "where 2 or more single phase are supplied by a three phase ...service...." the calc would look like this (as shown in the Annex D5(A):Max rages btwn any 2 phases (34) times 2 (68) then use 68 "ranges" in Table 220.55 Column "B" (cause under 8750 watts) for the "61 & Over" Line so: 25,000W & (68 *.75kW =) 51000W for 76,000W, divided by 2 for Single Phase Load (38000W) then times 3 for three phase = Total Electric Range Load on the 3 Phase Service Feeder of 114kW divided by 360 = 316.6 AmpsIn the Multifamily Load Cal Option 220.84 though is says Add Electric Nameplate to total (of Gen Lighting & Small Appliances & Fixed Appliances) then use table for over 62 units and multiply by 23%. In this case 8000W * 100 Units = 800,000 *.23 = 184,000W Divided by 360 = 511.1 AmpsBig Difference for the exact same Line Item.Since in the 220.84 method the Ranges are the same exact ranges and *If they dont exist yet the calc can be the Gen/Appliance loads times 23% then a year from now they add electric ranges and THEN I can use 220.55?I dont understand if 220.55 trumps 220.84 now, and I can still use the Single to Three Phase electric range calc... or if 220.84 must have the full nameplate. When I can just as easily merely calculate the Service Feeder Load based on 220.84 for everything but the ranges then say Im adding the ranges later for 316 amps and "luckily" I already sized the Service Feeders for those 316 additional amps coming.

You've hit on a common point of confusion when applying the NEC to multifamily dwelling load calculations. Here's a breakdown to clarify the application of 220.55 and 220.84, and how to approach your situation

Understanding 220.55 vs. 220.84
220.55 (Ranges)

This section deals
specifically with calculating the demand load for electric ranges in dwellings. It takes into account that not all ranges will be used at their full nameplate rating simultaneously, hence the demand factors in Table 220.55. Annex D is simply an example, 220.55 and 220.54 are used for the calculation.

220.84 (Optional Method for Multifamily Dwellings)

This is an optional method for calculating the entire service or feeder load for a multifamily dwelling. It's intended to be a simplified approach, but it can sometimes lead to significantly higher calculated loads than a more granular approach.

Key Difference

220.55 focuses on
one specific load type (ranges) and applies demand factors. 220.84 is a comprehensive load calculation method for the entire building, and the use of nameplate is the issue at hand.

Applying to Your Scenario


Here's how to best approach your situation, combining the strengths of both methods:1. Decide if you meet the requirements of 220.84

This option requires you to meter the building for a year and meet the requirements of this section.2.

If you are not using 220.84, Calculate General Loads

Calculate general lighting, small appliance, and other fixed appliance loads according to the standard calculation methods in Article 220 (e.g., 220.12 for lighting, 220.14 for receptacle outlets, etc.).
3.


Calculate Range Load Using 220.55

This is where you use the method you described at the beginning of your question. Use the provisions in 220.55 to determine the demand load for the electric ranges. This is the most accurate way to account for the diversified usage of the ranges.
4.


Combine the Loads

Add the general loads from step 2 to the range load calculated in step 3. This will give you the total calculated load for the service or feeder.

Why the Difference and Addressing the "Loophole"


You correctly identified that using 220.84 with full nameplate ratings for the ranges can result in a significantly higher load calculation. This is because 220.84 applies a general demand factor to the
entire load, rather than specific demand factors tailored to the characteristics of each load type (like 220.55 does for ranges).Regarding your "loophole" concern (calculating service size without ranges using 220.84, then adding ranges later using 220.55): While technically possible, it's unethical and could lead to an undersized service in the future if loads increase beyond what you initially considered. Inspectors are generally aware of these types of strategies.

Recommendations1. Use 220.55 for Ranges

This is the
most appropriate and accurate* method for calculating the range load in your scenario.2.

Use 220.84 Carefully (If Applicable)

If you use 220.84, be aware that it will likely result in a higher calculated load than the combination of standard calculations and 220.
55.3.


Consider Future Load Growth

When sizing the service, always factor in potential future load growth beyond just the initial range upgrade. Think about electric vehicle chargers, additional appliances, etc.4.

Consult with the AHJ

It's always a good idea to discuss your load calculation approach with the local Authority Having Jurisdiction (AHJ) to ensure they are comfortable with your method and that you meet all local requirements.

In summary, 220.55 is the best practice to address the ranges, and if 220.84 can be used, use the higher of the two methods to be as safe as possible.