Topic: Newer Home Disconnect Panel Lug Piggybacking

User: Matt.W, Location: Charleston

Asked on: Monday, August 26, 2024 at 6:58 pm EDT
Answered on: Thursday, March 6, 2025 at 1:42 am EST

Question: Newbee to the forum, Retired Naval Engineer, USCG. Living in Charleston, SC. Recently (2yrs) had an inground swimming pool installed. The pool company sub-contracted electrician piggybacked the pool panel (pump, heat pump, controls, and lights) into the lugs inside the Schneider Electric RC200S disconnect panel which had 2 #6-350 CU cables for the disconnect. The disconnect panel is rated for the 2 #6-350 CU/AL. The job was approved the the Charleston city inspector.I contract Schneider and they advised "It might be safe, but the main issue is the devices are not UL tested and listed for that, so when they are changed or parts added that are not from the factory that voids the UL and Warranty."The Pool company wants to come out and put Polaris Taps in place. Thoughts?The Charleston city inspectors office ghosted me... Thoughts?Question; is that safe, legal and meets code, do I worry? Getting ready to have a generator installed and these items will be bypassed.v/r. Matt W.

Okay, Matt, welcome to the forum! As a fellow engineer (though not naval), I understand your concern and desire for clarity. Let's break this down

Understanding the Issue: Tap Rules
UL Listing is Key

Schneider's response hits the nail on the head. Electrical components, especially those handling significant current, are designed and tested as a system. Altering that system by tapping into existing lugs can void the UL listing and create a potential safety hazard. It's not just about the
size of the conductors; it's about how the component was tested and listed for termination.

Lug Ratings

Electrical lugs are designed to terminate conductors of a specific size and type (copper or aluminum). Piggybacking multiple conductors under a single lug that isn't specifically rated for that purpose can lead to loose connections, overheating, and potentially fires.

Code Compliance

While the inspector signed off, that doesn't necessarily mean it's
best practice or even correct over the long term. Inspectors can miss things, and interpretations of code can vary.

Polaris Taps as a Potential Solution
Purpose

Polaris taps are insulated multi-port connectors designed to allow multiple wires to be spliced, tapped, or terminated from a single conductor.

Potential Merits

If properly sized and installed, Polaris taps
can provide a safe and code-compliant way to add the pool equipment's wiring to the existing conductors. They're a recognized method for making connections.

Crucial Caveats



Proper Sizing

The Polaris taps
must be rated for the conductor size (#6-350 CU in your case) and the amperage draw of the pool equipment.

Professional Installation

Installation is critical. The wires must be properly stripped, cleaned, and torqued according to the manufacturer's instructions.

Access and Enclosure

The Polaris taps need to be enclosed in a suitable junction box (NEMA 3R or similar) to protect them from the elements and accidental contact.

Addressing Your Specific Questions


"Is that safe, legal, and meets code, do I worry?" (Referring to the initial piggybacking)



Safe?
Potentially not. The lack of UL listing for that configuration creates a concern. Legal? Depends on your local interpretation of the electrical code. The fact that it was signed off on is an issue. Meets Code? Questionable. While it might scrape by, it's not best practice, and Schneider's statement is telling. Do I worry? Yes. Electrical safety is paramount. The potential for overheating and loose connections warrants addressing the issue.2. "Thoughts on the Pool Company installing Polaris Taps?" Good if done correctly

It's a potentially acceptable solution, if the taps are appropriately sized, properly installed, and enclosed in a suitable junction box. Demand to see the product documentation to ensure compliance.

Verify Contractor Competency

Make sure the electrician doing the work is experienced with Polaris taps and understands the importance of proper installation.


Get a Second Opinion

I'd highly recommend getting a second opinion from a qualified, independent electrician before letting the pool company proceed. Explain the situation, show them the Schneider Electric response, and get their assessment.3.

"Thoughts on the Charleston City Inspector's office ghosting me?"
Frustrating, but not uncommon

Government agencies can be unresponsive. It might be due to workload, staff turnover, or simply a lack of understanding of the technical details. Don't take it personally.


Try again

Persistence can sometimes pay off. Try contacting a different inspector or supervisor within the department.

Focus on getting it done right

Ultimately, your priority is ensuring the safety and compliance of your electrical system.4.

"Getting ready to have a generator installed and these items will be bypassed."
Bypassing helps, but doesn't solve the underlying problem

Even if the generator installation bypasses the problematic connection, the existing piggybacked connection will still be present and could still pose a hazard.

Best to address the issue now

It's better to fix the wiring issue properly, regardless of the generator installation. This will ensure the safety and reliability of your entire electrical system.

Recommendations


Independent Electrical Inspection

Hire a qualified, independent electrician (not affiliated with the pool company) to inspect the current wiring and provide a written report with recommendations. This is the most important step.2.

Review Polaris Tap Specs

If the electrician recommends Polaris taps, have them provide you with the specific model numbers and their specifications to ensure they are properly rated for your application. Make sure the taps are fully listed for safety, i.e. UL.3.

Proper Installation

If Polaris taps are used, ensure they are installed by a qualified electrician according to the manufacturer's instructions.4.

Secure Enclosure

Ensure the Polaris taps are enclosed in a properly sized and rated junction box (NEMA 3R or similar).5.

Documentation

Keep records of all inspections, reports, and work done on your electrical system.6.

Consider a Subpanel

Depending on the power requirements of your pool equipment, it might be beneficial to install a dedicated subpanel for the pool equipment. This would provide a cleaner and more organized solution.

In summary

The initial piggybacking of the pool equipment wiring onto the lugs is questionable and potentially unsafe. Polaris taps
can be a viable solution, but only if they are properly sized, installed, and enclosed. Prioritize getting a second opinion from a qualified, independent electrician to assess the situation and recommend the best course of action. Don't rely solely on the original inspector's approval.Good luck, and feel free to ask if you have more questions!

Disclaimer:
This information is for general guidance only. Always consult with a qualified and licensed electrician for any electrical work.* Flag for review