User: SteveO NE, Location: Northeast
Asked on: Wednesday, August 28, 2024 at 10:58 am EDT
Answered on: Thursday, March 6, 2025 at 1:46 am EST
Question: I am wondering what the general consensus is with the following circles I've seen discussions go regarding this with Electricians, AHJs, and Engineers. Aux grounding electrode, or EGC is adequate? I am currently a fly on the wall between 3 parties arguing this (and I'm staying out of it for now) but its not the first time I've seen it come up so I was curious what others thought of this.690.47 - This seems debated amongst people in my area but this says the EGC is adequate for bonding a detached carport structure (Steel/conductive). The debate as compared to a ground mount is that it is providing a separate covered structure for parking. Feel free to weigh into that.250.32 (A) - Separate building, separate electrode. Goes to the point of the structure providing covered parking. It gives an exemption of a single branch circuit so lets clarify we aren't talking about that.Scenario 1: Multiple Inverters with a combiner PanelScenario 2: Single or Multiple Inverters but with another single circuit serving lights affixed to the carport. This one seems to get people going. I've heard two arguments here: the lighting circuit further supports the concept that this is a separate functional building beyond just a "PV support structure." I have also heard that if the lighting is a single branch circuit, then it meets the exemption in 250.32 (A) and the PV doesn't count as a branch circuit.In both scenarios we can assume its fed by a separately derived source because typically we are stepping up, but it would be behind an OCPD at the origination of the feeder (in the primary building structure) side so it shouldn't be a factor really.Finally, regardless of what the code says, what do you think is best practice? Aux rod or not?
This is a classic, and often contentious, issue in PV installations. Here's my breakdown of the arguments, common interpretations, and my take on best practices
Understanding the Code Sections
690.47 (PV System Grounding): This section dictates the grounding requirements specifically for the PV system. It essentially states that the Equipment Grounding Conductor (EGC) is usually sufficient for bonding the metallic parts of the PV system to the main grounding system. The intent is to provide a low-impedance fault current path. 250.32 (Grounding at Separate Buildings or Structures): This is the core of the debate. It generally requires a grounding electrode system at a separate building or structure supplied by a feeder or branch circuit. The intent is to minimize voltage differences between the earth potential at the main building and the separate structure, preventing shock hazards. 250.32(A) Exception: This provides an out for a single branch circuit supplied to the separate building, where the EGC is sufficient for grounding.
Arguments and Interpretations
Let's address the specific scenarios and the arguments surrounding them: General Argument (Carport as a Separate Structure): The crux of the debate lies in whether a carport should be considered a "separate building or structure" under 250.32. Some argue it is a separate structure because: It provides covered parking, a distinct function from the main building. It has its own structural integrity and isn't merely an appendage of the main building.Others argue it is not a separate structure, especially if: It's closely attached to the main building, making it a physical extension. Its primary purpose is to support the PV array, not to provide a functionally separate building.
Scenario 1: Multiple Inverters with a Combiner Panel Arguments for Additional Grounding Electrode
The sheer number of inverters and the presence of a combiner panel suggest a substantial electrical system, leaning towards treating it as a separate structure. Following 250.32 strictly, regardless of the code's original intent.
Arguments Against Additional Grounding Electrode
690.47 might be interpreted as overriding 250.32 in this specific case, as the EGC provides the necessary fault current path for the PV system. The key here is the purpose of the grounding. 690.47 focuses on fault current within the PV system, while 250.32 is about overall earth potential differences between buildings.
Scenario 2: Single or Multiple Inverters with a Lighting Circuit Arguments for Additional Grounding Electrode
The lighting circuit strengthens the argument that the carport serves a function beyond simply supporting PV. It's now undeniably a place for parking and potentially other activities (maintenance, etc.) that require lighting. The presence of the additional circuit arguably nullifies the single-branch-circuit exception in 250.32(A).
Arguments Against Additional Grounding Electrode
The "single branch circuit" exception is tricky. Some argue that the PV system is not a branch circuit in the traditional sense, so the lighting circuit is the only branch circuit, making the exception applicable. This is a very narrow and potentially dangerous interpretation.
Separately Derived System (SDS) Considerations You correctly point out that the SDS is behind an OCPD. This is important! The presence of an SDS itself doesn't automatically trigger the need for a grounding electrode at the separate structure. However, the SDS does influence how the grounding is implemented if one is required. The OCPD on the primary side, it sounds like you are saying at the main building, would remove the requirement for an aux electrode at the carport because it is a branch circuit and meets the exceptionBest Practices and My Recommendation Erring on the Side of Safety
I lean strongly towards installing an additional grounding electrode (ground rod or equivalent) at any carport structure with a significant PV installation, especially if it has additional electrical loads like lighting. The small additional cost is well worth the peace of mind and enhanced safety.
The 'Why' Matters
The purpose of a ground rod is for safety to reduce shock hazards. By adding one, it's cheap insurance and better chance of being safe.
Reasons for My Recommendation
Mitigating Ground Potential Differences
PV systems can inject current into the ground, potentially creating voltage gradients. An auxiliary grounding electrode helps equalize the ground potential between the main building and the carport, reducing the risk of shock if someone touches a grounded part of the PV system while standing on the earth.2.
Enhanced Fault Current Path
While the EGC provides a fault current path within the PV system, an additional grounding electrode provides a more robust path to ground for faults originating outside the PV system (e.g., a fault in the lighting circuit).3.
Future-Proofing
The carport might be modified in the future (e.g., adding outlets for electric vehicle charging). Having an existing grounding electrode simplifies future upgrades and ensures continued safety.4.
AHJ Acceptance
Many AHJs prefer or even require an additional grounding electrode, even if the code interpretation is ambiguous. It avoids conflict and ensures a smoother inspection process.
Important Considerations
Local Codes and AHJ Authority
Always defer to local codes and the interpretation of your local AHJ. They have the final say.
Soil Resistivity
If the soil has very high resistivity, a single ground rod might not be sufficient. Consider using multiple rods bonded together or other grounding methods (e.g., ground plate).
Bonding to Other Metallic Structures
Ensure that any metallic structures (fences, railings, etc.) near the carport are properly bonded to the grounding system.
Documentation
Clearly document the grounding system design and installation, including the location and type of grounding electrodes, in the PV system documentation.
In summary: While the code can be interpreted in different ways, the safest and most practical approach is usually to install an auxiliary grounding electrode at a carport with a substantial PV system, especially if it includes additional electrical loads. It's cheap insurance, minimizes potential shock hazards, and often simplifies the inspection process. Ultimately, consult with your local AHJ to determine their specific requirements and preferences. Flag for review