Topic: Split Enphase Combiner Output

User: hitehm, Location: Las Vegas NV

Asked on: Wednesday, August 28, 2024 at 12:01 pm EDT
Answered on: Thursday, March 6, 2025 at 1:46 am EST

Question: Our problem:Coming off the roof we have 3 Enphase 20A microinverter circuits landing in the Enphase combiner box, then leaving the combiner box on 1 60A circuit (52.94 actually) through the disconnect and what would normally land on a 60A backfed solar breaker in the MSP. However, the customer's MSP won't allow more than a 50A 2P breaker in the top slots where we need to land our 60A solar breaker.Possible Solution: (And fyi, we are trying to avoid 2 separate combiner boxes with 2 separate discos)Place a small 4 slot MLO subpanel after the disco before the MSP and split the one 240V 60A 2P PV circuit into two 240V 30A 2P feeder circuits that will land in the top 2 slots on two 30A backfed breakers in the MSP.So the questions are:Is there anything wrong electrically, code wise, safety wise or other that I'm missing?

Okay, let's break down this situation and analyze your proposed solution. You've got a common problem and you're thinking about it the right way.

Understanding the Problem Oversized OCPD Requirement

Your calculations dictate a 60A breaker for the combined Enphase circuits, but the MSP physically won't accommodate it in the required location.


Avoidance of Extra Hardware

You're looking to avoid the cost and complexity of adding a second combiner box and disconnect, which is understandable.

Analyzing Your Proposed Solution


Your idea of using a small subpanel to split the 60A circuit into two 30A circuits is a viable approach, IF done correctly and in accordance with code. Here's a detailed breakdown

Here's a breakdown of the proposal and potential pitfalls:
Legality

It would violate the UL Listing on the IQ Combiner box and the Inverter's UL Listing for parallel connections.


Code Compliance (NEC Considerations)
: NEC 705.12(B)(2)(3)(a) states "The sum of the overcurrent devices supplying power to a busbar or conductor shall not exceed 120 percent of the rating of the busbar or conductor." In the MSP, you must verify that the existing busbar can handle the sum of the main breaker, all other loads, and the combined backfed solar breakers. If the MSP busbar is, for example, rated at 200A and the main breaker is 200A, the maximum backfed solar breaker amperage would be limited to 40A (200A 1.2 = 240A; 240A - 200A = 40A). UL Listing of Equipment

You are modifying the original UL listing by landing on the disco (the 60 amp rated disco) and then landing on a subpanel and splitting up to two 30 amp breakers backfed into the MSP. This violates the UL listing on the Enphase IQ Combiner 4.

Feeder Conductor Sizing

The conductors between the disconnect and the subpanel must be rated for at least 60A (or whatever the calculated load demands based on NEC 705.12).

Subpanel Rating

The subpanel must be rated for at least 60A.


Overcurrent Protection in the Subpanel

You need to install two 30A breakers in the subpanel to protect the conductors feeding back to the MSP.

Conductor Sizing to MSP

The conductors from each 30A breaker in the subpanel to the 30A backfed breakers in the MSP must be sized appropriately for 30A.


Physical Installation

All wiring and equipment must be installed according to code and manufacturer's instructions. This includes proper conduit, connectors, and secure mounting.

Labeling

Clear and permanent labeling is crucial. You need to label:
The subpanel as a "PV Subpanel" or similar. The 30A breakers in the subpanel as "Feeders to PV System" or similar. The 30A backfed breakers in the MSP as "PV System Input" or similar.

Potential Issues and Considerations
Voltage Drop

Consider voltage drop, especially if the distance between the subpanel and the MSP is significant. Use appropriately sized conductors to minimize voltage drop.


Working Space

Ensure adequate working space around the subpanel and MSP for safe installation and maintenance.

AHJ Approval



This is critical.
Discuss this solution with your local Authority Having Jurisdiction (AHJ) before implementing it. They may have specific requirements or concerns that you need to address. Document the conversation and obtain their approval in writing if possible. Alternative Solutions (Revisit These)

Before proceeding, carefully reconsider these alternatives. They may be less desirable but potentially more straightforward:

Derating

Can you adjust the Enphase system settings (if possible and without compromising performance significantly) to reduce the output current and allow for a smaller breaker? This is often not ideal, but sometimes an option.


Load-Side Tap (If Allowed)

Some AHJs allow a load-side tap if the tap conductors are sized appropriately, protected by an overcurrent device, and meet specific requirements. This is highly jurisdiction-dependent.

Line Side Tap

If the power company will allow a line side tap, you could add a new meter and MSP that would accept the 60 amp breaker. It is very unlikely they would do this however.


Main Panel Upgrade

While costly, upgrading the main panel is often the cleanest solution to meet growing energy needs, but it is still expensive.

Recommendation
1. Consult with the AHJ

This is the most important step. Present your proposed solution and get their feedback and approval.2.

Detailed Calculations

Perform thorough calculations to ensure all conductors are sized appropriately and that the overall system complies with NEC 705.12 and other relevant codes.
3.


Document Everything

Keep detailed records of your calculations, discussions with the AHJ, and all installation procedures.4.

Consider Alternatives

Re-evaluate the other options (derating, load-side tap, panel upgrade) to see if one might be more practical in your specific situation.5.

Double-Check Everything

Before energizing the system, have a qualified electrician thoroughly inspect the entire installation to ensure it meets all applicable codes and standards.

In summary, while your proposed solution is theoretically possible, it requires careful planning, strict adherence to code, and the approval of your local AHJ. Proceed cautiously and prioritize safety and compliance.