Question: When you have an MIGB on the conduit what work is involved to actually bond it to enclosure? Thank you.
When you have a MIGB (Main Grounding/Bonding Jumper) on a conduit, the work involved in actually bonding it to an enclosure depends on the type of enclosure and the grounding/bonding requirements of your jurisdiction (NEC in the US, for example). However, the general principle is to create a low-impedance path from the conduit to the enclosure's grounding system. Here's a breakdown of the process and considerations
Understanding the Context
Purpose of the MIGB
The MIGB is a conductor (usually a wire) that ensures the metallic conduit is electrically connected to the grounding electrode system and the enclosure. This helps to: Provide a low-impedance path for fault current, facilitating the operation of overcurrent protective devices (circuit breakers or fuses) during a fault. Minimize voltage differences between metallic parts, reducing the risk of electric shock.
Conduit Type
The type of conduit matters. Common types include:
Rigid Metal Conduit (RMC)
Offers excellent grounding characteristics when properly installed.
Intermediate Metal Conduit (IMC)
Similar to RMC but lighter weight. Also offers good grounding.
Electrical Metallic Tubing (EMT)
Thinner-walled than RMC or IMC. Grounding depends on proper fittings.
Flexible Metal Conduit (FMC)
Requires a separate grounding conductor unless specifically listed for grounding without one (look for markings indicating its suitability as an equipment grounding conductor).
Liquidtight Flexible Metal Conduit (LFMC)
Similar to FMC, but with a liquidtight jacket.
Enclosure Type
The type of enclosure also matters. Common types include:
Metal Enclosures
Bonding is usually done to the metal body of the enclosure.
Non-Metallic Enclosures
Often have a grounding terminal specifically for this purpose.
General Steps for Bonding the MIGB to an Enclosure1. Identify the MIGB
Make sure you've correctly identified the MIGB. It should be sized according to the relevant code and often originates from the grounding electrode system (e.g., from the service disconnect).2.
Prepare the Enclosure Surface (if applicable)
Metal Enclosures
Clean the area where the MIGB will be connected. Remove any paint, rust, or other coatings to ensure a good metal-to-metal contact. A wire brush or emery cloth can be used.
Non-Metallic Enclosures
Usually, the enclosure provides a grounding terminal, eliminating the need for preparation.3.
Connecting the MIGB
Use one of the following methods, depending on the enclosure and available hardware:
Grounding Bushing and Jumper
Install a grounding bushing on the conduit entering the enclosure. The grounding bushing has a lug for connecting the MIGB. Connect the MIGB to the grounding lug on the grounding bushing using an appropriate connector (e.g., a compression connector or a set-screw connector). Connect the other end of the MIGB to the enclosure's grounding terminal or a location on the enclosure that has been prepared for grounding.
Grounding Locknut and Jumper
Install a grounding locknut on the conduit entering the enclosure. The grounding locknut has a lug for connecting the MIGB. Connect the MIGB to the grounding lug on the grounding locknut using an appropriate connector (e.g., a compression connector or a set-screw connector). Connect the other end of the MIGB to the enclosure's grounding terminal or a location on the enclosure that has been prepared for grounding.
Direct Connection to Enclosure Grounding Terminal
If the enclosure has a designated grounding terminal (a lug or screw intended for grounding), directly connect the MIGB to this terminal using a suitable connector.
Compression Connector/Lugs
Attach a suitable compression lug to the end of the MIGB. Use a bolt or screw to securely attach the lug to the enclosure, ensuring good metal-to-metal contact (again, clean the area first if necessary).4.
Torque Connectors Properly
Tighten all connectors (lugs, screws, bolts) to the manufacturer's recommended torque specifications. This is crucial for a reliable connection. Over-tightening can damage the connector or the enclosure; under-tightening can result in a loose connection and increased impedance.5.
Inspect
Double-check the connection to ensure it is secure and that there are no loose strands of wire.6.
Document
Keep records of the grounding and bonding connections, as this may be required for inspection and maintenance.
Important Considerations Code Compliance
Always follow the requirements of your local electrical code (e.g., the NEC in the United States). Specific rules govern grounding and bonding, including conductor sizing, acceptable connection methods, and required inspection procedures. Consult the relevant articles of the code (e.g., NEC Article 250).
Conductor Sizing
The size of the MIGB must be appropriate for the size of the service conductors or the overcurrent protective device protecting the circuit. Consult the applicable code tables (e.g., NEC Table 250.102(C)(1)) for sizing.
Listed Equipment
Use only listed (e.g., UL-listed) connectors and grounding hardware. This ensures that they have been tested and certified for their intended purpose.
Qualified Personnel
Electrical work should be performed by qualified and licensed electricians who are familiar with electrical codes and safety procedures.
Grounding vs. Bonding
Understand the difference between grounding and bonding. Grounding connects the electrical system to the earth. Bonding connects metallic parts to create a low-impedance path for fault current. The MIGB is part of the bonding system.
Continuous Run
Ideally, the MIGB should be a continuous run of wire, without splices. If splices are necessary, use approved splicing methods that maintain the integrity of the conductor.
Corrosion Protection
In corrosive environments, use corrosion-resistant connectors and consider applying a corrosion-inhibiting compound to the connections.
Example Scenario (using RMC conduit and a metal enclosure)1. RMC conduit enters a metal enclosure.
2. A grounding bushing is installed on the conduit inside the enclosure.3. The MIGB (sized appropriately for the service) is connected to the lug on the grounding bushing using a compression connector.
4. The other end of the MIGB is run to the enclosure's grounding terminal (if it has one). If not, a clean, bare spot on the enclosure is located.5. A compression lug is attached to the MIGB.
6. The lug is bolted to the prepared spot on the enclosure, ensuring good metal-to-metal contact.7. All connections are torqued to the manufacturer's specifications.
In Summary: Bonding the MIGB to an enclosure requires careful attention to detail, proper selection of hardware, and adherence to electrical codes. The goal is to create a reliable, low-impedance connection that will safely carry fault current and protect against electrical shock. Always consult with a qualified electrician if you are unsure about any aspect of the process. Flag for review