Topic: location of transformer for computer server room.

User: steve61, Location: Nebraska

Asked on: Wednesday, August 28, 2024 at 9:19 am EDT
Answered on: Thursday, March 6, 2025 at 1:46 am EST

Question: I am installing a circuit in my place of work to have the computer server room hooked up to an emergency generator. I will be using a 15 KVA transformer to step the voltage down from 460 VAC to 208 VAC. The circuit will be about 450 feet long from the generator panel to the server room. Can I locate the transformer at the generator panel,Or do I have to have the transformer located closer to or in the server room ? Also,Do I need to install a ground rod for the transformer ? Thank You for any info. Thanks,Steve Wiese.

Okay, Steve, let's break down the best approach for your emergency generator circuit and address your questions about transformer placement and grounding.

Transformer Placement: Generator Panel vs. Server Room

The best practice is generally to locate the transformer closer to the load (server room). Here's why: Voltage Drop

At 450 feet, voltage drop will be a significant factor at 460V. By stepping down closer to the server room, you can use smaller gauge conductors for the 460V run, saving on cost. When you are at a low voltage like 208v every foot counts and its much more difficult to compensate at low voltage.


Smaller Conductors on Primary

You'll be carrying a lower current at the 460V primary side of the transformer. This allows for smaller, less expensive conductors for the long run to the generator panel.

Safety

A lower voltage is generally considered safer.

However, there are situations where placing the transformer at the generator is preferred



Environmental Considerations

If the server room environment is not suitable for the transformer (dust, high humidity, lack of space, etc.), placing it at the generator panel (assuming that location is suitable) might be necessary.

Existing Infrastructure

If you have existing conduits or wiring that are best suited for the 460V run, it might be more cost-effective to keep the transformer at the generator.

Calculations are Crucial



Voltage Drop Calculations

Regardless of where you place the transformer, you must perform voltage drop calculations for both the 460V and 208V portions of the circuit. This is critical to ensure that the voltage at the server room equipment stays within acceptable limits under full load. Use a voltage drop calculator or consult with an electrical engineer. You'll need to know the total load in amps (at 208V) that the server room will draw.

Conductor Sizing

Properly size the conductors for both the 460V and 208V sections of the circuit based on the calculated current and voltage drop requirements. Refer to the National Electrical Code (NEC) for ampacity tables and derating factors.

Grounding: Ground Rod for the Transformer
NEC Article 250 (Grounding and Bonding) is Key

The NEC dictates the grounding requirements. Generally, you

will
need to establish a grounding electrode system at the transformer location. Separately Derived System

Because the 208V power is derived from the generator's 460V, the transformer output is considered a
separately derived system. This means you need to treat it like a new service entrance, from a grounding perspective.

Grounding Electrode Conductor (GEC)

You will need to run a grounding electrode conductor (typically copper) from the neutral point (X0) of the transformer secondary to a suitable grounding electrode.

Acceptable Grounding Electrodes

Acceptable grounding electrodes, as defined by the NEC, include:


Ground Rods

Usually two ground rods driven at least 8 feet apart.

Metal Water Pipe

If a metallic water pipe is available and meets the NEC requirements, it can be used as part of the grounding electrode system.


Building Steel

The metal frame of the building, if effectively grounded.

Concrete Encased Electrode (Ufer Ground)

If available.


Bonding

You must also properly bond the transformer enclosure and any metallic conduits to the grounding electrode system.

In summary

1. Evaluate the pros and cons of each transformer placement.
2. Perform thorough voltage drop calculations for both scenarios.3. Size conductors appropriately.
4. Consult the NEC and local electrical codes for grounding requirements.5. Implement a proper grounding electrode system at the transformer location.


Disclaimer:
This information is for general guidance only. You must consult with a qualified and licensed electrical engineer and electrician to ensure that your installation complies with all applicable codes and regulations and is safe and reliable. Failure to do so could result in serious injury, death, or property damage. Flag for review