Question: Under 625.43 in the new edition, is it possible to have a disconnect remote from the equipment?625.43(A) says yes, but 625(B) says that even if (A) applies that (B) applies also, which prohibits it.
You've correctly identified a potential conflict in the interpretation of 625.43 of the NEC. Let's break down the clauses to understand the situation and possible interpretations: 625.43 Electric Vehicle Supply Equipment Disconnecting Means
This section generally deals with disconnecting means for EVSE.
625.43(A) Location
This section permits the disconnecting means to be installed either "at the supply equipment" or "remotely located."
625.43(B) Disconnect Identification
This section requires clear identification of the disconnecting means.
The Apparent Conflict
Your concern stems from the interplay between 625.43(A) allowing remote disconnects and 625.43(B) seemingly implying limitations on that remote placement. 625.43(B) doesn't necessarily prohibit a remote disconnect, but it imposes requirements on it:
625.43(B)
The disconnecting means shall be readily accessible and suitable for the conditions.
Resolution and Interpretation
The key here is that
625.43(B) modifies 625.43(A), it doesn't negate it. You can have a remote disconnect, but only if it also meets the requirements of 625.43(B).
How to Make a Remote Disconnect Compliant
To legally have a remote disconnect, you must comply with all aspects of 625.43:
625.43(A)
It can be remotely located (as long as it meets all other requirements).
625.43(B)
The disconnect MUST be
readily accessible and suitable for its environment. Furthermore, it must be properly identified.
Example Scenarios
Compliant
EVSE inside a garage, disconnect located on the outside of the garage. The disconnect is readily accessible (anyone can get to it easily), suitable for outdoor conditions, and properly labeled as disconnecting the EVSE. This would be compliant.2.
Non-Compliant
EVSE inside a building, disconnect located in a locked electrical room several floors away. This is likely not readily accessible, and may not be properly identified, even if it's suitable for the environment.
In summary
A remote disconnect is permitted, but it
must be readily accessible, suitable for the conditions, and properly identified according to 625.43(B). 625.43(B) acts as a constraint or condition on 625.43(A), not a prohibition.Always consult with a qualified electrical inspector for final approval on any installation to ensure it meets local and national code requirements. They are the final authority in your jurisdiction. They can interpret the code based on the specific details of your installation. Flag for review