Question: Comments? Angry letters?The following is the text of a proposed adjustment to the text of NEC120.57, which is under revision for the 2026 NEC cycle with comment due August 28th 2024:Right now if you have a low power L2 EVSE, you have to load calculate it at 7200 Watts regardless.If you had many such L2 chargers that would result in a vast overstatement of the necessary power.:CURRENT SECOND DRAFT120.57 Electric Vehicle Supply Equipment (EVSE) Load.The EVSE loads shall be calculated at either 7200 watts (volt-amperes) or the nameplate rating of the equipment, whichever is larger, for each EVSE served, unless modified by 625.42.
Okay, here's an analysis of the proposed change and potential comments, both for and against. I'll break it down into potential arguments, improvements, and possible areas of concern.
Summary of the Situation
Problem
The current requirement forces a minimum load calculation of 7200W (7.2kW) per EVSE, regardless of its actual power output. This is particularly problematic for low-power Level 2 chargers.
Consequence
Inflated load calculations lead to larger service entrances, transformers, panelboards, and wiring than are realistically needed, increasing costs unnecessarily.
Proposed Solution
The proposed change (not explicitly shown here, but implied) likely involves removing or modifying the "7200 watts" minimum.
Potential Arguments For Changing the Requirement
Accuracy and Realism
The current rule is demonstrably inaccurate. Many L2 EVSEs are significantly less than 7.2kW. For example, a 16A, 240V charger is only 3.84kW (16A 240V). A 6A charger is only 1.44kW (6A 240V). The current rule doesn't reflect the reality of available EVSEs.
Cost Savings
More accurate load calculations lead to reduced costs for electrical infrastructure. This makes EV charging more accessible and affordable.
Reduced Burden on the Grid
Overly conservative load calculations can lead to unnecessary strain on the grid, especially as EV adoption increases. More accurate calculations allow for better grid management.
Promotion of Energy Efficiency
Encouraging the installation of lower power chargers through accurate calculations can promote energy efficiency.
Consistency
The 7200W blanket rule is inconsistent with how other loads are calculated, which are generally based on nameplate ratings.
Addressing Large-Scale Installations
The problem compounds in multi-unit dwellings (MUDs), workplace charging, and other situations with multiple EVSEs. The 7.2kW minimum makes deploying EV charging at scale far more expensive.
Potential Arguments Against Changing the Requirement (Concerns to Address)
Future-Proofing
Some might argue that the 7.2kW minimum provides future-proofing for higher-power chargers that may become more common. However, this argument is weak since you can easily change the EVSE to a higher-power one later when they become necessary.
Safety Margin
The 7.2kW could be viewed as providing a safety margin to account for variations in EVSE output or potential future increases in output.
Complexity
A more nuanced calculation method might be more complex to implement and enforce. (Note: This can be mitigated by providing clear guidelines and examples.)
Gaming the System
Some might worry that installers will deliberately choose the lowest possible rated EVSE to minimize load calculations, even if a more powerful EVSE is needed. (Note: This is unlikely as the end user wants to charge as quickly as possible. )
Suggested Comments/Feedback to the NEC Committee
Here are some examples of comments you could submit, depending on your viewpoint:
If you support the change
"I strongly support the proposed change to 120.57. The current 7200W minimum load calculation for EVSEs is inaccurate and results in significant overestimation of power needs, particularly for Level 2 chargers. This leads to unnecessary costs for electrical infrastructure, hindering the widespread adoption of EVs. An accurate nameplate-based calculation is essential for promoting cost-effective and efficient EV charging." "The current 7.2kW minimum should be removed and the load calculation should be based only on the nameplate rating. This aligns with the calculation methods used for other loads and is consistent with NEC requirements." "I believe that using the nameplate rating of the EVSE is the most sensible way to determine the appropriate load calculation. This ensures that the electrical system is adequately sized without being excessively oversized." "In multi-unit dwellings, the mandatory 7.2kW load per EVSE significantly impacts feasibility and cost. Adopting a nameplate calculation method will remove a major barrier to entry for providing EV charging in these locations." "A revision to the 7.2kW calculation allows for more efficient grid resource utilization. Overly conservative load calculations contribute to undue strain on the grid during peak EV charging times. Accurate calculation is vital for effective grid management."
If you have concerns (and want to propose a modified change)
"While I agree that the 7200W minimum can be excessive, I am concerned about the potential for undersizing if only the nameplate rating is used. Perhaps a compromise would be to use the maximum possible continuous output power as specified on the EVSE's documentation, even if it's higher than the nameplate. This would allow for safety but also provide a more accurate number than 7200W." "I support moving away from the 7200W minimum, but I want to ensure clarity in enforcement. Perhaps the code could include examples demonstrating how to calculate the load for various Level 2 EVSE configurations." "I propose that 120.57 be revised to say "...the EVSE loads shall be calculated at the greater of the nameplate rating of the EVSE or the EV's onboard charger input current/voltage specification (if the charger is integrated), unless modified by 625.
42." This avoids issues where the EVSE may be limited but the EV can pull more, as this can overload the circuit." "I support using the nameplate rating, but I want to ensure that the code includes a clear definition of 'nameplate rating' for EVSEs. This will reduce ambiguity and ensure consistent application of the rule."
Improvements to the Proposed Change (Regardless of Your Position)
Clarity
The revised wording needs to be extremely clear and unambiguous. Provide specific instructions on exactly how to determine the EVSE load.
Definitions
Define "nameplate rating" (if that's the chosen metric) in the context of EVSEs.
Examples
Include example load calculations for common Level 2 EVSE scenarios, including: A simple 16A, 240V EVSE. A variable current EVSE (e.g., allows the user to set the current limit). A multi-EVSE installation.
Coordination with Article 625
Ensure the revised 120.57 is perfectly aligned with and references Article 625 (Electric Vehicle Charging Systems). Pay close attention to 625.42, as it's the exception clause.
Before Submitting
Review the entire NEC document
Make sure your proposed change doesn't inadvertently create conflicts with other sections of the code.
Consider the perspective of the NEC committee
They are concerned with safety and practicality. Frame your arguments in those terms.
Be specific and concise: Clearly state the problem, your proposed solution, and the rationale behind it.By addressing these potential arguments and providing clear, specific, and well-reasoned comments, you can help the NEC committee make an informed decision about this important change to the code. Flag for review