Topic: Breaker Larger than Fused Disconnect Rating

User: elecshop, Location: FL, USA

Asked on: Monday, August 26, 2024 at 6:06 pm EDT
Answered on: Thursday, March 6, 2025 at 1:42 am EST

Question: This is probably a straightforward question but for some reason I keep getting confused.I have a 2-pump motor (lift station) that has 60A breakers integrated in its front panel (1 pump is the primary, 1 is a standby). FLA=20A for 1 pump.The OCPD rating should be 250% x FLA1 + FLA2 = 250%x20 + 20 = 70A.Can I use an existing 100A (3-phase) circuit without replacing the 100A breaker with a 70A breaker? Since the OCPD is already installed inside the equipment.

You're correct in your calculation: 250% of the larger motor FLA + the smaller motor FLA = (2.5 20A) + 20A = 70A.Here's the breakdown of whether you can use the existing 100A circuit: NEC Code Considerations



430.53(C)

This section generally discusses overload and short-circuit protection for motor circuits with multiple motors or loads.


Key Points



Internal Protection

You correctly point out that the motor starter has

integrated 60A breakers
. These provide the short-circuit and ground-fault protection required for each individual motor. Feeder Protection

The feeder supplying the lift station panel must be sized and protected appropriately for the entire load, including the potential simultaneous operation of both motors, plus any other loads connected to the panel.

The 100A Feeder Breaker

The 100A breaker is protecting the feeder conductors running
to the motor panel/lift station. The internal 60A breakers protect the individual motors from overcurrent.

Answer



YES, you can likely use the existing 100A breaker,
provided it's properly sized to carry the full load of the lift station panel.
However... MUST VERIFY TOTAL LOAD

You need to determine the total load on the lift station panel. This includes: The FLA of both motors (20A + 20A = 40A). Consider starting currents, although the internal breakers will trip first. Any control circuit loads (lights, sensors, etc.). Any other equipment powered from that panel. The calculated load on the feeder should not exceed 80% of the 100A breaker rating (80A). This is a common practice to avoid nuisance tripping and to account for continuous loads. (100A 0.8 = 80A) If your total calculated feeder load, including both motors running and any other loads, is less than 80A, then the 100A breaker is acceptable. If your total calculated load is above 80A, then the 100A breaker is

undersized
and needs to be upgraded accordingly.

In summary

The 60A breakers inside the lift station panel protect the individual motors. The 100A breaker protects the feeder conductors leading to the panel. Ensure the 100A breaker is appropriately sized for the total load connected to the lift station panel (including both motors running simultaneously and any other loads).

IMPORTANT - Consult a Qualified Electrician

This is a simplified explanation. Electrical codes and regulations are complex and vary by jurisdiction.

Always consult with a qualified electrician
to perform load calculations, verify compliance with applicable codes, and ensure the safety and proper operation of the electrical system. A licensed electrician will be able to make the final determination based on a complete assessment of the installation. Flag for review