Question: Would there be an wiring this with an MC cable that has 2 hots and 2 neutrals if they make it? Not sure they do but will check with my supplier.

Okay, let's break down the scenario of using an MC cable with two hots and two neutrals. While MC cable configurations do exist with multiple conductors, a cable specifically containing two hots and two neutrals is extremely rare and likely non-standard. Here's why and what alternatives exist

Why It's Unlikely & Potential Problems:
Code Compliance (NEC)

The National Electrical Code (NEC) dictates how circuits must be wired for safety. Generally, circuits require a properly sized equipment grounding conductor. A 2-hot, 2-neutral configuration
without a dedicated ground wire creates a potential safety hazard.

Neutral Sharing

While it's possible to have two hots sharing a single neutral in a Multiwire Branch Circuit (MWBC), this requires specific configurations (like a two-pole breaker ensuring opposite phases) and a properly sized neutral conductor to handle the potential additive current. You would not simply run two separate circuits with two independent neutrals in the same cable, as this could overload one of the neutrals.

Lack of Standardization

Manufacturers tend to produce cables that meet common wiring needs and code requirements. A 2-hot, 2-neutral MC cable isn't a common need, hence the rarity.

Alternatives & Better Practices

Here are more likely and code-compliant ways to achieve similar wiring goals:1.

Two Separate MC Cables

This is the simplest and often most practical approach. Run two individual MC cables: one 12/2 or 14/2 MC cable for each circuit. Each cable will have one hot, one neutral, and a ground wire (required).2.

MC Cable with More Conductors

You might find MC cable with more conductors than just 2 hots, 1 neutral, and ground. For example, 12/4 or 14/4 MC cable exists.


Example use of 12/4 MC

It has 4 insulated conductors (typically black, red, white, and blue) and a ground wire. You can use black and red as your two hots, white as one neutral, and blue as the other neutral.3.

Multi-Wire Branch Circuit (MWBC) with Shared Neutral

This is an efficient way to run two circuits using fewer conductors within a single cable. However, it's critical that you meet all NEC requirements:

2-Pole Breaker

You
must use a two-pole circuit breaker where the two hot wires connect to opposite phases (180 degrees apart). This ensures that the current in the shared neutral is the difference between the two hot legs, rather than the sum.

Properly Sized Neutral

The neutral conductor must be sized to handle the maximum potential current draw from both circuits.

Common Trip

The breaker needs to be a common trip type, so if one circuit faults, both circuits are shut off simultaneously.

Important Considerations



Local Codes

Always check with your local electrical codes and permitting requirements. They may have specific restrictions or preferred wiring methods.

Consult a Qualified Electrician

If you're unsure about any aspect of electrical wiring, especially complex scenarios like shared neutrals or using uncommon cable configurations, it's
essential* to consult with a licensed and experienced electrician. They can ensure the wiring is safe, code-compliant, and meets your needs.

In summary, while you could technically use a 4-conductor MC cable and dedicate two wires to hot and two wires to neutral, it's not the intended use and a properly wired MWBC is generally a better and safer solution. Ensure that you understand the code requirements and consult a qualified electrician before attempting any electrical work.