Question: What size generator is good for 5000sqft 4-2ton ac with handlers, 2 motors for pool equipment, dishwasher, washers gas dryer 3 bath, microwave, customer wants whole house. No load shedding. What's a good rule of thumb when sizing something like this. I've heads 22 26 being able to handle but I'm thinking a 48kw because customer is serious it need to be whole house

You're right to be cautious and lean towards a larger generator. Here's a breakdown of the considerations and a reasonable approach to sizing the generator for your customer's needs

Understanding the Challenge: Whole House, No Load Shedding
High Demand

Whole-house generators without load shedding have to handle the
peak load of all devices potentially running simultaneously. This is considerably more demanding than sizing for essential circuits only.

Inrush Current

Motors (AC compressors, pool pumps) have a very high inrush current when starting, often 3-5 times their running wattage. This is the single biggest factor in generator sizing.

Customer Expectations

If the customer truly wants whole-house coverage and no interruptions, under-sizing the generator will lead to nuisance tripping, frustration, and potential damage to equipment.

Estimating Power Requirements: The Key Components


Let's break down the major appliances and their power needs. Remember, these are
estimates – check the actual appliance nameplates for more precise figures. Air Conditioners (Most Critical)

2-Ton AC: A 2-ton AC typically draws about 2400 watts running (10 amps at 240V). However, the starting surge (Locked Rotor Amperage - LRA) can be much higher. A common LRA for a 2-ton unit is 30-40 amps. This translates to 7200 - 9600 watts per unit during startup. With TWO 2-ton ACs, and if they potentially start close to the same time, you need to account for this. Air Handlers: Assume 500-750 watts each. Two handlers, call it 1500 watts total.

Pool Equipment

Pool Pump Motor: A typical pool pump motor can draw 1500-2000 watts running. The inrush current can be significantly higher, similar to AC compressors. Assume 6000 watts inrush. Other Pool Equipment (heater, cleaner): Add another 500-1000 watts depending on the equipment.

Kitchen Appliances

Microwave: 1000-1500 watts Dishwasher: 1200-1500 watts (mostly heating element)

Laundry

Washer: 500-800 watts (motor, pump) Gas Dryer: 300-500 watts (mostly controls and drum motor)

Bathrooms

Hair Dryers: 1200-1800 watts (important to consider if someone might use it during an outage)

Lighting and General Outlets

This is the hardest to estimate. Assume at least 2000-3000 watts for a house this size. This covers refrigerators, TVs, computers, and general lighting. LED lighting helps keep this down.

Calculations and Considerations
1. Running Wattage Estimate

AC Units (2 x 2400) + Air Handlers (1500): 6300 watts Pool Equipment (2000 + 1000): 3000 watts Kitchen: 3000 watts (microwave + dishwasher) Laundry: 1200 watts Bathrooms (allow for hairdryer): 1800 watts Lighting/Outlets: 3000 watts

Total Estimated Running Watts: ~18,300 watts
2. Startup Surge (Key Factor)

This is where you need to be realistic. Assume the worst-case scenario where one or both AC units and the pool pump could try to start simultaneously (or within a few seconds of each other). AC Unit 1 Surge: 7200 - 9600 watts AC Unit 2 Surge: 7200 - 9600 watts Pool Pump Surge: 6000 watts Other motors or appliances: 2000 Watts3.

Total Estimated Startup Surge: 22,400 - 27,200 Watts
4. Generator Sizing

You need a generator that can handle both the running wattage and the startup surge. The startup surge dictates the generator's peak capacity. Add the running wattage to the estimated Surge wattage. 18,300 + 27,200=45,500

Therefore, you are looking at a minimum of 45kw generator
. It is better to get a 48kw or higher in this situation.

Why a Larger Generator is Justified (and Safer)
Headroom

Running a generator consistently near its maximum capacity shortens its lifespan. Having extra capacity allows the generator to run more efficiently and reliably.

Future Proofing

The customer might add appliances or devices in the future. A larger generator provides some buffer.


Voltage Regulation

Generators perform best (and provide the cleanest power) when they aren't heavily loaded. A larger generator will maintain more stable voltage, which is crucial for sensitive electronics.

Customer Satisfaction

Avoid callbacks and customer complaints. It's better to over-deliver than to under-deliver on power.

Important Considerations and Recommendations
Appliance Nameplates

Absolutely verify the wattage and amperage (especially the LRA for motors) on the actual appliances. Don't rely solely on estimates.

Transfer Switch

Make sure the transfer switch is appropriately rated for the generator's output and the electrical service of the house.


Professional Installation

Generator installation requires a qualified electrician and often a gas fitter.

Fuel Source

Consider the available fuel source (natural gas or propane) and the generator's fuel consumption at different load levels. Natural gas typically requires a larger generator because it produces less energy.

In conclusion:


While a 22-26 kW generator might
theoretically* handle some of the load with careful load management, it's highly unlikely to provide true whole-house coverage without any interruptions, especially with two AC units and pool equipment. The 48 kW or higher is a more appropriate and realistic choice to meet the customer's requirements and ensure reliable operation. Flag for review