Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: 3p Open Leg Delta Woes

User: ArcLife, Location: Japan

Asked on: Monday, August 26, 2024 at 10:30 pm EDT
Answered on: Thursday, March 6, 2025 at 1:43 am EST

Question: Hello. I'm in Japan, where three phase is mostly open-delta. The short story is that there's no real "problem," but more that I just don't understand what's going on. While testing the current draw on a three phase DC transformer welder, I see that L1 is only about two-thirds of the other two legs, which is "normal" for here. Ditto the three-phase air compressor, etc. However, when I test the current draw on two different inverter welders, it shows no current on L1, and a more or less balanced current on L2 and L3... I'm perplexed as to why this is. I went to a friend's shop and tested his feed using an inverter welder of the same brand I had tested at mine, and L1 shows two-thirds of L2 and L3. I have a much larger service contract than he does; much larger lines from the transformers, etc.The longer part. I tested multiple machines, and all of the inverter machines show no current on L1 at my place. Transformer welders, as well as multiple pieces of gear like air compressors all show L1 as having two-thirds the current of L2 and L3. This is inherent to open-delta 3p. Everything works fine, and I would have never known. It started as just testing a piece of gear to see what it actually draws, and then turned into a runaway train of testing and trying to figure out why the inverters are doing what they're doing. Swapping phases, swapping what panel and breaker power is taken from. Checking for voltage drop, etc. No current on ground. Nothing changes. I was concerned about the rectifiers in the inverters not sharing load, but when testing one machine, a high-end Panasonic TIG welder, it was showing about 35A while at full power (300A output verified) on L2 and L3, which is what it states for maximum draw, so I doubt it's cooking the diodes. I went as far as messaging Panasoinc, as I'm in the market for a couple of new machines. I explained what's happening, and that I was worried about the bridge rectifier and DC bus capacitor. I was hoping for some detailed info, like maybe components are upsized to deal with open-delta imbalance, but their response was pretty much "you'll be alright" LOL!In short, I'd like to understand why the power seems fine, but the inverter welders at my shop show no current on L1. My best guess is that the impedance is higher on L1 at my place than my friends place, and that's why his inverters draw current on L1, albeit at 2/3 of L2 and L3.Thank you for your time.

Okay, this is a fascinating situation and your detailed description is very helpful. Let's break down the factors at play and try to get to the bottom of this mystery.

Understanding Open-Delta (V-Phase) Three-Phase Unequal Loading

The core characteristic of open-delta (V-phase) is that the load on each phase is
inherently unequal. You always see this. One phase (often designated as L1) typically carries significantly less current than the other two. This is due to the way the transformer windings and load are connected.

Capacity Reduction

Open-delta provides only 57.7% of the capacity of a closed-delta system using the same transformer sizes. It's often used where the initial three-phase load is relatively small, with the expectation of upgrading to a full delta configuration later if demand increases.

Phase Angle

Keep in mind that even with balanced currents, the current in each phase will be offset by 120 degrees with respect to each other.

Why Inverter Welders are Different


Inverter welders are sophisticated pieces of equipment that can behave differently from traditional transformer-based machines. Here's why they are likely behaving differently at your location:1. Power Factor Correction (PFC)

Inverter welders often incorporate power factor correction circuits. PFC aims to draw current from the AC line in a way that is as close to sinusoidal and in phase with the voltage as possible. Good PFC minimizes harmonic distortion and maximizes power transfer. While they are likely not explicitly designed for open-delta, they can alter the behavior of how the load is applied to each phase.2.

DC Bus Capacitor

Inverter welders have a large DC bus capacitor that stores energy. The AC input power is rectified and used to charge this capacitor. The welder then draws power from the capacitor to generate the welding current. This capacitor acts as a buffer, smoothing out the AC waveform and providing a stable DC voltage.3.

Input Bridge Rectifier & Control Algorithm

The inverter is powered by a three-phase bridge rectifier. The inverter welder's control system monitors the DC bus voltage and actively controls the current drawn from each phase to maintain a stable DC voltage and, ideally, balance the load across the input phases. However, under open-delta conditions, the control system may be "overcompensating" and effectively shutting off current draw on L1.4.

Tolerance for Imbalance (or Lack Thereof)

Some inverter welders might be more sensitive to voltage imbalances inherent in open-delta systems than others. The design of the input circuitry, specifically the rectifiers and the DC bus capacitor charging circuit, might be such that it reacts unfavorably to the unbalanced voltages on the three phases.5.

Software Compensation

Some inverter welders have software algorithms designed to compensate for input voltage fluctuations and imbalances. However, these algorithms may not be fully optimized for open-delta systems.

Why No Current on L1?


This is the key question. Here's a breakdown of the most probable reasons:
Overcompensation by the Inverter Control System

The inverter welder's control system may be sensing the lower voltage on L1 (due to the inherent imbalance of the open-delta system) and actively reducing or shutting off current draw from that phase to maintain a "balanced" DC bus voltage. It's trying to make the best of a bad situation. This is especially likely if the inverter is designed with the assumption of a balanced three-phase supply.

DC Bus Capacitor Saturation

In the open-delta configuration, the DC bus capacitor is primarily charged by the two phases that have more voltage and current available. It's possible that, at your location, with your specific voltage imbalance and load, the DC bus capacitor is becoming saturated, or close to it, which limits the need for the inverter to draw current from L1.


Harmonic Distortion

The unbalanced nature of open-delta can lead to increased harmonic distortion on the power lines. Inverter welders are sensitive to harmonic distortion, and it is possible that the inverter control system is reacting to the harmonics on L1 by reducing or shutting off current draw from that phase.

Why Different Behavior at Your Friend's Shop?


Your friend's shop shows current on L1, even with the same type of inverter welder. This suggests that the imbalance in the open-delta system is less severe at their location. The reasons could be: Load Distribution

The types and amounts of other loads connected to the open-delta system at each location can significantly affect the voltage balance. If your friend's shop has more balanced loads, the voltage imbalance will be less pronounced.


Transformer Impedance

The impedance of the transformer supplying power to your friend's shop may be different from the impedance of the transformer supplying power to your location. Different transformer impedances will cause different voltage drops under load.

Line Length/Resistance

Your location may have longer power lines or higher resistance connections, leading to a greater voltage drop on L1 under load.


Voltage Taps

Although not likely (as it is difficult to reconfigure transformers in Japan) some customers have different voltage taps from the utility provider.

What You Should Do
1. Confirm Voltage Imbalance

Measure the voltage between each phase at your service entrance under load. This is critical. You need to know the actual voltage on each phase while the inverter welder is operating. The difference in voltages is more important that just the unloaded voltage.2.

Measure THD

Measure the Total Harmonic Distortion (THD) of the voltage on each phase, both with and without the inverter welder operating. High THD could be a contributing factor.3.

Transformer Impedance

If possible, obtain information about the impedance of the transformer supplying power to your location. This might be difficult to get, but it would be valuable.4.

Try a Different Brand/Model Inverter Welder

Test other inverter welders from different manufacturers. Some may be more tolerant of open-delta systems than others.5.

Talk to a Local Electrical Engineer

Consult with a local electrical engineer who is familiar with open-delta systems in Japan. They may be able to provide more specific insights based on local conditions and practices.6.

Upgrade to Closed-Delta (If Feasible)

The ultimate solution is to upgrade your service to a closed-delta three-phase system. However, this can be expensive and may not be practical.

Important Considerations
Don't Ignore the Problem

While the Panasonic representative said "you'll be alright," consistently running an inverter welder with no current on L1 could potentially stress the components on the other two phases and shorten the lifespan of the machine.


Warranty

Check the warranty on your inverter welders. Operating them on an unbalanced power system might void the warranty.*

Safety:
Always prioritize safety when working with electrical equipment. Consult with a qualified electrician if you are unsure about anything.In summary, the inverter welder's sophisticated control system is likely the cause of the L1 current dropping to zero. The underlying cause is the unbalanced voltage inherent in the open-delta system, which the inverter is trying (and perhaps over-zealously) to correct for. The severity of the imbalance at your location is likely the reason your friend's inverter draws some current on L1, while yours draws none. I hope this is helpful! Flag for review

Previous Question Next Question