Topic: Interpretation of CEC 18-202 (2) Wiring Methods Zone 21

User: Geddes, Location: BC

Asked on: Wednesday, August 28, 2024 at 1:53 pm EDT
Answered on: Thursday, March 6, 2025 at 1:47 am EST

Question: I have a junction box that will be housing terminal blocks being used as a termination point for field devices. The box is located in a Class II div 1 (Zone 21) hazardous area.The terminal blocks are WDU 2.5, with a rating of Ex eb II C GbThe rules read:18-200 Equipment, Zone 21 locations (see Appendix B)Electrical equipment installed in a Zone 21 location shall be in accordance with Table 18.18-202 Wiring methods, Zone 21 (2) : Boxes, fittings, and joints shall be threaded for connection to conduit or cable glands, and boxesand fittings shall be suitable for use in Zone 21 locations.The way I read this is that the box must be "suitable for use" and not marked for use in Zone 21 so it could be any dust-tight general purpose box, however the equipment (Terminal blocks) are not rated for the hazardous area so must be encapsulated by a enclosure rated ta or tb as per table 18What makes me second guess it is that 18-150 Equipment, Zone 2 locations (2c) had a specific permissive for enclosures that reads:Notwithstanding Subrule 1) and Rule 18-052, the following shall be permitted:equipment that is installed in a Type 4 or 4X enclosure, or an IP65 or higher enclosure, and isi) non-sparking in normal operation;ii) not used for heating purposes; andiii) not otherwise provided for in Subrule 2);Terminal blocks meet the CEC definition for electrical equipment.Can anyone advise to similar installations.

You've highlighted a key area of interpretation within the Canadian Electrical Code (CEC) and the application of equipment in hazardous locations. Let's break down your understanding and address the considerations

Your Understanding and Concerns
Zone 21 Requirements

You correctly identified that Rule 18-200 requires equipment in Zone 21 to comply with Table 18. Rule 18-202(2) is also correctly interpreted, that Boxes and fittings need to be threaded for conduit or cable glands and suitable for zone 21.


Terminal Block Rating

You recognize that the WDU 2.5 terminal blocks, while rated Ex eb II C Gb, are component level certifications and not complete equipment certifications for Zone 21. Ex eb protection relies on preventing arcs and sparks within the device under normal and abnormal conditions.

Enclosure for Encapsulation

Your conclusion that you might need to use a `ta` or `tb` rated enclosure based on Table 18 to encapsulate the terminal blocks is accurate. This is a common approach when the equipment itself doesn't have a Zone 21-specific rating.


Comparison to Zone 2 (18-150(2c))

This is where the confusion often arises. The Zone 2 rule provides a specific exception that allows general-purpose equipment to be used in a Type 4/4X or IP65 enclosure under certain conditions.

There is no similar exception in Zone 21.
Analysis and Guidance1. The Absence of a Zone 21 Exception

The crucial point is the absence of a permissive rule like 18-150(2c) for Zone 21. The CEC is quite specific about hazardous locations, and if a permissive rule exists, it will be explicitly stated. Since there isn't one for Zone 21, you

cannot
assume that a Type 4/4X or IP65 enclosure is sufficient for unrated electrical equipment (like the terminal blocks) in that zone.2. Table 18 and Protection Techniques

Table 18 directs you to acceptable protection techniques for Zone 21. For equipment that is not already certified for Zone 21, encapsulation (`ta` or `tb`) is a common and generally accepted method. `ta` refers to protection by enclosure and `tb` refers to protection by enclosure (dust ignition protection by enclosure "t")

Encapsulation (`ta`/`tb`)

This involves fully enclosing the terminal blocks in a certified enclosure designed to prevent dust ingress and limit surface temperatures. These enclosures are specifically designed and tested to meet Zone 21 requirements. Crucially, the enclosure's temperature rating must be appropriate for the specific dust present and the maximum expected operating temperature of the terminal blocks. You need to perform a temperature classification calculation, considering the enclosure's ambient temperature and the heat generated by the terminal blocks.3.

Enclosure Selection Considerations



Zone 21 Marking

Ensure the enclosure you select is specifically marked for Zone 21 (or Class II, Division 1 if using older terminology).

Temperature Rating

The enclosure must have a temperature code (e.g., T6, T5, T4) that is suitable for the specific dust present in your environment and the operating temperature of the terminal blocks. This is critical for preventing dust ignition. This is the most important part in selecting an enclosure.


Material

The enclosure material must be suitable for the environment (corrosion resistance, etc.).

Entry Points

Use appropriately rated cable glands or conduit seals to maintain the integrity of the enclosure.


Certification

Look for certifications from recognized testing laboratories (e.g., CSA, UL) to ensure the enclosure meets the applicable standards.4.

Terminal Block Certification (Ex eb II C Gb)

While the terminal blocks have an Ex eb rating, that rating alone doesn't allow them to be used directly in Zone 21. The Ex eb rating is a component-level protection method; it indicates that the blocks are designed to prevent ignition sources under normal and abnormal conditions. However, it doesn't guarantee that the entire assembly (terminal blocks within a non-Zone 21 enclosure) meets Zone 21 requirements.

In Summary


Your interpretation is mostly correct. You cannot rely on a Type 4/4X or IP65 enclosure alone to make unrated terminal blocks suitable for Zone 21. You must either: Use terminal blocks and an enclosure specifically certified for Zone 21 (or Class II, Division 1) as a complete assembly. Use a Zone 21-certified (`ta`/`tb`) enclosure that encapsulates the terminal blocks, ensuring the enclosure's temperature rating is appropriate.The safest and most code-compliant approach is to use properly certified equipment for the hazardous location. When in doubt, always consult with a qualified electrical engineer or inspector who is familiar with hazardous location installations.

Recommendation1. Reiterate: Zone 21 requires suitable equipment. The terminal blocks are components with a Ex eb rating, not fully compliant devices for Zone 21.2. Enclosure Selection: Choose a Zone 21/Class II, Div 1-rated enclosure with the correct temperature rating for the dust and the equipment inside. Make sure it's properly sealed and grounded.3. Documentation: Document your reasoning, the ratings of all equipment, and the applicable code sections. This will be valuable during inspections.4. Consult: If you are still unsure, consult with a qualified electrical engineer experienced in hazardous location design. This is the best way to ensure compliance and safety. Flag for review