User: 729Zoom, Location: Los Angeles
Asked on: Monday, August 26, 2024 at 5:53 pm EDT
Answered on: Thursday, March 6, 2025 at 1:42 am EST
Question: When I moved into my house 42 years ago, there was already a 100 amp panel with a 100 amp main breaker but I recently found out that the service wire to my house and all my neighbors (who also have 100 amp min panels) is a #8 aluminum, which is only rated for 40 amps! I checked my historical usage as far back as I could on the utility site and bought an emporium energy monitor and found I have never pulled more than 30 amps at one time and, most of the time, I am pulling only 10-20 amps total. I think because I have all gas appliances, just two of us and we don't use a lot. So, it seems the #8 is more than enough.BUT, we recently had to replace the panel when one of the bus bars went bad and we lost power. Our electrician replaced it with one that would let us get solar in the future without having to redo it. But it has a 200 amp breaker and I was thinking he should have put in a 100 amp breaker like I had before. I read that downgrading breakers is not uncommon. But now that this is already done and the utility company has already come and locked the meter, we would have to have them out to do that again to either downgrade the breaker or ask for a service upgrade, which we don't really need and hate to pay for that.My thinking is if the service wire was undersized for the 100 amp panel and breaker we had and it never had issues over 42+ years, that a 200 amp breaker won't make any difference? And I should just keep it in case we do go to solar in the future? But, I wanted to get input from others. thanks.
You've outlined a situation that, unfortunately, is not uncommon in older homes. Here's a breakdown of the issues and my thoughts
The Problem:
Undersized Service Wire
A #8 aluminum wire rated for 40 amps feeding a 100 amp (and now 200 amp) panel is a code violation and a potential fire hazard. While you've never overloaded it knowingly, the potential for doing so exists.
Oversized Breaker
The main breaker's purpose is to protect the wiring from overload, not necessarily the individual circuits within your house (those are protected by their own breakers). A 200 amp breaker on a 40 amp wire offers little to no protection to that service wire. It will only trip if you draw substantially more than 200 amps.
Why it likely hasn't been a problem (yet)
Low Usage
As you've observed, your actual electrical consumption is far below the capacity of the 40 amp wire.
Luck
The undersized wire could have overheated and caused insulation degradation over the years, which could lead to a fire.
What to consider now
Ignoring the Problem is Risky
While it hasn't caused an issue so far, there's no guarantee it won't in the future. A significant surge, a faulty appliance, or even a change in your lifestyle could push you over the 40 amp limit.
Future Changes
You mentioned future solar. Depending on the size of the system you are looking into, you may have to upgrade the service. And it would be best to do it now if it is in the near future.
Possible Options
Service Upgrade
This is the correct solution. Replace the #8 aluminum wire with properly sized wire for a 100 amp or 200 amp service. This ensures safety, meets code, and allows you to fully utilize your new panel. It's the most expensive option, but also the most responsible. Get quotes from multiple electricians. Inquire about potential rebates or incentives from your utility company. Factor in the cost of the service upgrade into your solar planning, as this is the most important factor for your solar project.2.
Downsize the Main Breaker
While not a perfect solution, this is a significantly better option than doing nothing. Replace the 200 amp breaker with a 40 amp breaker. This will more closely protect the existing #8 aluminum wire from overcurrent.
Important
This does not mean you can safely draw 40 amps continuously. The wire is old, and its capacity may have degraded. It's still best to keep your usage well below 40 amps. It will likely trip more frequently if you suddenly draw a lot of power. You will need to weigh if this is worth having the utility company come out to do this.3.
Combination of Both
You can get a 100amp breaker installed and start saving for the service upgrade to the 200 amps for your solar project. Then you don't have to pay twice for two call outs.
Why Keeping the 200 Amp Breaker is a Bad Idea
False Sense of Security
You might think you have a "200 amp" service, but you don't. The weak link is the #8 wire.
No Overload Protection
The 200 amp breaker will not protect the #8 wire. It's like putting a giant fire hose on a garden hose – the garden hose will burst long before the fire hose is even close to its capacity.
Liability
If a fire occurs due to an overloaded #8 wire, your insurance company could deny your claim, and you could be held liable.
Recommendation
Prioritize Safety
Your immediate concern is safety. An undersized service wire is a serious fire hazard.2.
Get More Quotes
Get a few more quotes from licensed electricians, specifically addressing the undersized service wire and the options available. Discuss the pros and cons of each approach.3.
Factor in Future Needs
If solar is definitely in your future, factor the cost of a full service upgrade into your plans.4.
Start saving for the service upgrade as soon as possibleIn Conclusion:
While you've been fortunate to avoid problems so far, continuing to operate with an undersized service wire is playing with fire. A service upgrade is the only* way to guarantee safety and code compliance. At the very least, downgrade to a 40 amp breaker until you can afford a proper upgrade. Flag for review